I need to wire two switches, one to light, one to bath exhaust fan, through a gfci outlet. Like attached picture. lightswitches.jpg
 
To avoid these ads, REGISTER NOW!

Shiftless

Well-known member
Joined
Mar 9, 2014
Messages
14,818
Location
East Bay SFO
Better check with your local inspector. When I rewired our master bathroom (in a 70 year old house) after a full gut job remodel, the inspector insisted on a dedicated 20 amp circuit with all of the receptacles, lights and the exhaust fan protected by GFCI. All wire had to be 12 ga. as well, even though the lights were LED and the fan drew less than 100 watts.

So I fed lights and the fan off the LOAD side of the first in line GFCI receptacle.
 

dogdog

Well-known member
Joined
Nov 15, 2011
Messages
12,711
don't route the lights via GFCI protected portion of the gfci plug... just put them in parallel if you are sharing the same breaker. Everything else is pretty straight forward.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,684
Location
VT
don't route the lights via GFCI protected portion of the gfci plug... just put them in parallel if you are sharing the same breaker. Everything else is pretty straight forward.
If the lights and fan are in a wet location, don't they have to be GFCI protected?
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
I need to wire two switches, one to light, one to bath exhaust fan, through a gfci outlet. Like attached picture. lightswitches.jpg
If you want them gfi protected, feed the switches from the second set of terminals on the receptacle. If you don't, feed the switches in parallel to the line feeding the receptacle.

I wouldnt protect the switches in my house
 

dogdog

Well-known member
Joined
Nov 15, 2011
Messages
12,711
If the lights and fan are in a wet location, don't they have to be GFCI protected?


Those other comments + also it dependents on definition of wet location, if it is just inside the bathroom and the fan/lights are not directly over your shower (means your shower or water doesn't spalsh to it and you are touching it.), probably not. If your wet location is your steam bath room like those Japanese/Chinese shower bath toilet/washroom/ bathtub /wet room... then probably a good idea to GFCI it. Not that I even know what GFCI means. pretty sure NEC doesn't require GFCI on fan/lights if it is not directly over something wet. So... I dunno.
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,359
Location
Coastal NJ
There are examples of damp and wet location light fixtures the have a requirement to be connected to a GFCI. This requirement would appear in the instructions for the fixture and likely part of the UL listing info.
 

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,271
Location
Penngrove, California
Whether it is required by code or not seems to be uncertain, but what is certain is running them through the GFCI is very easy for you to do right now and no one has been chastised by doing more than NEC requires.
 

Shiftless

Well-known member
Joined
Mar 9, 2014
Messages
14,818
Location
East Bay SFO
Whether it is required by code or not seems to be uncertain, but what is certain is running them through the GFCI is very easy for you to do right now and no one has been chastised by doing more than NEC requires.
Right
As I said earlier, my city inspector called my little 40 sq. ft. remodeled bathroom with a 3x3 stall shower tiled all the way up to the ceiling and open above the glass door a wet area. Wiring the lights and the fan after the GFCI receptacle was the same amount of work and no extra material. The only disadvantage I can see is that if somebody drops a running hairdryer into a sink full of water and trips the GFCI and it’s nighttime, they will end up in the dark. Anybody else think of a downside?
 

acer66

Well-known member
Joined
Dec 4, 2010
Messages
4,442
Location
Western North Carolina
Right
As I said earlier, my city inspector called my little 40 sq. ft. remodeled bathroom with a 3x3 stall shower tiled all the way up to the ceiling and open above the glass door a wet area. Wiring the lights and the fan after the GFCI receptacle was the same amount of work and no extra material. The only disadvantage I can see is that if somebody drops a running hairdryer into a sink full of water and trips the GFCI and it’s nighttime, they will end up in the dark. Anybody else think of a downside?
This would be my concern also, I am a bit paranoid when it comes to stuff like that and try to have if multiple lights are present to have them on different circuits.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
Unless the fan is in the shower, it does not need to be GFCI protected. Unless of course your local jurisdiction requires it. The light also does not need to be GFCI protected.
 
To avoid these ads, REGISTER NOW!

snyder

Well-known member
Joined
Dec 18, 2008
Messages
545
Location
Baltimore md.
Our bathroom fan and light share the gfci. If you turn the fan and light off at the same time the gfci trips and leaves you in the dark..
 

Just_Steve

Well-known member
Joined
Jun 2, 2020
Messages
989
Location
Dutchess County, NY
IMG_2608-1.jpeg

The above light/exhaust fan combo unit in my just remodeled bathroom is on a GFCI and timer. My understanding is if the light and fan are in the foot print of shower/tub it needs to be on a GFCI.
 

mikedodge

Well-known member
Joined
Jun 27, 2017
Messages
2,949
Usually gfci is for protection when something can be touched or dropped in water. Codes change but I've never heard of lights needing to be on it, that seems more dangerous if the lights go out then the electrical risk. My first thought was that if anything it would be a switch issue if for some reason there was no way of keeping the proper distance between the switch and shower and they allowed for gfci instead.
 
OP
M

Markinred

New member
Joined
Feb 10, 2022
Messages
2
Thanks for the help everyone. I just needed to know what to do with the wires, how to connect them. Thanks anyways.
 

ycgoat

Well-known member
Joined
Mar 28, 2020
Messages
971
Location
S.E. Va
You identify the cable from the power source into the box Black =hot, White = Neutral, Bare copper = Ground.
Typically the outlets will have a copper colored screw a Silver screw, and a green screw.
On the LINE end of the GFCI land the Black wire from the source to the copper colored screw and the White wire to the Silver screw.
On the LOAD end of the GFCI connect a Black wire to the first switch and from there to the second switch.
Connect one each Black wire from the lights to the other terminals on the switches.
Put a new White wire on the Silver screw on the Load side of the GFCI and wire nut it to the White wires for the fan and lights
Connect all green screws to the bare copper wire.
 

ycgoat

Well-known member
Joined
Mar 28, 2020
Messages
971
Location
S.E. Va
Something like this
 

Attachments

  • Light-Switch-Connected-to-the-Load-Terminals-are-GFCI-Protected.png
    Light-Switch-Connected-to-the-Load-Terminals-are-GFCI-Protected.png
    22.8 KB · Views: 41

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
210.8(A)(1) says that all RECEPTACLES in the bathroom need to be GFCI protected. It doesn't say anything about luminaires or fans, except that if a luminaire has a convenience receptacle built-in, then it needs GFCI. 210.8(C) says that luminaires in crawl spaces need GFCI, and nothing about bathrooms. 210.8 doesn't say anything else about GFCI being required for luminaires or fans, except that there may be additional requirements in Chapters 4, 5, and 6. I know Chapter 6 mentions GFCI required on luminaires and fans near swimming pools, but aside from that, I don't believe there's anything in those chapters that mentions GFCI for luminaires or fans.

410.10(D) addresses luminaires in bathtub and shower areas and just says where they can be located and that they need to be rated for damp or wet locations. No mention of GFCI being required.
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,359
Location
Coastal NJ
210.8(A)(1) says that all RECEPTACLES in the bathroom need to be GFCI protected. It doesn't say anything about luminaires or fans, except that if a luminaire has a convenience receptacle built-in, then it needs GFCI. 210.8(C) says that luminaires in crawl spaces need GFCI, and nothing about bathrooms. 210.8 doesn't say anything else about GFCI being required for luminaires or fans, except that there may be additional requirements in Chapters 4, 5, and 6. I know Chapter 6 mentions GFCI required on luminaires and fans near swimming pools, but aside from that, I don't believe there's anything in those chapters that mentions GFCI for luminaires or fans.

410.10(D) addresses luminaires in bathtub and shower areas and just says where they can be located and that they need to be rated for damp or wet locations. No mention of GFCI being required.
Yes and the next place to look is in the instructions for the luminaire. Some will say that if you locate this damp or wet rated fixture in a (whatever the manual states) location then this fixture must be GFCI protected. NEC is one piece of the detail. The manufacturers directions are another part.
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,274
Location
Coronado, CA
The “Code” lists the minimum requirements for electrical installations. We are free to build better than the minimum.
 

BreeStephany

ALLIANCE MEMBER
Joined
May 19, 2012
Messages
870
Location
Oregon
As 35Ford suggested, if the circuit for the bathroom is on its own circuit and your panel is new enough to find AFCI/GFCI breakers for, I would simply just wire in a AFCI/GFCI breaker at the start of the circuit and then just pigtail off the line coming into the box to the receptacle and to each switch.

With that said, you can also simply run incoming power into the line side of the GFCI receptacle, then run a short neutral and line wire out of the load side of the GFCI, which you can pigtail to both switches.

Either would be code compliant solutions. As others have said though, as long as your light fixtures / fan are not within reach of the envelope of the shower / bathtub, they do not need to be GFCI protected.

Just my two cents.
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
12,029
Location
Austin, TX
Use a dual function arc fault / ground fault breaker to feed the circuit and everyone will be happy.
Well, NEC will be happy. Inspectors will be happy. Residents happy? They sure aren't in my home.. These dual function breakers work great for anything with moderate loads and are a great "code solution". But try running a hair dryer or vacuum cleaner on one.

Running a hair dryer or *any* vacuum cleaner on AFI/GFI breakers in my home - they have a 100% trip rate. Do not recommend.
 