How much service do I need?

Elder

Member
Joined
May 21, 2013
Messages
17
Location
Sioux City,IA
I'm running a 220v single phase compressor, a syncrowave 180sd tig and a yet to be purchased heat and ac unit (motel style) among several outlets and lights. I've been told I need more than 100amp service. Does anyone want to weigh in on this for me?
 
To avoid these ads, REGISTER NOW!

porschedude996TT

Well-known member
Joined
Oct 28, 2007
Messages
2,384
Location
Santa Maria, California
I have a one or two man shop, 6hp 240v compressor, Miller 200 Syncrowave, tons of lights, forced air furnace, and I am running it off a 100 amp breaker to a sub-panel in the shop. The welder is hooked up to another 50 amp sub-panel that has my spa tub connected to it. I just turn off the spa when i run the welder. The 100 amp sub is getting its power from a 100 amp breaker in a 125 amp panel on the house.

Each leg of that 100 amp feed is capable of 100 amps at 120volts or 100 amps at 240 volts.

I say your fine if your heating and cooling loads are low. What is your weather like? You don't have a location on your avatar.
 
Last edited:
To avoid these ads, REGISTER NOW!

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,114
Location
SE MI
I have a one or two man shop, 6hp 240v compressor, Miller 200 Syncrowave, tons of lights, forced air furnace, and I am running it off a 100 amp breaker to a sub-panel in the shop.
I concur.

100A should be fine. You may have to turn off the compressor while welding at max. Your combo heat and A/C unit should not be an issue.

If you are even remotely thinking about a plasma cutter, this changes the equation a lot because it requires the compressor to be running at the same time.
 

BD1

Well-known member
Joined
Mar 18, 2007
Messages
4,602
Location
north side
100 will be fine. Like stated , using plasma may have the compressor kick on. That won't be a issue.
 
OP
E

Elder

Member
Joined
May 21, 2013
Messages
17
Location
Sioux City,IA
I don't have intentions for a plasma but if I did could I shut off the heat or air unit to be able to run both? Good news then I really didn't want to have to run more than 100amp because then they were going to charge me more monthly just to have the service
 

FDNY-L107

Member
Joined
May 30, 2011
Messages
8
Make sure you also take into account future growth needs. Double whatever you come up with, you can never have too much power.
 