pattenp
Well-known member
Well.. I'm down for the count on this one. Time to move on.
Oh... shoot, I said I was moving on.Not intending to kick this too much further down the road but
>Technically because the garage is attached to the house via a carport it’s >considered one structure
Who makes that determination - because local to me, this is not true. I was going to do this to get around boundary issues and the city does not recognize this "trick" as making the two one structure. Other places do, which is why I wanted to do it.
I also think to clarify things that 4 wires to a structure with a ground rod/UFER/whatever that also has no other metallic connection to the main structure will not be in danger of a ground loop because you'd have (per NEC) to have 4 wires, with that ground system tied to the grounded wire from the main panel. Which (ground loop) is what I think Speedy was avoiding saying out loud. I also read where Speedy says "3 or 4 wire" which is not in 2008 up NEC as I read it and has been discussed many times here - only 4 allowed now. Maybe on a farm, coming from the service drop?
Sic: "On unattached structure yes u can run three wires or four but u still have to grd. rods either way."
Ground loops have nothing to do with AC wiring. That is an electronics thing where loops can cause interference, etc.Not intending to kick this too much further down the road but
>Technically because the garage is attached to the house via a carport it’s >considered one structure
Who makes that determination - because local to me, this is not true. I was going to do this to get around boundary issues and the city does not recognize this "trick" as making the two one structure. Other places do, which is why I wanted to do it.
I also think to clarify things that 4 wires to a structure with a ground rod/UFER/whatever that also has no other metallic connection to the main structure will not be in danger of a ground loop because you'd have (per NEC) to have 4 wires, with that ground system tied to the grounded wire from the main panel. Which (ground loop) is what I think Speedy was avoiding saying out loud. I also read where Speedy says "3 or 4 wire" which is not in 2008 up NEC as I read it and has been discussed many times here - only 4 allowed now. Maybe on a farm, coming from the service drop?
Sic: "On unattached structure yes u can run three wires or four but u still have to grd. rods either way."
Not in this thread, or any other. If I wrote that elsewhere it was with regard to existing installations only.I also read where Speedy says "3 or 4 wire" which is not in 2008 up NEC as I read it and has been discussed many times here - only 4 allowed now. Maybe on a farm, coming from the service drop?
Sic: "On unattached structure yes u can run three wires or four but u still have to grd. rods either way."
Are you referring to this:I also read where Speedy says "3 or 4 wire" which is not in 2008 up NEC as I read it and has been discussed many times here - only 4 allowed now.
I'm sorry, but this is COMPLETELY wrong.
A ground rod does NOT derive a ground such as an equipment ground. A grounding electrode has NOTHING to do with the equipment ground in so far as clearing faults or tripping breakers.
A grounding electrode was always required at a detached structure served by a feeder, regardless if it was an older (allowable under certain circumstances) 3-wire feeder or the typical 4-wire feeder. Again, this feeder had NO relationship to the grounding electrode.
That would be the local Authority, if not the same structure a different set of rules will apply. The OP should check this.Not intending to kick this too much further down the road but
>Technically because the garage is attached to the house via a carport it’s >considered one structure
Who makes that determination -
Your definitely not in the trade. Your wrong I have said what issue is and yes, your wrong. The reason you don't understand is bc you don't have any background about electrical.
I'm not in the trade, huh?
I guess I lied when I put my occupation in my profile?
The bottom line is, you've been on this site for all of 5 mins and you don't know anyone on here or what their background is.
This was very helpful. Thx to whomever posted.
http://www.selfhelpandmore.com/home...o-dwellings/wiring-a-detached-garage-2002.php
Well they kind of do.Ground loops have nothing to do with AC wiring. That is an electronics thing where loops can cause interference, etc.
Some folks like to apply the term, but in real world construction electric the term is simply not used.
I won't even bring up R-56 Grounding at communications site. Everything is grounded and bonded together that is metal. From the boxes to the A/C grates , fence posts, doors to the frames all grounded.
Mac