Help! ISO correct breaker cover/door.

TimTaylor75

Well-known member
Joined
Sep 15, 2010
Messages
412
Location
Lecanto, Florida
Good morning fellow GJ brethren. I am trying to determine the correct cover for my breaker as the current one is far from being accurate. I’m pretty much ignorant to all things electrical, so any guidance is greatly appreciated!

Dimensions are 32” x 14”

Thanks in advance!
 

Attachments

  • 3836ED39-46DF-4808-837E-43A4DDE56DF9.jpeg
    3836ED39-46DF-4808-837E-43A4DDE56DF9.jpeg
    421.8 KB · Views: 66
  • 51078E87-570C-4275-B856-DF1CA4E0BA88.jpeg
    51078E87-570C-4275-B856-DF1CA4E0BA88.jpeg
    285.8 KB · Views: 66
To avoid these ads, REGISTER NOW!

Chuckster in NJ

Well-known member
Joined
Jan 26, 2010
Messages
2,401
Location
Hunterdon County NJ
It’s a SIEMENS panel (appears to be in good condition) and most likely the General Electric panels are "roughly" the same size and MAY fit….….. However some modification may be necessary.
There "should be" a sticker on the side panels or stamped "tattoo" inside the panel that indicates the model number of the panel that would help you find the cover on a internet search.
This panel is vintage mid 1980’s to late 1990’s.……. Good luck finding a cover!

BTW! At worst you will have to do a panel change and given the age of the breakers it would be an "investment in the future".
 
OP
T

TimTaylor75

Well-known member
Joined
Sep 15, 2010
Messages
412
Location
Lecanto, Florida
Darn, that’s a bummer. I’m in contract to sell and trying to make it right for the inspection. Looks like I may be investing a bit before I sell. Any idea of what a box replacement would be?
 

Stuff

Well-known member
Joined
Aug 31, 2013
Messages
572
You'll need more than a cover to make it right for inspection. Wires coming in at the bottom and upper right without a connector. Wrong brand 100 amp breaker. Red wires on ground bus (isolated grounds? need marked green). White on dual pole breakers need marked black or other color. Bottom right single pole breakers have black hot but white not connected in panel. Don't see the main bonding jumper to connect the ground bars to the panel shell - if not service panel then grounds need separated from neutrals. If service then GEC missing unless it is at meter.

It would be easier for you to simply let their inspection find everything and then give them $$$$ to settle.
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,253
Location
Modesto, CA
yikes. that panel is a mess.

mixed brand of breakers (I assume it a siemens panel). The eaton BR top right is not kosher

Is this a main service panel or subpanel?

Either way, items are missing for either config

If main, as said above, no bonding screw, no GEC or water/gas bonding wire,

If sub, then neutral needs to be isolated(move EGCs over to ground bar on left), and the EGC feeder wire is missing(or i cant see it up top)....

you cant just use a dead front and or panel cover from another brand. gonna be tough to find the panel cover you need... has to be same brand and model.... needle in a haystack...

no cable clamps either
 
Last edited:

walta

Well-known member
Joined
Jan 13, 2017
Messages
2,322
Location
Dutzow Missouri
If I was the buyer I would insist on a new panel before closing.

Short of pulling a rabbit out of a hat and finding a cover from the same make and model panel you no longer have a UL listed panel assembly and a big fat code violation.

Now there is a record of this known code violation you would need to disclose this should this buyer back out.



Walt
 
To avoid these ads, REGISTER NOW!

haveissues

Well-known member
Joined
Feb 9, 2011
Messages
379
Location
Hudson Valley NY
There are some older panel covers on ebay for sale-you might get lucky. As for everything else, if your market is like ours is I wouldn't fix it.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
There are some older panel covers on ebay for sale-you might get lucky. As for everything else, if your market is like ours is I wouldn't fix it.
Be prepared for sticker shock, but in the long run would be cheaper then a panel swap if one can be found.
 

Stuff

Well-known member
Joined
Aug 31, 2013
Messages
572
You could jury-rig a panel cover but even a newbie inspector would call out some of the other issues. A current Siemens panel would be either 30" or 36" so the cover wouldn't fit your 32" but drilling a few mounting holes would at least cover things.
 