Ok I’m hooking up my new furnace. My question in the electrical is do I have to run a wire from the fuse box or can the juice be tied into an outlet 10 feet away or so. I’m pretty sure if wire comes from fuse box I won’t need a switch if not exclusive thei need the switch..
What gauge wire up to furnace.?
Thanks
 

Attachments

  • 09803114-5282-4A86-9032-CE806CD9B8A3.jpg
    09803114-5282-4A86-9032-CE806CD9B8A3.jpg
    120.9 KB · Views: 61
To avoid these ads, REGISTER NOW!

Showkey

"MEMBER EMERITUS"
Joined
Aug 9, 2014
Messages
8,638
Location
Wausau WI
Think code requires a switch within a certain distance of the heater.

Tie in to an existing circuit would be allowed. Wire size would be determined by the circuit amperage likely a 15 or 20 amp.
 
OP
T

Triman8654

Well-known member
Joined
Feb 28, 2015
Messages
45
Cool, thanks showkey. The last one I did 7-8 years ago I put in a switch. But it was direct to breaker box.
 

xyster101

Well-known member
Joined
Jul 3, 2013
Messages
640
Location
Upstate NY
I would think you would want a switch just so you can easily turn it off.
What is the volts and amps of that? I would not think that 120 volts at 20 amps would be enough power for that unit. In which case you would need to run larger wire.
 
To avoid these ads, REGISTER NOW!

Showkey

"MEMBER EMERITUS"
Joined
Aug 9, 2014
Messages
8,638
Location
Wausau WI
I would think you would want a switch just so you can easily turn it off.
What is the volts and amps of that? I would not think that 120 volts at 20 amps would be enough power for that unit. In which case you would need to run larger wire.

That appears to be a propane or NG gas unit ? The total amp draw is 3.7 to 2.5 depending on the model.
 

D45

Well-known member
Joined
Mar 21, 2014
Messages
4,836
Location
NW INDIANA
I just used a plug in to an outlet, no switch

Such a small amp draw, silly to have its own circuit

The tstat is my on off switch
 

PeteyDaMan

Active member
Joined
Apr 27, 2014
Messages
29
Location
Chester, NY
I just installed the 75K unit and the instructions don't give any indication as the amperage required. Since it is an LP unit and it only uses AC for the fans, I went on the safe side and ran a 20amp dedicated circuit so I could disconnect power for service.

Just my .02
 