I am adding a 100amp subpanel in my garage.
Square-D subpanel going in the garage...keeping ground and neutral bars separate in that panel. I have 2" conduit run between the garage panel and into the house, all the way to the main panel in the house. It is buried ~20"-24" deep. Two ground rods driven near the garage, roughly 10' apart and bonded with a #6 copper run into the subpanel.
I have 4 runs of #2 THWN, one re-marked red, one re-marked white, one left black and one green.
100-amp breaker in the main box to connect it all together.
Have I overlooked anything?
Square-D subpanel going in the garage...keeping ground and neutral bars separate in that panel. I have 2" conduit run between the garage panel and into the house, all the way to the main panel in the house. It is buried ~20"-24" deep. Two ground rods driven near the garage, roughly 10' apart and bonded with a #6 copper run into the subpanel.
I have 4 runs of #2 THWN, one re-marked red, one re-marked white, one left black and one green.
100-amp breaker in the main box to connect it all together.
Have I overlooked anything?