I'm putting in some 30A 240V outlets in my shop with 8/3 wire. Am I allowed to put more than one of these outlets on a 30A circuit? (Obviously not to be all used at once)
Also, since I'm using 8ga wire, can I use a 40A breaker instead of a 30?
Mostly I'm going to split it up even further into 20A 120V circuits with a spider box. Also will occasionally plug in an air compressor. I already had the wire so....What are you planning on using the circuits for?
I'm confused. Why would a 10ga ground not be enough for a 30A circuit? What application is 8/3 NM with a 10ga ground for then? Can I run a separate ground wire with the romex?You will need to upsize the grounding conductor if you use 8 AWG on a 30A circuit, I am assuming your using NM "Romex®" which has a 10 AWG grounding conductor, NEC art 250.122(B) does require a larger grounding conductor when ungrounded conductors are increased in size.
I'm putting in some 30A 240V outlets in my shop with 8/3 wire. Am I allowed to put more than one of these outlets on a 30A circuit? (Obviously not to be all used at once)
Also, since I'm using 8ga wire, can I use a 40A breaker instead of a 30?
Mostly I'm going to split it up even further into 20A 120V circuits with a spider box.What are you planning on using the circuits for?
Also will occasionally plug in an air compressor. I already had the wire so....
So I can move things around if I want to. I don't need 30 amps for the compressor but it shouldn't hurt either.The question which immediately comes to mind is, why would you want to?
Yes, I have a 30A box. (The original twist lock cord has been replaced with a 30A dryer cord)Let's be clear here. Are you referring literally to a PORTABLE Spider box
According to that article posted, #10 ground is good up to 60 amps so why wouldn't it be good enough for 30.
You're wrong as usual. You should get a Code book, and read it before you post.
250.122(B) Increased in Size.
Where ungrounded conductors are increased in size, equipment grounding conductors, where installed, shall be increased in size proportionately according
to the circular mil area of the ungrounded conductors
You're wrong as usual. You should get a Code book, and read it before you post.
250.122(B) Increased in Size.
Where ungrounded conductors are increased in size, equipment grounding conductors, where installed, shall be increased in size proportionately according
to the circular mil area of the ungrounded conductors
It's the same in either the 2008 or 2011.
Simply using the table is a good way to get in trouble.
Read the actual text of Article 250.122 (B) hint: (B) and see for yourself.
It's not an exception, and is mandatory.
Still not making any sense to me. What application is NM 8/3 with 10ga ground for if it is not suitable for a 30A circuit? But 10/3 would be just fine? Nonsense! Makes just as much sense as saying I have to wear red shoes when I'm installing it...
Depending on the length of the run. I would also add a grounding rod if it was mine!
I suppose you also have to consider the fact that after your dead and gone, the circuit will still be there. Consider the next owner will not know to not use both all the multiple outlet, you put in, at the same time.

Obviously it's all about money, but I'm in a rural unincorporated area so they aren't too picky...So why then do they bother to sell 8/3 NM cable with a 10 gauge ground if you aren't allowed to use it?
Quite frankly I'm not going to get a permit so it doesn't really matter. I'll do it up to code in the name of safety but not in the name of ridiculousness. I'm not going to pay an inspector $100 to nit pick about things like this...
Because code allows #10 ground on a #8 wire, but the circuit has to be properly sized. Put the proper breaker and receptacles on a circuit wired with #8 and a #10 ground, and you have a legit circuit. Use that #8 with a #10 ground to upsize a smaller circuit, and you don't have a legit circuit.
Charles
So in other words with a 40A breaker and a 40A outlet I can use the 8/3, but if I go down to a 30A breaker and a 30A outlet I have to replace the 8/3 with smaller gauge?
I almost want to break that code out of principle alone.
Yeah I understand that but it's one of those things that don't make sense
Yep, the more I think about it the more it pisses me off. The NEC is there for safety and no other reason. It should not ever cost anywhere near $100 to get a permit and an inspector, and the code itself should make perfect sense, and be easy to understand.
That is your local/state government at work, and unrelated to the NEC.