Posted this in the hearing section and not getting any notice, guess it's more of an electrical issue anyway.
Decided for my uses Electric heat was the best solution to keep my shop about freezing this winter, so I purchased a King Electric GH-2407 heater. Specs are 7.5kw/3.7kw, single phase 220v rated at 31.2a. Pulled 8/2 NM-B for the >50' run from the shop subpanel to the heater, and wired it into a 50a two pole breaker that was used by the previous owner for a TIG welder. I set up an Aube rc840t-240 switching relay/transformer so I can control the unit with a 24v thermostat.
After making all the connections, on first turning on the breaker with the relay set up, I couldn't get anything. Checked to verify power, which read 125v on each leg of the heater terminals: power isn't the issue. So I disconnected the relay and reattached the internal thermostat, to make sure the relay wasn't faulty. Turned up the thermostat and within a second of the elements turning on, the branch circuit went down, as did the main subpanel breaker (60a), along with the 60a breaker in the main panel feeding the shop. Did the same thing in the lower voltage mode as well.
Need a little direction on where to start looking next, clearly I am drawing more that the 60a of the main breaker, but why?
Decided for my uses Electric heat was the best solution to keep my shop about freezing this winter, so I purchased a King Electric GH-2407 heater. Specs are 7.5kw/3.7kw, single phase 220v rated at 31.2a. Pulled 8/2 NM-B for the >50' run from the shop subpanel to the heater, and wired it into a 50a two pole breaker that was used by the previous owner for a TIG welder. I set up an Aube rc840t-240 switching relay/transformer so I can control the unit with a 24v thermostat.
After making all the connections, on first turning on the breaker with the relay set up, I couldn't get anything. Checked to verify power, which read 125v on each leg of the heater terminals: power isn't the issue. So I disconnected the relay and reattached the internal thermostat, to make sure the relay wasn't faulty. Turned up the thermostat and within a second of the elements turning on, the branch circuit went down, as did the main subpanel breaker (60a), along with the 60a breaker in the main panel feeding the shop. Did the same thing in the lower voltage mode as well.
Need a little direction on where to start looking next, clearly I am drawing more that the 60a of the main breaker, but why?