Help with new air compressor

gnxtc2

Well-known member
Joined
Sep 3, 2010
Messages
304
Location
New york
Install a disconnect on the outside, it is required, and hardwire the compressor to it. You must have some sort of disconnect within 50 ft and within line of sight from the panel that supplies the compressor. Being outside, you do not have line of sight, so you have to have a disconnect. A plug and receptacle is a legal disconnect, but with a 5 hp motor, it is not a good thing to use, especially since the compressor is not portable and you won't be taking it anywhere.

Charles

I still can't find the disconnect within 50' in the NEC. Would you know where it is in the NEC? You are correct on the disconnecting means within sight.

Being that the NEC loves the number "6", I would've thought that it would say "Disconnecting means within 6 feet"

Billy T.
[email protected]
 
To avoid these ads, REGISTER NOW!

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
I still can't find the disconnect within 50' in the NEC. Would you know where it is in the NEC? You are correct on the disconnecting means within sight.

Being that the NEC loves the number "6", I would've thought that it would say "Disconnecting means within 6 feet"

Billy T.
[email protected]

When the code uses the terminology "in sight from", "within sight from", or "within sight" the definition in Article 100 says that "...the specified equipment is to be visible and not more than 15m (50 ft) distant from the other."

Thus the 50 ft is implied by referring to the definition of "within sight".

Charles
 
To avoid these ads, REGISTER NOW!
OP
G

gapfast

Well-known member
Joined
Jun 19, 2011
Messages
213
Nevermind
 