Hydronic heat safety switch

gayler

Well-known member
Joined
Sep 22, 2011
Messages
3,276
Location
Lakin Kansas
My system was put in nearly 25 years ago by a company that was new to hydronic. There were several things designed wrong. One is the lack of a safety to turn off the gas in the event of pressure loss in the system. I would like to add something to turn off the gass if the heater loses liquid due to a leak. What would be needed for this? I’m running a 50 gallon natural gas water heater. I’m assuming a pressure switch to control a solenoid valve on the gas line?
 
To avoid these ads, REGISTER NOW!

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,048
Boiler low water cut out (LWCO) controls are a pretty common thing.
Mine won't fire at all until it's over 7.3 PSI, and won't fire at full rate until it's over 13 PSI.
 

PWC Repair

Well-known member
Joined
Dec 27, 2012
Messages
3,182
Location
Arkansas
Mine is a low pressure switch tied into the low voltage thermostat controls. If it gets below 5 psi (closed loop liquid loss) it opens the circuit so no matter what the thermostat tries to do.....nothing will come on.
 

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
2,981
Location
Peace Valley,mo
Are you questioning a boiler or a stand alone water heater?
Hot water boiler above 400k btu's low water cut off is required. If its a water coil or tube it's protected by flow switch.
Stand alone water heater is protected by a relief valve set at 210°f and or 150lbs
Thermocouple protects gas valve from opening if pilot flame isn't detected. Being connected to city water or well if there is a leak the leak would be pressurised unless the water would be off and tank would drain and gas valve thermostat would also fail.
 
To avoid these ads, REGISTER NOW!
OP
G

gayler

Well-known member
Joined
Sep 22, 2011
Messages
3,276
Location
Lakin Kansas
Are you questioning a boiler or a stand alone water heater?
Hot water boiler above 400k btu's low water cut off is required. If its a water coil or tube it's protected by flow switch.
Stand alone water heater is protected by a relief valve set at 210°f and or 150lbs
Thermocouple protects gas valve from opening if pilot flame isn't detected. Being connected to city water or well if there is a leak the leak would be pressurised unless the water would be off and tank would drain and gas valve thermostat would also fail.
50 gallon natural gas water heater. If the heater drains due to a leak wouldn’t the thermostat still fire the burner? This is a closed system with antifreeze and water.
 
OP
G

gayler

Well-known member
Joined
Sep 22, 2011
Messages
3,276
Location
Lakin Kansas
On a related note. My expansion tank is leaking. It is a 6 gallon tank, 50 gallon water heater, five loops in the floor and 1200sq ft garage. I’m not sure if I really need a tank that size. Is this the correct size for my garage?
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,073
Location
VT
50 gallon natural gas water heater. If the heater drains due to a leak wouldn’t the thermostat still fire the burner? This is a closed system with antifreeze and water.
So?

I don't see a safety risk here
 

PWC Repair

Well-known member
Joined
Dec 27, 2012
Messages
3,182
Location
Arkansas
On a related note. My expansion tank is leaking. It is a 6 gallon tank, 50 gallon water heater, five loops in the floor and 1200sq ft garage. I’m not sure if I really need a tank that size. Is this the correct size for my garage?
Sounds a bit large. My system is almost just like yours. I believe my tank is a 2.5 or 3 gallon. You don't need a very large tank for the lower pressures of a small (ish) closed loop system. I only run 5-10psi pressure in mine.
 
OP
G

gayler

Well-known member
Joined
Sep 22, 2011
Messages
3,276
Location
Lakin Kansas
Sounds a bit large. My system is almost just like yours. I believe my tank is a 2.5 or 3 gallon. You don't need a very large tank for the lower pressures of a small (ish) closed loop system. I only run 5-10psi pressure in mine.
Thanks! That’s what I was thinking too. The company that did it used a six gallon tank and the biggest I can find is 4.5.
 