Lineman again
Just a side not on the neutral issue, your neutral has to be disconnected as well with a portable generator, that's why generator panels use a 3 phase breaker and switch the neutral as well.
Ever notice the big sticker on your generator that says floating Neutral do not ground ( that means your ruining your generator hooking it to a grounded neutral)
Its actually for 2 reasons,
1 the first is so you don't backfeed the neutral with imbalance
2. And this is for all the guys that don't care about the safety, your ruining your generator leaving it hooked to the utility neutral, portable generators work of a modified sine wave, they actually work by putting a positive 60 volt on the hot leg and negative 60 on the neutral side and with ac reverse the orientation 60 times per second ( hertz )
I hope that helps guys here some, I am happy to help with anyone looking to do it right, first off it is a huge safety issue hooking thru a plug and opening your main, your actually creating a fire hazard as eventually you will burn up your ground to the house, as your ground and neutral are hooked together at the first point of entry to the house. When you use a transfer switch the neutral is floated
Just a side not on the neutral issue, your neutral has to be disconnected as well with a portable generator, that's why generator panels use a 3 phase breaker and switch the neutral as well.
Ever notice the big sticker on your generator that says floating Neutral do not ground ( that means your ruining your generator hooking it to a grounded neutral)
Its actually for 2 reasons,
1 the first is so you don't backfeed the neutral with imbalance
2. And this is for all the guys that don't care about the safety, your ruining your generator leaving it hooked to the utility neutral, portable generators work of a modified sine wave, they actually work by putting a positive 60 volt on the hot leg and negative 60 on the neutral side and with ac reverse the orientation 60 times per second ( hertz )
I hope that helps guys here some, I am happy to help with anyone looking to do it right, first off it is a huge safety issue hooking thru a plug and opening your main, your actually creating a fire hazard as eventually you will burn up your ground to the house, as your ground and neutral are hooked together at the first point of entry to the house. When you use a transfer switch the neutral is floated