Gfi outlet problem

machsnell

Well-known member
Joined
Jun 12, 2010
Messages
942
Location
Northern Virginia
I have 4 20 amp circuits wired in garage with the first outlet in the circuit being a gfi outlet.

I wired it late at night and I reversed the line and load wires.

Didn't work and looked in and saw my mistake.

I really wired correctly and it worked fine.

3 days later I go out and it doesn't work.

I reset it and it immediately trips. Immediately like my finger doesn't leave button

I open it up and remove the load side and it is works fine. I didn't remove the tied together grounds just the hot and neutral load side.

7 outlets downstream. I don't think I touched any of these after I fixed earlier mistake but I might have been putting on cover plates.

What is my best route to find problem?



Sent from my SM-G900V using Tapatalk
 
To avoid these ads, REGISTER NOW!

bottom feeder

Well-known member
Joined
Dec 10, 2012
Messages
331
Location
Utah
Do you have a spare GFCI outlet that you can try? Maybe the original is defective or got fried.
 

The Cobbler

Super Moderator
Staff member
Joined
Oct 24, 2013
Messages
25,962
Location
Niagara Region, Ontario, Canada
I would do the cut in half approach. disconnect the outlet that's half way to the last one and try the gfi, if it trips your problem is in the forst half, if it doesn't trip, problem is in last half. then try the cut in half again, narrow it down that way .
 

Rookie2

Well-known member
Joined
Feb 27, 2013
Messages
1,925
Location
Western Pa.
I think you have to open up each outlet and check the wiring for nicks etc (when you shoved the outlet in ).
 

checkthisout

Well-known member
Joined
Sep 5, 2008
Messages
5,232
Hook the load side back up and just work your way down the line pulling out device and removing and inspecting the wires until you find the wire that got nicked.

I would: Pull the next outlet out, attempt to reset, if no reset, remove power wires from outlet, attempt to reset, if it resets, then move to next out down the line and repeat the process.
 

landyacht

Well-known member
Joined
Mar 26, 2011
Messages
71
Location
Langley BC
Also check your bare ground wire didn't get pushed up against the neutral screw on one of your downstream outlets when you pushed them in. That will cause nuisance tripping
 
OP
M

machsnell

Well-known member
Joined
Jun 12, 2010
Messages
942
Location
Northern Virginia
So I figured out what happened.

One of my guys was there framing out a small wall and moved 3 receptacles out. He wired two of them by the time I was back there.
I told him not to wire anything in the future that I was doing all 9f the wiring and wanted to know that is was all correct.

Anyway he tied 2 grounds together and left 9ne long but never put one 9f the green wire nuts on it. They were touching but definitely not getting great contact.

I opened up the other receptacle he has done and the screws were looser than they should have been and the wire was a little mangled and the grounds were the same. Ugh!

I don't think they even use a ground in Honduras.

I guess that is why it worked at first but maybe when face plate went on it moved the receptacle enough to disrupt the ground.

Thanks for the help all.


Sent from my SM-G900V using Tapatalk
 
To avoid these ads, REGISTER NOW!

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
I would do the cut in half approach. disconnect the outlet that's half way to the last one and try the gfi, if it trips your problem is in the forst half, if it doesn't trip, problem is in last half. then try the cut in half again, narrow it down that way .
In situations like this this is always your best approach. :thumbup:
 
OP
M

machsnell

Well-known member
Joined
Jun 12, 2010
Messages
942
Location
Northern Virginia
Yes made life easier than undoing all unecessarily. Gfci s are delicate huh? Good thing in reality

Sent from my SM-G900V using Tapatalk
 

6t7gto

Well-known member
Joined
Dec 6, 2005
Messages
522
Location
bedford,ohio
Interesting that you are saying the ground caused it.
Because GFCI's can be used on a two wire system without a ground.
 
OP
M

machsnell

Well-known member
Joined
Jun 12, 2010
Messages
942
Location
Northern Virginia
That is the only thing I can attribute it to. I only temp wired it but isolated it to that circuit. I really did the connections and pigtails also is it possible one of those was more likely the issue?

Sent from my SM-G900V using Tapatalk
 

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,268
Location
Penngrove, California
Interesting that you are saying the ground caused it.
Because GFCI's can be used on a two wire system without a ground.

GFCIs look for equal current on the hot and neutral, within 5ma of one another.

In a typical three wire receptacle, if the hot lead touches the ground, than there is a short, and most likely the breaker will trip.

If the ground wire touches neutral, than the ground wire is carrying part of the current that should all be on the neutral. This causes the GFCI to trip.

You are correct that a GFCI does not need to have a ground, since as stated, it really just looks to be sure there is equal current on hot and neutral.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,243
Location
SE MI
Interesting that you are saying the ground caused it.
Because GFCI's can be used on a two wire system without a ground.

CONCUR and have done it in an older house. (This is safer than one of those 3-to-2 adapters which is not properly grounded.)

In theory, GFCI only looks at current in the HOT and NEUTRAL conductors. Ground is ignored.

Intermittents, even on the ground ... who know what could happen !
 

tac

Well-known member
Joined
Sep 2, 2015
Messages
69
Location
Colleyville Texas
GFCIs look for equal current on the hot and neutral, within 5ma of one another.

In a typical three wire receptacle, if the hot lead touches the ground, than there is a short, and most likely the breaker will trip.

If the ground wire touches neutral, than the ground wire is carrying part of the current that should all be on the neutral. This causes the GFCI to trip.

You are correct that a GFCI does not need to have a ground, since as stated, it really just looks to be sure there is equal current on hot and neutral.

I agree :thumbup:
 
OP
M

machsnell

Well-known member
Joined
Jun 12, 2010
Messages
942
Location
Northern Virginia
alright so i thought i had this figured out.

i narrowed it down to one of my outlets that i though was the problem because the grounds werent tied together. then you all told me ground didnt matter.

when i disconnect outlet 4 and separate the hots and neutrals (left ground tied together) the gfi stays on.

This outlet has one line in and two lines out. so it goes to one outlet below and continues along the wall to 3 more outlets.

when i connected the outlet it tripped.

i disconncted the next outlet in line and it still stays tripped.

i disconnected 5 outlet from screws that had the pigtail hot and pigtail neutral and the pigtail ground connected as well as the lower set of screws which had the outlet below. and it tripped.

i hope i explained this well enough to follow.

what do i do next? i am totally confused.
 

Attachments

  • outlet 5.jpg
    outlet 5.jpg
    141.1 KB · Views: 15
OP
M

machsnell

Well-known member
Joined
Jun 12, 2010
Messages
942
Location
Northern Virginia
the only other possibility? is one neutral had a nick in the insulation. it is the one with the electrical tape wrapped around it. I will put white on there so no one gets confused and thinks its a hot i just didnt have any at the moment.

the wire didnt look damaged it looked like my employee was careless stripping the insulation on the romex.

would this cause it to trip?
 

checkthisout

Well-known member
Joined
Sep 5, 2008
Messages
5,232
when i connected the outlet it tripped..

No gonna be a bit of a ***** here...don't mind my prickedness and no you're not explaining it will enough to follow.

Do 1 thing at a time. It's stupid simple. Don't make it complicated.

At your current outlet, as long you just have incoming power hooked up it's ok, right?

Ok, if you have two wires going out, which wire going out causes it to fail to reset?

Ok, now on the loop that fails do the same thing. Go down and disconnect the OUTGOING wires from each outlet and inspect the wiring until the GFCI will reset.
 

checkthisout

Well-known member
Joined
Sep 5, 2008
Messages
5,232
the only other possibility? is one neutral had a nick in the insulation. it is the one with the electrical tape wrapped around it. I will put white on there so no one gets confused and thinks its a hot i just didnt have any at the moment.

the wire didnt look damaged it looked like my employee was careless stripping the insulation on the romex.

would this cause it to trip?

The neutral touching the ground, or the hot touching a neutral in a downstream outlet will cause an upstream GFCI to trip.
 
OP
M

machsnell

Well-known member
Joined
Jun 12, 2010
Messages
942
Location
Northern Virginia
prickness i am good with.

and i feel like a numbnut.

i was confused because i had one outlet out of sequence on the ceiling that was the next in line after outlet 5" and so when i checked what i thought was outlet 6 i was checking outlet 7 and as soon as i figured it out sure enough...

the ground was hitting the neutral just as previous posters had said. you can see the green plastic on the ground that scraped the neutral screw if you look close

doh.....

thanks
 

Attachments

  • outlet 6.jpg
    outlet 6.jpg
    134.3 KB · Views: 20

checkthisout

Well-known member
Joined
Sep 5, 2008
Messages
5,232
prickness i am good with.

and i feel like a numbnut.

i was confused because i had one outlet out of sequence on the ceiling that was the next in line after outlet 5" and so when i checked what i thought was outlet 6 i was checking outlet 7 and as soon as i figured it out sure enough...

the ground was hitting the neutral just as previous posters had said. you can see the green plastic on the ground that scraped the neutral screw if you look close

doh.....

thanks

Neatly accordioning (I made up a word!) wires into a box is an art I have yet to master.
 