Help with Home A/C Unit Troubleshooting

Larey

Well-known member
Joined
Sep 10, 2013
Messages
135
Location
Fussa, Japan
I have a Goodman GSZ130361 unit and the handler is upstairs in the attic, and the condenser is outside in the backyard. (disclaimer we did just recently have a power surge that effected my kids WII U.
So short story I got home today and it was hot in the house, so I knew something was wrong. Fan was on the "on" selection which I never move from auto. Luke warm air barely blowing out but the unit was running. So with previous events occurring I knew to check the outside unit to see if it was running and it was not. Checked all the breakers and they are all good. Open up the side and the circuit board and contactor are available to me access.

If I remember right I have burned up a few ants before in the contactor but am not exactly sure on how to test it, except when I push the middle of it down it turns on the unit and the air gets cold. So I get the circuit board loose and inspect the back and it is discolored at two resistors that are the same in coloring. I remember some of my electronics class from a awhile ago and look up the resistance and they are bad compared to the two next to them with the same coloring.

So I am not real sure on which one to deal with first as I am not real good with schematics. Contactor is 40 bucks and circuit card is about 70. Oh and to add to this we move out in a month to a new home, but this one will be rented out.

Thanks for the help in advance,

Larey
 
To avoid these ads, REGISTER NOW!
OP
L

Larey

Well-known member
Joined
Sep 10, 2013
Messages
135
Location
Fussa, Japan
Tells me to discharge it thru a 20-30 ohm resistor prior to testing dont have one available at the moment.
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
That's your capacitor,Can you post a picture of the contactor?
The simplest way to check the capacitor with out removing the wires is to look at the top of capacitor under where the wires connect.
The top should be flat under the connectors,if its bulged out then chances are its bad.
depending on your contactor you should be able to test it by pushing it in with an insulated screwdriver,need a picture though.;)
 
OP
L

Larey

Well-known member
Joined
Sep 10, 2013
Messages
135
Location
Fussa, Japan
I have tested the contactor with a meter lead by pushing it in, I will take better pictures in the morning, so hopefully that is it...but what about the two resistors?
 

Rockhead261

Well-known member
Joined
Aug 28, 2013
Messages
1,911
Location
10509
That unit model number looks like a heatpump, correct?

Push in the contactor. Does the unit run? If so, make sure you have 24vac going to the outdoor unit. If you do, replace the board.
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
It's not the run cap. You already said that if you manually push the contactor in, the compressor and fan run. The circuit board has burned resistors, it's probably you bad part.

Tommy
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
I have tested the contactor with a meter lead by pushing it in, I will take better pictures in the morning, so hopefully that is it...but what about the two resistors?

So what did it show when you checked it with the meter,Are you getting 24v to the coil?
Are you getting 240v to the contactor,are you getting 240v out the other side of contactor when you push it in?;)
 
To avoid these ads, REGISTER NOW!

bazar01

Well-known member
Joined
Jan 30, 2009
Messages
326
Location
Leesburg, GA
I think he just used the meter lead to manually engage/push on the contactor contacts.

His unit has a control issue.
 

acmikee

Well-known member
Joined
Feb 2, 2005
Messages
301
Location
olympia, wa
so you pushed in the contactor and the compressor ran and the fan ran=cap is good
now check for 24 volts at the Y to C terminal or cycle the fan on at the Tstat=fan cycles you have 24V.
look at the wiring diagram at the condensing unit and look for a low pressure or loss of charge control....connect those wires together if compressor starts you are off on those safeties
 
OP
L

Larey

Well-known member
Joined
Sep 10, 2013
Messages
135
Location
Fussa, Japan
Acmikee so with y and c terminal I have about 26 v. Now when I jumper my low pressure switch on the board outside it works so I assume I have a leak or low pressure.
 
OP
L

Larey

Well-known member
Joined
Sep 10, 2013
Messages
135
Location
Fussa, Japan
As you can see I have an oily residue above the warning label.
 

Attachments

  • uploadfromtaptalk1417106232746.jpg
    uploadfromtaptalk1417106232746.jpg
    141.6 KB · Views: 21

acmikee

Well-known member
Joined
Feb 2, 2005
Messages
301
Location
olympia, wa
yes your low on charge or flat. remove the service cap and press in the valve core (just like a tire)if you hear a hiss then you have some refrigerant then you can leak check it. remove the screws to access the coil then soap the area around the oil stain. if no hiss then the unit is flat and you need to call a service tech.
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
yes your low on charge or flat. remove the service cap and press in the valve core (just like a tire)if you hear a hiss then you have some refrigerant then you can leak check it. remove the screws to access the coil then soap the area around the oil stain. if no hiss then the unit is flat and you need to call a service tech.

X2. When the OP said when he manually pushed the compressor contactor in it blew cold air I figured most likely culprit was the burned control board...

Tommy
 
OP
L

Larey

Well-known member
Joined
Sep 10, 2013
Messages
135
Location
Fussa, Japan
Well the unit was empty, and it ended up being a pin hole at the top of the coil right before the fins. Tech fixed it and serviced for 274.
 