Who on this forum actually works in the industry?
20+ year tech. here
About 60/40 commercial/residential.
:beer:
 
To avoid these ads, REGISTER NOW!

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,406
Location
N CA
45 yrs laborer, apprentice, journeyman, contractor, manuf rep. Goes by fast!
 

bonneyman

Well-known member
Joined
Apr 22, 2010
Messages
8,772
Location
Desert SW
23 years in the industry. Service tech, installer, troubleshooter, and now owner.
Might make another 23 years if the dog-gone EPA would **** out!:shocking:
 

xravenx

Well-known member
Joined
Nov 4, 2010
Messages
147
Location
Baltimore, MD
Only do commercial stuff, was a tech/installer for 24 years, business owner for the last 9 years. Still get out in the field once in a while........way better then the office.

John
 

xrdad

Well-known member
Joined
Mar 14, 2011
Messages
487
Location
Ontario Canada
Any HVAC guys in the Toronto area looking to do a weekend A/C install this year? I'm also looking for a gas heater for my shop.. if someone knows of a bargain?
Yes, I'm cheap and broke.. bad combination.
 

Frank The Plumber

Well-known member
Joined
Feb 19, 2011
Messages
2,644
Location
Chicago.
If some one called me a tech I'd slap them. The kid at Jiffy Lube is a tech. I'm a mechanical contractor. Plumbing and Piping Mechanic / craft tradesman.
 

59 wagon man

Well-known member
Joined
Oct 25, 2010
Messages
1,589
Location
hollywood fla
piping mechanic? thats a new one on me been doing it 35 yrs been called a steamfitter ,pipefitter, plumber,journeyman, master plumber tradesman ,my guys in the field can be referred to as technicians but never a piping mechanic. anything "mechanic"= auto related just my .02
 

rickairmedic

Well-known member
Joined
May 31, 2005
Messages
4,165
Location
louisville ,Ky
If some one called me a tech I'd slap them. The kid at Jiffy Lube is a tech. I'm a mechanical contractor. Plumbing and Piping Mechanic / craft tradesman.



Frank that kinda sounds like that other fancy Title um Sanitation engineer :D. We ued ta call em da garbage man :D and you would be Da Plumba :D. I have no problems being a Heating and Air Technician :D.


Rick
 

jbarbrey

Active member
Joined
Dec 22, 2008
Messages
41
Going on 12 years in the field. Started out refrigeration now I service and repair mostly commercial equipment.
 

ambenz

Well-known member
Joined
Dec 12, 2010
Messages
4,236
Location
NW Chicago Suburbs
HVAC Automation Service Tech....automate all the mechanics so you can see room temps and control boilers, chillers, and Air Handlers from anywhere on the world wide web...if, you know the password..LOL!

energy.jpg
 

padstack

Well-known member
Joined
Feb 25, 2010
Messages
246
If some one called me a tech I'd slap them. The kid at Jiffy Lube is a tech. I'm a mechanical contractor. Plumbing and Piping Mechanic / craft tradesman.

People say things like that in my field as well (electrical). I say, call me anything you want as long as those checks show up! LOL! :beer:
 
To avoid these ads, REGISTER NOW!

bonneyman

Well-known member
Joined
Apr 22, 2010
Messages
8,772
Location
Desert SW
Heck, if things keep going the way they are, I'll be happy with some fried chicken and apple pies for payment!
 

neverenoughtools

Well-known member
Joined
Nov 15, 2009
Messages
494
Location
Near Toronto !
Any HVAC guys in the Toronto area looking to do a weekend A/C install this year? I'm also looking for a gas heater for my shop.. if someone knows of a bargain?
Yes, I'm cheap and broke.. bad combination.

You'd think there might be 1 or 2 guys from our neck of the woods on here......perhaps you should inquire on the Canadian site as well. :beer::beer:
 

Jack Olsen

Super Moderator
Staff member
Joined
Mar 22, 2009
Messages
6,678
Location
Los Angeles
Here's an AC question where it might be easy for you guys to save me (at least some) aggravation. My house has central AC, not sure how old. At the end of last season, it failed. The symptoms were this: the outside compressor would switch on and operate normally (I'd replaced the capacitor for that about a year prior). But then the inside-the-house blower would not kick in at all. I suspect this means I'm low on freon -- that there's a pressure switch that's not allowing the furnace blower to move air over the evaporator.

The same blower is working normally with the heating system.

Any tricks I should try or components I should look at before I call one of you pros?
 

rickairmedic

Well-known member
Joined
May 31, 2005
Messages
4,165
Location
louisville ,Ky
Jack chances are you have a bad fan relay on the cooling side . I would bet if you can get me a model number and serial number and the make of your furnace I can get a part number for you :D.


Rick
 

Mike007

Well-known member
Joined
Dec 4, 2010
Messages
2,594
Switch the stat to "Fan on". If it comes on you need a new t-stat.
 

rickairmedic

Well-known member
Joined
May 31, 2005
Messages
4,165
Location
louisville ,Ky
Mike the T-stat is not always the answer . Most often if the fan works in heating mode and also works in fan on the culprit is a relay in the furnace that is energised when in cooling mode . The contacts in the relay go bad or become corroded and the relay stops working . I had an old carrier furnace with this issue just last week and see it way more often than I do a bad T-stat.

Rick
 

The Hot Rod Grille

Well-known member
Joined
Jul 29, 2005
Messages
1,020
Location
Winfield, WV
I retired July 31, 2009 at age 56 after 34 years in R&D for a major chemical company. I will graduate in June after completing a pair of two year programs in Electrical Technology (will receive my Journeyman License) and HVAC/Refrigeration. I have already passed my EPA 608 Universal Certification and the 609 Automotive Certification. My objective is to be able to service my own equipment and possibly help family and friends. My soda fountain and vintage Pepsi machines use R-12 and since I have purchased a Snap-On recovery unit, I will be able to keep them original and operating for many years to come!

Jim
 

Attachments

  • Bastian-Blessing soda fountain.jpg
    Bastian-Blessing soda fountain.jpg
    68.4 KB · Views: 10
  • Ideal 55 Pepsi.jpg
    Ideal 55 Pepsi.jpg
    69.1 KB · Views: 10
  • LaCrosse Pepsi.jpg
    LaCrosse Pepsi.jpg
    61.1 KB · Views: 11
  • Snap-On #1.jpg
    Snap-On #1.jpg
    134.3 KB · Views: 10
  • Snap-On #2.jpg
    Snap-On #2.jpg
    129.7 KB · Views: 6

xravenx

Well-known member
Joined
Nov 4, 2010
Messages
147
Location
Baltimore, MD
If you switch the thermostat to "fan on" and the fan won't start, reach in the furnace and spin the blower wheel, if it starts the run capacitor is bad.

John
 

Jack Olsen

Super Moderator
Staff member
Joined
Mar 22, 2009
Messages
6,678
Location
Los Angeles
Thanks, rickairmedic. And everyone else. (And I apologize for diluting the thread with a tech issue. I'll delete it later to keep the thread only about HVAC guys who are on GJ.)

The furnace is a Goodman model GMP100-4. (The Evaporator is an ADP model HA05248C175B252084.) Here's a cell phone picture of the plate for the furnace:

furnace.jpg


Here's the evaporator plate:

ha05248c175b252084.jpg
 
Last edited:

rickairmedic

Well-known member
Joined
May 31, 2005
Messages
4,165
Location
louisville ,Ky
Ok Jack you have a 100,000 BTU furnace and a 4 ton Air conditioning system :D. I sell Goodman products . I will check with my supplier in the morning and verify the location of the blower relay ( although I am pretty sure on that model it is on the furnace control board ) . I will also verify that that is your problem but I am betting on it :D. The good news is in the meantime if you need AC you should be able to switch the thermostat from auto to on and get the blower to run it will just run the blower full time instead of just running it while the AC or Heat is on . I have an install going tomorrow so it will most likely be 6PM or so eastern before I get back to you on it Jack.


Oh yeah your system was installed in 1997 or early 1998 :D.


One more thing if you get a chance tonight pull the lower door off of the furnace where the blower motor is and see if you can get me a picture of the control board and I can most likely tell you where to put your test leads to make sure it is the fan relay :D.

Rick


Rick
 
Last edited:

Mike007

Well-known member
Joined
Dec 4, 2010
Messages
2,594
Mike the T-stat is not always the answer . Most often if the fan works in heating mode and also works in fan on the culprit is a relay in the furnace that is energised when in cooling mode . The contacts in the relay go bad or become corroded and the relay stops working . I had an old carrier furnace with this issue just last week and see it way more often than I do a bad T-stat.

Rick

Maybe Rick, but how is a HO supposed to check the relay? Obviously if he turns it to fan on and the fan comes on it's the stat. If it doesn't it could be the relay but the stat is at least ruled out.
 

rickairmedic

Well-known member
Joined
May 31, 2005
Messages
4,165
Location
louisville ,Ky
I PM'd Jack instructions on testing the relay :D. Also the fan on position can bypass the cooling relay on the board thus meaning he has a new stat and still no AC.


Rick
 

Mike007

Well-known member
Joined
Dec 4, 2010
Messages
2,594
I will also verify that that is your problem but I am betting on it :D. The good news is in the meantime if you need AC you should be able to switch the thermostat from auto to on and get the blower to run it will just run the blower full time instead of just running it while the AC or Heat is on . I have an install going tomorrow so it will most likely be 6PM or so eastern before I get back to you on it Jack. Rick

Ummm Rick, if you are sure it's the relay, why would you think turning the fan switch to "fan on" is going to run the fan? If the relay on the board has failed, turning the switch to on is going to do nothing.
 

Mike007

Well-known member
Joined
Dec 4, 2010
Messages
2,594
I PM'd Jack instructions on testing the relay :D. Also the fan on position can bypass the cooling relay on the board thus meaning he has a new stat and still no AC.


Rick

I think you are mistaken. If I'm understanding you.
 

rickairmedic

Well-known member
Joined
May 31, 2005
Messages
4,165
Location
louisville ,Ky
Mike although it could go either way there are tests I will walk Jack through before he buys a new control board or Tstat to make sure we get the right component. When I chatted with him through PM earlier he noted that it was a perfect 72* currently at his home and he just wanted to work through this issue before it hits 110* :D. Jack would not be the first member I have walked through diagnostics on their systems long distance and I asure you Mike I will make sure we have the right part before we go buying any :D.

Rick
 

Garage5.9

Well-known member
Joined
Jan 26, 2011
Messages
2,508
Location
Maui,Hawaii
HVAC Automation Service Tech....automate all the mechanics so you can see room temps and control boilers, chillers, and Air Handlers from anywhere on the world wide web...if, you know the password..LOL!

energy.jpg

Thats pretty cool and scary at the same time. Imagine what you could do if some one pissed you off in said building.
 

Mike007

Well-known member
Joined
Dec 4, 2010
Messages
2,594
Mike although it could go either way there are tests I will walk Jack through before he buys a new control board or Tstat to make sure we get the right component. When I chatted with him through PM earlier he noted that it was a perfect 72* currently at his home and he just wanted to work through this issue before it hits 110* :D. Jack would not be the first member I have walked through diagnostics on their systems long distance and I asure you Mike I will make sure we have the right part before we go buying any :D.

Rick

I'm not breaking your balls Rick, but if the fan relay on the board is failed, turning the stat to fan on is not going to bypass the relay. Wasn't sure I was understanding you correctly.
 