Grounding receptacles and switches

Junkman

Well-known member
Joined
Dec 18, 2006
Messages
6,639
Location
Northeastern CT
If you are using a metal box, and have attached the ground wire to the back of the metal box with a dedicated ground screw, is it necessary to put a ground wire onto the receptacle and / or the switch that is screwed to that metal box? To me, it is redundant, and when I wired the garage in 1985, the person that helped me (licensed electrician), said that it wasn't necessary. I will be doing some other work in the garage, and if that needs to be corrected, I might as well do it now. thanks
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,038
Location
Modesto, CA
Depends on the device and whether its self grounding or not.

Check the device and see if the yoke is connected to the ground screw.
 

LutzTD

Well-known member
Joined
Dec 31, 2011
Messages
3,673
Location
Lutz, Florida
I would pigtail to the ground on the switch/outlet, the screw tab is a casual connection and could get dirty or corroded easier than a firm connection
 
OP
J

Junkman

Well-known member
Joined
Dec 18, 2006
Messages
6,639
Location
Northeastern CT
The receptacles are 20 amp, and all the wiring is 12 gauge. Can I put a 14 gauge pigtail onto the grounding bundle and put that to the receptacle? It will be a lot easier than fighting 12 gauge wire. thanks
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,038
Location
Modesto, CA
The receptacles are 20 amp, and all the wiring is 12 gauge. Can I put a 14 gauge pigtail onto the grounding bundle and put that to the receptacle? It will be a lot easier than fighting 12 gauge wire. thanks

Why are you using 20a outlets?

What size breaker feeds this? If 20a, then no u cant use #14 for the grounds...
 
OP
J

Junkman

Well-known member
Joined
Dec 18, 2006
Messages
6,639
Location
Northeastern CT
Everything in the home was wired with 12 gauge, and the breakers are all 20 amp, except for those that are for the stove, air conditioner, etc..
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,038
Location
Modesto, CA
Everything in the home was wired with 12 gauge, and the breakers are all 20 amp, except for those that are for the stove, air conditioner, etc..

U can use 15a receptacles on 20a circuits as long as there is more than 1 outlet on the circuit.

Very hard to find any tool these days with a 20a plug on the cord..
 
To avoid these ads, REGISTER NOW!

Marctrees

Well-known member
Joined
Mar 5, 2015
Messages
6,265
Location
TX/LA border - Toledo Bend
I think Junkman is misspeaking... means a 20 a breaker, rather than actual 20 a recepts.

Pretty odd to have 20 a recepts all over a home.

Never seen that.

Pretty sure he meant he has 15a recepts, on 20a ckts,or 15a, which is most common and normal.


Wylie sed - "Depends on the device and whether its self grounding or not.

Check the device and see if the yoke is connected to the ground screw."

Ya, but whats the current code on differentiating between bearing like on a mud ring, rather than like an "industrial cover"?

On surface work, open boxes.... I used to of course pigtail when using ind cover, but not on mudring, whether or not the grounded screw retained yokes.

Was I wrong?

Code is virtually always logical common sense.

Marc
 
Last edited:

EOC_Jason

Well-known member
Joined
Jun 25, 2012
Messages
11,388
Location
Bentonville, AR
If they have this little tab, then they will be grounded to the metal box and no extra ground wire is required to the typical ground screw.
 

Attachments

  • maxresdefault.jpg
    maxresdefault.jpg
    64.9 KB · Views: 34

6PTsocket

Well-known member
Joined
Mar 12, 2014
Messages
4,593
I would pigtail to the ground on the switch/outlet, the screw tab is a casual connection and could get dirty or corroded easier than a firm connection
That has always been a concern with me. Often the receptacle is loosely screwed in to be even with the sheet rock. I feel safer carrying the ground to the recptacle with a ground wire.

Sent from my SM-G900V using Tapatalk
 

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
I always run a wire to the receptacle -- they make a pigtailed wire nit that would great with the large plastic boxes i always use.
 

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,730
Location
SE Michigan
I ground the (metallic) box and the wiring device (switch, outlet) no matter what. I keep a larger size of wire nut as the grounds always end up with more conductors inside of them.

That said I just do wiring jobs for myself and am not bound by the time = money conundrum.
 

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
That has always been a concern with me. Often the receptacle is loosely screwed in to be even with the sheet rock. I feel safer carrying the ground to the recptacle with a ground wire.
Totally agree.
I ground the (metallic) box and the wiring device (switch, outlet) no matter what. I keep a larger size of wire nut as the grounds always end up with more conductors inside of them.

That said I just do wiring jobs for myself and am not bound by the time = money conundrum.

If you guys will pull out 1 foot of wire when pulling you can cut the ground wire long and wrap it around the box screw and have enough for the device same as your current carrying conductors. If you have the circuit passing through that box you can use the green wire nut with the hole in the end to save one additional wire used in the pigtail.

Takes not a moment longer to do this.
 