Hey got a reference for left and right of the sink? What happens if my sink is in the island and there is no backsplash?
Can left side receptacles cross over and be right side receptacles also? Like I might have 1 receptacle left of sink and 5 on right. Can I make my circuits 3 and 3?
Kitchens are required to have
at least two 20amp Small Appliance Branch Circuits (for a while now
I don't remember any requirement in the NEC as to 'left' and 'right' of a sink.
The SABC requirement applies to
all the countertop area/length in the kitchen.
Thus an island fits in the requirement for requiring outlet(s) as well.
Which generally is/was any countertop area/length greater than 12 inches has to have an outlet available. And countertop (or island
) outlets have to be spaced such that any space between outlets can be no more than 24 inches from outlet to outlet.
If the space 'behind' a sink/range/cooktop on an island is less than 12 inches deep (behind the 'thingy'
), then the 'thingy' divides the countertop space and you then just have to space outlet(s) based on the countertop space left and right of the 'thingy'. But if the depth 'behind' is greater than 12 inches deep, then the countertop is considered 'continuous' and outlet(s) must be spaced accordingly. No face-up countertop outlets.
Don't for get the GFCI requirements within 6 feet of a sink in the kitchen as well.