How should I wire this? 220v

92GreenYJ

Well-known member
Joined
Jun 9, 2012
Messages
488
Location
San Diego, CA
Hey all. So I'm working on getting the garage set up in the new house. I just installed a 100 amp sub panel just to run the garage. As I understand it the sub panel requires the neutral and ground to be separate and isolated which I did.

Now I'm wiring up the 3 prong outlets for my welder and plasma cutter. So I have 4 wires to work with. Obviously the black and red hot wires go to the side prongs. My question is the center prong. Should that be the white neutral wire or the bare ground wire? And then where do I attach the other wire?

2A697B68-9B23-4A97-B7A0-2084ECFEE8E2-8703-00000EB1FA8970F0_zps9ced122a.jpg
 
To avoid these ads, REGISTER NOW!

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
That's the wrong kind of receptacle for a welder. That is an old non-grounding type dryer receptacle. You should have gotten a 6-30R receptacle.
 

Highbeam

Well-known member
Joined
Feb 15, 2011
Messages
2,292
Location
Mt Rainier foothills, WA
You use the bare ground for the ground. The white should be capped at both ends or at least capped at the outlet end. I've done this same thing many times since I have lots of 6/3 laying around.
 
OP
9

92GreenYJ

Well-known member
Joined
Jun 9, 2012
Messages
488
Location
San Diego, CA
These are the same receptacles I had wired in my old garage. I just moved them to the new house. Been running my welder and plasma off these for years.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
That doesn't make it the right outlet. But, wire it as Highbeam stated. I suggest you mark/label the outlet for welder use only. If you move and leave it for the next owner they may try to plug in a stove or dryer.

These are the same receptacles I had wired in my old garage. I just moved them to the new house. Been running my welder and plasma off these for years.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,061
Location
Modesto, CA
The issue with that plug is that its non grounding meaning the chassis isbt grounded and its meant for a 120/240v appliance NOT a strictly 240v appliance. Yes, it will work, but its not right nor upto code, if u care about that!
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
You don't need the white. You only use the Red,Black and bare for ground. The white is used with appliances that also need 120V. The plug and receptacle typically used for welders and plasma cutters is a 6-30 or 6-50 250V. The outlet and plug you have is a 10-50 125V/250V.

ok so if my Welder and Plasma have three prong plugs on them, how am I supposed to add the 4th to the machines?
 