High quality Square D panel board ?

Steve from Socal

Well-known member
Joined
Jan 27, 2009
Messages
3,502
Location
Hutchinson Ks.
I am looking for a good quality single phase panel and it seems that Square D has cheapened the line. What would be a good quality industrial panel MLO preferred 100-200 amp with 30-42 spaces?

Steve
 
To avoid these ads, REGISTER NOW!

ddawg16

Well-known member
Joined
Jul 11, 2008
Messages
21,005
Location
S. California
Steve....I installed (not wired yet) a SO2040M200 panel for my 2-story addition....

20 Space....40 ckts using tandum breakers...I think it's well made for the money....
 

djjsr

Well-known member
Joined
Sep 4, 2006
Messages
4,796
Location
In the cornfields
I think the regular Square D stuff is ok. I got one last year and it seems the same quality as another one I have that's 20 years old. HOWEVER, I think the Homeline Square D boxes aren't quite as good. I've looked at them and they seem a bit "light duty" in their construction. I think they still use the QO breakers.
 

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,681
Location
Maine
I think the regular Square D stuff is ok. I got one last year and it seems the same quality as another one I have that's 20 years old. HOWEVER, I think the Homeline Square D boxes aren't quite as good. I've looked at them and they seem a bit "light duty" in their construction. I think they still use the QO breakers.

Homeline do not use QO breakers.
 
OP
S

Steve from Socal

Well-known member
Joined
Jan 27, 2009
Messages
3,502
Location
Hutchinson Ks.
I would like to use QO breakers, this will be in a commercial building. It is going next to this so, I would like a quality piece.

Steve
 

Attachments

  • 018.jpg
    018.jpg
    117.9 KB · Views: 49

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
I would like to use QO breakers, this will be in a commercial building. It is going next to this so, I would like a quality piece.

Steve

Call your local Square D distributor, heck you might be able to price it on Grainger, but they make a "bolt on" QO breaker as well. Remember, with Sq D if you want nice, you're going to pay for it.

There is a difference between loadcenters(residential) and panels(everything else). When you buy a panel, you're buying a can, guts, and a trim seperately. A loadcenter has all that combined.

So if you're truly interested in buying a "commercial" panel, you're best bet would be a local distributor who can put together a complete package of all the components which will ensure they fit together properly. These packages will come with a full panel of breakers, so your supplier should ask you what type and how many you like. For instance, twenty single pole 20's, five 2 pole 40's, etc. They usually throw in breakers in for practically nothing when you buy a panelboard package, but if you try and buy them a few at a time later they will hammer you on price!

That is one reason we choose not to use Sq D, individual breaker prices are often ridiculous for commercial panels when we go to add a circuit. We'll sometimes buy a whole panel with breakers just to steal the breakers out of it, it's cheaper!?!?
 

jack stand

Well-known member
Joined
Feb 29, 2012
Messages
3,346
Location
Lakes Region Maine
I am looking for a good quality single phase panel and it seems that Square D has cheapened the line. What would be a good quality industrial panel MLO preferred 100-200 amp with 30-42 spaces?

Steve

Sq D QO line. Been makin em for years. It's nice to be able to get replacement breakers 20 years form now. HD and Lowes has (had) a 200A panel that came with a bunch of breakers, good deal. It might be larger than you need but do the math and it prolly makes sence and it's nice to have the extra space.
 
To avoid these ads, REGISTER NOW!

ishiboo

Well-known member
Joined
Oct 27, 2010
Messages
9,481
Location
Oshkosh, WI
I would like to use QO breakers, this will be in a commercial building. It is going next to this so, I would like a quality piece.

Steve

Simple, QO panel unless the project warrants a NQ.

The actual circuit breaker is the same between QO and Homeline, it's just the packaging that differs - physical dimensions, trip indicator, etc.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
whats the available fault current where you are installing the subpanel? Can you use 10Ka breakers or do you need 22ka?
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
16.6ka where? whats the interrupt rating of the breakers in that I-line?
 
OP
S

Steve from Socal

Well-known member
Joined
Jan 27, 2009
Messages
3,502
Location
Hutchinson Ks.
The breakers in the I-Line are FC and FH the lowest rating at 480 is 25Ka

The panel is going on the secondary side of a 25KVa transformer with an Iz 6.1

Steve
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Except also the QO breaker cost almost twice as much as the Homeline breaker and they aren't interchangeable.

Simple, QO panel unless the project warrants a NQ.

The actual circuit breaker is the same between QO and Homeline, it's just the packaging that differs - physical dimensions, trip indicator, etc.
 

gnxtc2

Well-known member
Joined
Sep 3, 2010
Messages
304
Location
New york
Steve....I installed (not wired yet) a SO2040M200 panel for my 2-story addition....

20 Space....40 ckts using tandum breakers...I think it's well made for the money....

Wait until you buy a QO tandem.....thieves.

I limited in using Sq D stuff, the prices are getting out of hand. I switched over to the Cutlet Hammer CH line.

Billy T.
[email protected]
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
Wait until you buy a QO tandem.....thieves.

I limited in using Sq D stuff, the prices are getting out of hand. I switched over to the Cutlet Hammer CH line.

Billy T.
[email protected]

and how do you use tandems in a panel supplying a house where almost everything has to be afci?
 
OP
S

Steve from Socal

Well-known member
Joined
Jan 27, 2009
Messages
3,502
Location
Hutchinson Ks.
MRB,

My answer above may not have been very clear. The number I quoted was at the service entrance. The single phase panel I want to install will be on the secondary side of a 25 Kva single phase 480-240/120 transformer. The transformer will be getting power from the I-line panel. The I-line pane will have a 200 amp feed from one of these.

Steve
 