Ok, I got back on this project again this weekend. I ordered an 1/2" hose and greatly simplified my setup. Here is a poor picture of the setup...
You can see that I have the micron gauge on the suction line with the schrader valve still installed, since you can see I cannot get the VCT on that line because of the piping configuration. This also ensured that my micron gauge was as far away from the pump as possible. My 1/2" hose is hooked to the VCT on the liquid line with the schrader valve removed.
I hooked this up and let it run for about 4 hours. That got the system down to 315 microns. At this point I valved off the VCT and watched the rise. As soon as I valved off the VCT the rise was very slow. After 10 minutes I was at 580 microns and after 20 minutes I was at 770. After 1.5 hours I was at 1440 and not moving at all.
I'm assuming these results mean that I still have moisture in the system so I'll do a sweep with nitrogen this week and vacuum again to see if I can improve my results. This process has taken forever since I've been traveling for work the last 3 weeks. I think i'm finally on the home stretch though.
I appreciate everyone's input very much and as always let me know if I'm doing something wrong or should be doing something differently.
*edit* obviously I had my VCT open during the evacuation
The picture must have been at the 10 minute mark after closing off the system. You can also see I have a leak rate on the micron gauge of 0.4 microns per second.
You can see that I have the micron gauge on the suction line with the schrader valve still installed, since you can see I cannot get the VCT on that line because of the piping configuration. This also ensured that my micron gauge was as far away from the pump as possible. My 1/2" hose is hooked to the VCT on the liquid line with the schrader valve removed.
I hooked this up and let it run for about 4 hours. That got the system down to 315 microns. At this point I valved off the VCT and watched the rise. As soon as I valved off the VCT the rise was very slow. After 10 minutes I was at 580 microns and after 20 minutes I was at 770. After 1.5 hours I was at 1440 and not moving at all.
I'm assuming these results mean that I still have moisture in the system so I'll do a sweep with nitrogen this week and vacuum again to see if I can improve my results. This process has taken forever since I've been traveling for work the last 3 weeks. I think i'm finally on the home stretch though.
I appreciate everyone's input very much and as always let me know if I'm doing something wrong or should be doing something differently.
*edit* obviously I had my VCT open during the evacuation