andyvh1959
Well-known member
I just got the attached document from the Green Bay electrical inspector, after he reviewed my garage build last Friday. For me, I need to install a 2nd ground rod, no big deal for that, plus it matches NEC. All outlets must be GFIC, which I assume the 1st outlet in a run feeding other downline outlets meets that. Any outlet alone on a circuit from other GFIC must itself be a GFIC. NM cable must be stapled within 12" of an outlet box. On my build I have the outlet boxes recessed into wall, with the NM cable routed through holes drilled in the 2x6 wall studs. I positioned the holes for the wires about 6" above the boxes. But the NM cable from one box spans 16" to the next stud, and the NM cable goes through holes in the next three studs until getting to the next box 48" away. So at most I can staple the NM cable 6" above the box before it goes through the next three studs. I think that meets the intent of the 12" staple.