Ground Wire Between Panel and Transfer Switch

mobiledynamics

Well-known member
Joined
Mar 14, 2010
Messages
5,077
Location
Gotham City
Do I need to run a Ground Wire Between my Transfer Switch and Main Panel

Main Panel - Flex Conduit to Transfer Switch.

Transfer Switch has the following wires run to the Panel

Neutral
Ground
Common Wire
Branch Wire

Is the metal connection between the 2 panels sufficient enough ?
All my ~home runs~ don't have ground (BX land, all AC wire to my main panel).

If so, do I install the ground to the neutral bar ? I don't have a ground bar in my panel
 
Last edited:
To avoid these ads, REGISTER NOW!

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
Need more info on the transfer switch, does it have a main breaker or is it just a transfer switch. By what you posted you have a ground from panel to transfer switch so why would you need another.
 
To avoid these ads, REGISTER NOW!

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
Your neutral should be bonded in the main panel so you can just put it on the neutral bar. Your transfer switch is technically a small sub panel but really it isn't because the neutral going to the panel is only for when the gen is hooked up and running. Under normal operation the nuetral in the main is your neutral for the branch circuits, and each breaker in the transfer switch is like a mini interlock for each one.
 