How do I wire this?
Markinred
I need to wire two switches, one to light, one to bath exhaust fan, through a gfci outlet. Like attached picture. lightswitches.jpg
Shiftless
East Bay SFO
Better check with your local inspector. When I rewired our master bathroom (in a 70 year old house) after a full gut job remodel, the inspector insisted on a dedicated 20 amp circuit with all of the receptacles, lights and the exhaust fan protected by GFCI. All wire had to be 12 ga. as well, even though the lights were LED and the fan drew less than 100 watts.
So I fed lights and the fan off the LOAD side of the first in line GFCI receptacle.
dogdog
don't route the lights via GFCI protected portion of the gfci plug... just put them in parallel if you are sharing the same breaker. Everything else is pretty straight forward.
PCustoms
VT
If the lights and fan are in a wet location, don't they have to be GFCI protected?
mike93lx
Richmond, VA
If you want them gfi protected, feed the switches from the second set of terminals on the receptacle. If you don't, feed the switches in parallel to the line feeding the receptacle.
I wouldnt protect the switches in my house
dogdog
Those other comments + also it dependents on definition of wet location, if it is just inside the bathroom and the fan/lights are not directly over your shower (means your shower or water doesn't spalsh to it and you are touching it.), probably not. If your wet location is your steam bath room like those Japanese/Chinese shower bath toilet/washroom/ bathtub /wet room... then probably a good idea to GFCI it. Not that I even know what GFCI means. pretty sure NEC doesn't require GFCI on fan/lights if it is not directly over something wet. So... I dunno.
dave*99
Coastal NJ
There are examples of damp and wet location light fixtures the have a requirement to be connected to a GFCI. This requirement would appear in the instructions for the fixture and likely part of the UL listing info.
justsam
Penngrove, California
Whether it is required by code or not seems to be uncertain, but what is certain is running them through the GFCI is very easy for you to do right now and no one has been chastised by doing more than NEC requires.
Shiftless
East Bay SFO
Right
As I said earlier, my city inspector called my little 40 sq. ft. remodeled bathroom with a 3x3 stall shower tiled all the way up to the ceiling and open above the glass door a wet area. Wiring the lights and the fan after the GFCI receptacle was the same amount of work and no extra material. The only disadvantage I can see is that if somebody drops a running hairdryer into a sink full of water and trips the GFCI and it’s nighttime, they will end up in the dark. Anybody else think of a downside?
acer66
Western North Carolina
Right
This would be my concern also, I am a bit paranoid when it comes to stuff like that and try to have if multiple lights are present to have them on different circuits.
Terry D
St. Louis, MO.
Unless the fan is in the shower, it does not need to be GFCI protected. Unless of course your local jurisdiction requires it. The light also does not need to be GFCI protected.
snyder
Baltimore md.
Our bathroom fan and light share the gfci. If you turn the fan and light off at the same time the gfci trips and leaves you in the dark..
Just_Steve
Dutchess County, NY
The above light/exhaust fan combo unit in my just remodeled bathroom is on a GFCI and timer. My understanding is if the light and fan are in the foot print of shower/tub it needs to be on a GFCI.
mikedodge
Usually gfci is for protection when something can be touched or dropped in water. Codes change but I've never heard of lights needing to be on it, that seems more dangerous if the lights go out then the electrical risk. My first thought was that if anything it would be a switch issue if for some reason there was no way of keeping the proper distance between the switch and shower and they allowed for gfci instead.
Markinred
Thanks for the help everyone. I just needed to know what to do with the wires, how to connect them. Thanks anyways.
ycgoat
S.E. Va
You identify the cable from the power source into the box Black =hot, White = Neutral, Bare copper = Ground.
Typically the outlets will have a copper colored screw a Silver screw, and a green screw.
On the LINE end of the GFCI land the Black wire from the source to the copper colored screw and the White wire to the Silver screw.
On the LOAD end of the GFCI connect a Black wire to the first switch and from there to the second switch.
Connect one each Black wire from the lights to the other terminals on the switches.
Put a new White wire on the Silver screw on the Load side of the GFCI and wire nut it to the White wires for the fan and lights
Connect all green screws to the bare copper wire.
ycgoat
S.E. Va
Something like this
exranger06
CT
210.8(A)(1) says that all RECEPTACLES in the bathroom need to be GFCI protected. It doesn't say anything about luminaires or fans, except that if a luminaire has a convenience receptacle built-in, then it needs GFCI. 210.8(C) says that luminaires in crawl spaces need GFCI, and nothing about bathrooms. 210.8 doesn't say anything else about GFCI being required for luminaires or fans, except that there may be additional requirements in Chapters 4, 5, and 6. I know Chapter 6 mentions GFCI required on luminaires and fans near swimming pools, but aside from that, I don't believe there's anything in those chapters that mentions GFCI for luminaires or fans.
410.10(D) addresses luminaires in bathtub and shower areas and just says where they can be located and that they need to be rated for damp or wet locations. No mention of GFCI being required.
dave*99
Coastal NJ
Yes and the next place to look is in the instructions for the luminaire. Some will say that if you locate this damp or wet rated fixture in a (whatever the manual states) location then this fixture must be GFCI protected. NEC is one piece of the detail. The manufacturers directions are another part.
nadogail
Coronado, CA
The “Code” lists the minimum requirements for electrical installations. We are free to build better than the minimum.
BreeStephany
Oregon
As 35Ford suggested, if the circuit for the bathroom is on its own circuit and your panel is new enough to find AFCI/GFCI breakers for, I would simply just wire in a AFCI/GFCI breaker at the start of the circuit and then just pigtail off the line coming into the box to the receptacle and to each switch.
With that said, you can also simply run incoming power into the line side of the GFCI receptacle, then run a short neutral and line wire out of the load side of the GFCI, which you can pigtail to both switches.
Either would be code compliant solutions. As others have said though, as long as your light fixtures / fan are not within reach of the envelope of the shower / bathtub, they do not need to be GFCI protected.
Just my two cents.
dcg9381
Austin, TX
Use a dual function arc fault / ground fault breaker to feed the circuit and everyone will be happy.
Well, NEC will be happy. Inspectors will be happy. Residents happy? They sure aren't in my home.. These dual function breakers work great for anything with moderate loads and are a great "code solution". But try running a hair dryer or vacuum cleaner on one.
Running a hair dryer or *any* vacuum cleaner on AFI/GFI breakers in my home - they have a 100% trip rate. Do not recommend.