I am going to start by listing what I have and then will get to the issue at hand.
40X60X16 pole building
2 inch formular 250 around perimeter
2 inch crete-heat panels under slab
1/2 inch pex, 12 inch on center
2 zones
6 loops 295 ft long zone 1
3 loops 220 ft long zone 2
2 grundfos UPS15-58FC pumps, speed 2 for zone 1, speed 1 for zone 2
Nortitz NRC661 tankless water heater natural gas
bluefin stainless manifolds, 3 and 6 loop
Axel SP-82 2 zone pump controller
2 air and floor thermostats, currently set to control slab temp
Air eliminator
Expansion tank 2 gallon
fill and drain valve
All plumbing is 3/4 copper with the exception of the pex loops
I have a static system pressure of 15psi and as far as i can tell i have purged all air
Zone 1 is approx 1700 sqft
Zone 2 is approx 700 sqft, 20x35
Both zones are currently in the same air space, and not thermally separated in the slab. I did this for the future if I decide to drop a wall. I am aware i will have to cut out a strip of concrete and add insulation to thermally isolate the 2 zones, but for the time being, the thermostats will be set the same and they should still work.
I currently have no insulation, but the plan is to have R19 walls and R30 ceiling minimums, once I am done wiring and plumbing everything else I can have the insulation done.
My calculations are based on coldest outside temp of 10*, inside temp of 65*, 2400 sqft, puts me between 39600 and 79200 BTU. I have found 2 methods to calculated GPM requirement and head loss, these are the numbers from the worst case of the 2. Zone 1 requires 5.6 GPM with head loss around 10.4 and 2.3 GPM with a head loss of 6.2 on zone 2. With these numbers the pump curve chart shows this pump to be a fit.
My issue seems to be that the water heater doesn't see flow even though both pumps are running, I can watch the heater fire up, create heat, and after 5 or so min the burner shuts off and eventually the heater shuts off as its in standby mode. I have a transfer pump that I have connected to the fill and drain valves and a bucket that I used to bleed the air and if I run that pump and open the valves the heater will kick on as I am creating flow.
My thermostats control the pump motors only, the heater senses flow and turns itself on, or rather it is supposed to.
I am trying to get this up and running to keep the concrete at a minimum temp to just keep things from freezing until I can get the insulation done.
Anyone have any suggestions?
Thank you
Jon
40X60X16 pole building
2 inch formular 250 around perimeter
2 inch crete-heat panels under slab
1/2 inch pex, 12 inch on center
2 zones
6 loops 295 ft long zone 1
3 loops 220 ft long zone 2
2 grundfos UPS15-58FC pumps, speed 2 for zone 1, speed 1 for zone 2
Nortitz NRC661 tankless water heater natural gas
bluefin stainless manifolds, 3 and 6 loop
Axel SP-82 2 zone pump controller
2 air and floor thermostats, currently set to control slab temp
Air eliminator
Expansion tank 2 gallon
fill and drain valve
All plumbing is 3/4 copper with the exception of the pex loops
I have a static system pressure of 15psi and as far as i can tell i have purged all air
Zone 1 is approx 1700 sqft
Zone 2 is approx 700 sqft, 20x35
Both zones are currently in the same air space, and not thermally separated in the slab. I did this for the future if I decide to drop a wall. I am aware i will have to cut out a strip of concrete and add insulation to thermally isolate the 2 zones, but for the time being, the thermostats will be set the same and they should still work.
I currently have no insulation, but the plan is to have R19 walls and R30 ceiling minimums, once I am done wiring and plumbing everything else I can have the insulation done.
My calculations are based on coldest outside temp of 10*, inside temp of 65*, 2400 sqft, puts me between 39600 and 79200 BTU. I have found 2 methods to calculated GPM requirement and head loss, these are the numbers from the worst case of the 2. Zone 1 requires 5.6 GPM with head loss around 10.4 and 2.3 GPM with a head loss of 6.2 on zone 2. With these numbers the pump curve chart shows this pump to be a fit.
My issue seems to be that the water heater doesn't see flow even though both pumps are running, I can watch the heater fire up, create heat, and after 5 or so min the burner shuts off and eventually the heater shuts off as its in standby mode. I have a transfer pump that I have connected to the fill and drain valves and a bucket that I used to bleed the air and if I run that pump and open the valves the heater will kick on as I am creating flow.
My thermostats control the pump motors only, the heater senses flow and turns itself on, or rather it is supposed to.
I am trying to get this up and running to keep the concrete at a minimum temp to just keep things from freezing until I can get the insulation done.
Anyone have any suggestions?
Thank you
Jon