I'm also in Fairfax County - and had the same issue years ago when I built my detached garage. Randy Bowman was my inspector and a knowledgeable, helpful sort. While, they do not require a ground rod/UFER gnd for a sub panel fed with a 4-wire system,...
Either you misunderstood him, or he's not knowledgeable. Judging by other comments about that county, I'd say the latter.
The number of wires feeding a subpanel has
NOTHING to do with whether a GES/electrodes are required.
A subpanel in the same structure as the main service panel or primary subpanel does
NOT require any electrodes whatsoever. Again, # of wires doesn't matter.
A subpanel in a detached structure has ALWAYS required a GES/electrodes, regardless of number of wires in the feeder.
....if you install one, its OK. In my case, I installed both gnd rods and a UFER system also connected to the rebar mesh under the slab.
The UFER/CEE is far superior and there is likely no benefit to installing rods as a supplemental to the CEE
Excellent general rule.
UFER actually work really well. I have plastic underslab so used a ground rod. Electrician insisted burying it sideways in the trench. I used four wire for the well house. Have another at pole from former panel.
What about noise from ground loops with multiple rods? They must be at different potentials right?
There is no such thing as noise from ground loops between rods. Where did you hear about this?
Ground rods are for suppressing lightning. No amount of fault current flows on ground rods.