I am finding a ton of threads but in my old age and slight retardation not finding what I want.

I have this heater

21733.jpg


It is wired directly to my panel.
21734.jpg
21735.jpg


The heater has a built in thermostat of sorts that's basically a dial 1-5. But a) it is way to high to reach and b) the only way to stop it completely is kill the breakers.


I'd like a thermostat down by the panel that I can dial in a temp and shut off wirelessly.


From what I can gather I need a transformer to step the power down, a thermostat and a contactor that cycles power.


And I missing anything?


Any thoughts on how to wire it?
 
To avoid these ads, REGISTER NOW!

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,939
Location
Fargo, ND
I'd like a thermostat down by the panel that I can dial in a temp and shut off wirelessly.


From what I can gather I need a transformer to step the power down, a thermostat and a contactor that cycles power.


And I missing anything?


Any thoughts on how to wire it?

I would like to see a wiring diagram for the heater. There might be something that can be wired into the control side and use a 24 volt thermostat, or even a line voltage thermostat that just needs to handle a amp or two on the control side.

Is there a wiring diagram in the unit or an manual that came with the unit you can share?
 
OP
D

Dusten

Well-known member
Joined
May 19, 2015
Messages
847
Location
Camano Island
I would like to see a wiring diagram for the heater. There might be something that can be wired into the control side and use a 24 volt thermostat, or even a line voltage thermostat that just needs to handle a amp or two on the control side.

Is there a wiring diagram in the unit or an manual that came with the unit you can share?
Not a manual, as I bought the house with it installed. I can crawl up there look for a wiring diagram maybe tomorrow.

But according the heater manufacturers paperwork there is a control block I can wire a thermostat into and no external relay is needed.

If it’s 24V control
Use standard HVAC thermostat
Wire directly to T1/T2
Don’t put a thermostat inline with L1/L2
You control it through the control terminals only
 
OP
D

Dusten

Well-known member
Joined
May 19, 2015
Messages
847
Location
Camano Island
I would like to see a wiring diagram for the heater. There might be something that can be wired into the control side and use a 24 volt thermostat, or even a line voltage thermostat that just needs to handle a amp or two on the control side.

Is there a wiring diagram in the unit or an manual that came with the unit you can share?

From the unit

I should be able to interrupt t1 with a 24v tstat and be ok.

20260415_210601.jpg20260415_210650.jpg
 
OP
D

Dusten

Well-known member
Joined
May 19, 2015
Messages
847
Location
Camano Island

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,258
Location
NJ
That schematic is for a 3 phase unit. I find hard to believe mfr put the wrong one in it.

Im thinking someone field modified this.

Need pics of the upper hardware cut off in the Pic. There may not be any transformer.

The black tstat in lower right of Pic is your tstat. Those 2 wires to it are what needs to be interrupted with an external tstat.

External tstat needs to be 240v. 15/20a rating would be sufficient. (assuming no xformer present.) Measure the voltage across the 2 tstat terminals when unit is not running.
 
OP
D

Dusten

Well-known member
Joined
May 19, 2015
Messages
847
Location
Camano Island
That schematic is for a 3 phase unit. I find hard to believe mfr put the wrong one in it.

Im thinking someone field modified this.

Need pics of the upper hardware cut off in the Pic. There may not be any transformer.

The black tstat in lower right of Pic is your tstat. Those 2 wires to it are what needs to be interrupted with an external tstat.

External tstat needs to be 240v. 15/20a rating would be sufficient. (assuming no xformer present.) Measure the voltage across the 2 tstat terminals when unit is not running.

ITs weird because the factory literature states it has a 24v relay, and that an external thermostat is to be connected to the heater control terminal block.

I'll crawl up there again and get a better picture and some power readings.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,876
Location
NW Iowa
Looks like there is a contactor but no transformer that I see. The contactor handles the heavy current. You still need a 240v stat, but it only has to power the contactor coil less than an amp. A regular 22A rated line voltage stat will be the easiest choice.
 

BurtEggley

Well-known member
Joined
Oct 8, 2024
Messages
912
>>> the manufacturer appears to already have approved package solutions to do what you want, other than maybe the wifi features. Call their tech support with your model number, serial number and tell them it is wired for single phase. Ask them for a solution or a referral to someone who installs those features.
 
Last edited:
OP
D

Dusten

Well-known member
Joined
May 19, 2015
Messages
847
Location
Camano Island
>>> the manufacturer appears to already have approved package solutions to do what you want, other than maybe the wifi features. Call their tech support with your model number, serial number and tell them it is wired for single phase. Ask them for a solution or a referral to someone who installs those features.
My concern there is that they don't sell this anymore.
That is not what I see!
Ya the drawing shows it, but it's now how it's installed. Bummer. Thought I had an easy out.

20260416_194856.jpg20260416_194743.jpg20260416_194737.jpg20260416_194720.jpg
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,258
Location
NJ
This is what you have for the tstat circuit. (I didn't trace out the rest, but know it's not 3 phase.)

1776395791154.png


It's a simple replacement of the local tstat on the unit with a 240 volt single pole tstat at floor level.
Use 14 gauge nm-b between heater and tstat. Fuses protect the #14.

ETA:
Or you could put the new floor tstat in series with the local tstat. The local tstat would be set to 9/10 on the dial and the real temp setting is managed by the setting on the floor tstat.

The local tstat has a "0" setting to shut off heater if desired. This could be the reason to keep it in the circuit.
 
Last edited:

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,939
Location
Fargo, ND
This is what you have for the tstat circuit. (I didn't trace out the rest, but know it's not 3 phase.)

1776395791154.png


It's a simple replacement of the local tstat on the unit with a 240 volt single pole tstat at floor level.
Use 14 gauge nm-b between heater and tstat. Fuses protect the #14.

ETA:
Or you could put the new floor tstat in series with the local tstat. The local tstat would be set to 9/10 on the dial and the real temp setting is managed by the setting on the floor tstat.

The local tstat has a "0" setting to shut off heater if desired. This could be the reason to keep it in the circuit.
I agree that would be a simple way out of you don't mind the limited choices of a line voltage thermostat.

If the OP was to go this way this is on the control side and the only load if the contactor, probably way less than 1/2 of an amp, so pretty much any line voltage 'stat rated for 240 volt will work.

The relay set up I mentioned earlier would work with pretty much any 24V 'stat, even a programmable, or and WiFi enabled 'stat.
 
To avoid these ads, REGISTER NOW!

BurtEggley

Well-known member
Joined
Oct 8, 2024
Messages
912
My concern there is that they don't sell this anymore.

Really? I downloaded a PDF about 30 seconds ago showing a 240V single phase version, OASU10000AM-T2. The T2 means that it comes with a built in thermostat. Your sticker shows that yours was also built at the factory as a 240V single phase unit with a thermostat, and not a 3-phase 208V unit. The phone number on your sticker is still their customer service number.


heater.jpg
 
OP
D

Dusten

Well-known member
Joined
May 19, 2015
Messages
847
Location
Camano Island
Really? I downloaded a PDF about 30 seconds ago showing a 240V single phase version, OASU10000AM-T2. The T2 means that it comes with a built in thermostat. Your sticker shows that yours was also built at the factory as a 240V single phase unit with a thermostat, and not a 3-phase 208V unit. The phone number on your sticker is still their customer service number.


heater.jpg
I know how to read the sticker, thats why i posted it. Its also no longer for sale. Just because limited documentation exists, doesn't mean a company provides technical support anymore.
 
OP
D

Dusten

Well-known member
Joined
May 19, 2015
Messages
847
Location
Camano Island
I agree that would be a simple way out of you don't mind the limited choices of a line voltage thermostat.

If the OP was to go this way this is on the control side and the only load if the contactor, probably way less than 1/2 of an amp, so pretty much any line voltage 'stat rated for 240 volt will work.

The relay set up I mentioned earlier would work with pretty much any 24V 'stat, even a programmable, or and WiFi enabled 'stat.

you can get wifi capable line voltage t-stats. Something like this seems to fit the bill


or

 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,258
Location
NJ
I know how to read the sticker, thats why i posted it. Its also no longer for sale. Just because limited documentation exists, doesn't mean a company provides technical support anymore.
Or sells the optional accessories.

Part numbers of those options would be needed for a NOS search.

Or just move on with your own hardware choice as you just posted.
 

jlv03

Well-known member
Joined
Jan 19, 2020
Messages
353
Location
SE IA
you can get wifi capable line voltage t-stats. Something like this seems to fit the bill


or


Anything with WiFi will need continuous power. On 24V thermostats that's why you always see posts about running a "C" common wire to complete the circuit for continuous power.

In this case, the line voltage thermostats with WiFi will need either a neutral (if 120VAC) or the opposite leg (if 240VAC).

For your heater, we can still use the thermostat T1/T2 connections, but you'll need to pull off the opposite leg (L2). You'll need to use a 3 conductor cable (14-3 Romex for example).
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,954
I know how to read the sticker, thats why i posted it. Its also no longer for sale. Just because limited documentation exists, doesn't mean a company provides technical support anymore.
Have you called and asked? while it's entirely possible they don't support it, it's also possible they do, or can direct you to someone who might have the parts you wnat. Worst that happens is you waste a little time.
 
OP
D

Dusten

Well-known member
Joined
May 19, 2015
Messages
847
Location
Camano Island
Have you called and asked? while it's entirely possible they don't support it, it's also possible they do, or can direct you to someone who might have the parts you wnat. Worst that happens is you waste a little time.
I haven't. I'm generally asleep during the business day and it's not important enough to stay up until they open
 

BurtEggley

Well-known member
Joined
Oct 8, 2024
Messages
912
Here, don't worrry about it - took me all of 45 seconds to do this.

"Good morning Burt,

The thermostat built-in thermostat is: KIT-OAS-T.

If you need to order, you can by Gordon Electric in Chicago. Gordon accepts customer orders.

Gordon Electric Supply Inc. (Mokena) in Illinois. Gordon is dealing with web end-user. Phone: 708-479-4660.


Thank you. Regards"
Patricia Giasson
Ouellet Canada
Technicienne au service à la clientèle
Customer Service Technician
T.418‑247‑3947 ext. 341
1 800 463‑7043
 
Last edited:

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
20,239
Location
Northern Virginia
Here, don't worrry about it - took me all of 45 seconds to do this.

Good morning Burt,



The thermostat built-in thermostat is: KIT-OAS-T.

If you need to order, you can by Gordon Electric in Chicago. Gordon accepts customer orders.

Gordon Electric Supply Inc. (Mokena) in Illinois. Gordon is dealing with web end-user. Phone: 708-479-4660.


Thank you. Regards



Patricia Giasson
Ouellet Canada
Technicienne au service à la clientèle
Customer Service Technician
T.418‑247‑3947 ext. 341
1 800 463‑7043
And you can buy it on-line, off peak time for your work schedule.
 

jlv03

Well-known member
Joined
Jan 19, 2020
Messages
353
Location
SE IA
The 24V transformer, like the summer fan switch, internal thermostat, and 24V relay, are all marked with an * to denote they are options to the standard 3 phase design.
 

BurtEggley

Well-known member
Joined
Oct 8, 2024
Messages
912
the factory said "kit" when they gave the part number. That might imply that all the parts needed are in the kit. It looks to me like the factory thermostat takes the place of the onboard one, but goes at the remote location to make it easier to turn on and off.

The factory RT kit, with a relay and 24V transformer looks to use a standard hvac 24V thermostat.

It is probably moot because he sleeps days and in his words not worth the time to follow up.
 
Last edited:
OP
D

Dusten

Well-known member
Joined
May 19, 2015
Messages
847
Location
Camano Island
the factory said "kit" when they gave the part number. That might imply that all the parts needed are in the kit. It looks to me like the factory thermostat takes the place of the onboard one, but goes at the remote location to make it easier to turn on and off.

The factory RT kit, with a relay and 24V transformer looks to use a standard hvac 24V thermostat.

It is probably moot because he sleeps days and in his words not worth the time to follow up.

What follow up? An easy solution has been presented here that is available at my local hardware store. There is zero to be gained from calling the manufacturer. Between work and my kids I'm not going to devote any time to call a manufacturer about a discontinued product to ask a question that's already been solved.

The heater was installed a decade ago by a man who's dead(previous homeowner) so if a kit was purchased it's gone. And is a kit still exists from the manufacturer I have no need nor desire to buy it vs a readily available option that doesn't require shipping.

I stopped replying here because no further replies are needed. But since you want to judge my lifestyle I guess we're back.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,258
Location
NJ
What follow up? An easy solution has been presented here that is available at my local hardware store. There is zero to be gained from calling the manufacturer. Between work and my kids I'm not going to devote any time to call a manufacturer about a discontinued product to ask a question that's already been solved.

The heater was installed a decade ago by a man who's dead(previous homeowner) so if a kit was purchased it's gone. And is a kit still exists from the manufacturer I have no need nor desire to buy it vs a readily available option that doesn't require shipping.

I stopped replying here because no further replies are needed. But since you want to judge my lifestyle I guess we're back.