First off, let me say that I am not an HVAC contractor by day, but I've been researching and purchasing the tools for this project for months before actually starting the install.
Right now I'm in the last stages of installing my new Rheem gas furnace and HP system. I've finished the install and now am working on the final step of evacuating the lines before releasing the refrigerant into the lines. I'm running into a couple of issues...
The first issue is this...
The positioning of the piping inside the HP doesn't allow me enough room to get the Appion valve core removal tool on the service valve, let alone enough room to pull out the valve core.
Here is how I have things hooked up right now to evacuate the system; which is not ideal since I have to go through the valve core.
How do you guys get around situations like this?
Second question
Using the above setup, I can easily pull the system down to about 540 microns but can't really get any further, I'm guessing this is because of the valve core still being in the system on the low side. When I valve off the system I get a quick rise up to around 700 microns and after 30 minutes I'm at around 950.
Now some information I read, says that my evacuation is sufficient with these results but other things I read says I should be able to stabilize and not see a rise above 500.
After a few hours of having the system valved off I am up around 1600 microns.
Now my gut reaction is that I still have some moisture in the system and that I should sweep the system with inert gas and vacuum again.
Any insight you could provide would be greatly appreciated. TIA
Right now I'm in the last stages of installing my new Rheem gas furnace and HP system. I've finished the install and now am working on the final step of evacuating the lines before releasing the refrigerant into the lines. I'm running into a couple of issues...
The first issue is this...
The positioning of the piping inside the HP doesn't allow me enough room to get the Appion valve core removal tool on the service valve, let alone enough room to pull out the valve core.
Here is how I have things hooked up right now to evacuate the system; which is not ideal since I have to go through the valve core.
How do you guys get around situations like this?
Second question
Using the above setup, I can easily pull the system down to about 540 microns but can't really get any further, I'm guessing this is because of the valve core still being in the system on the low side. When I valve off the system I get a quick rise up to around 700 microns and after 30 minutes I'm at around 950.
Now some information I read, says that my evacuation is sufficient with these results but other things I read says I should be able to stabilize and not see a rise above 500.
After a few hours of having the system valved off I am up around 1600 microns.
Now my gut reaction is that I still have some moisture in the system and that I should sweep the system with inert gas and vacuum again.
Any insight you could provide would be greatly appreciated. TIA