Inline 240v outlets 6-50r and 14r

Xkylescorex

Well-known member
Joined
Jan 10, 2016
Messages
160
So I have my welder on a dedicated circuit using 10/2 wire. So two hots and a ground. Of course my powdercoat oven has a nema 4 prong connection. I was thinking since the plug is near the panel I could just jump off my welder outlet and then run a dedicated nuetral over to the box . Mainly because I have 10/2 and dont want to go buy a new length of 10/3. I see there are adapters on amazon to go from 3 to 4 prong but that wouldnt solve the problem of not have a nuetral on the oven plug and from what Ive read is dangerous. Also dont want to shell out for another $40 breaker since I will never use the two plugs at the same time and will probably use the oven twice a year
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,317
Location
Richmond, VA
If the oven is higher than 5750 watts, #10 isn't big enough anyway.

I bet you need to run a new wire, probably 8/3, which would also mean a 40a breaker as you can no longer have it be welder only. Keeping a 50a breaker will require 6/3, afaik
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,129
Location
NJ
If the oven is higher than 5750 watts, #10 isn't big enough anyway.

I bet you need to run a new wire, probably 8/3, which would also mean a 40a breaker as you can no longer have it be welder only. Keeping a 50a breaker will require 6/3, afaik
That's where I was heading. Once the stove is on the welder circuit, the welder exceptions go away.
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,303
Location
Coastal NJ
If the oven is higher than 5750 watts, #10 isn't big enough anyway.

I bet you need to run a new wire, probably 8/3, which would also mean a 40a breaker as you can no longer have it be welder only. Keeping a 50a breaker will require 6/3, afaik
I agree..... But I didn't see the OP mention having a 50A breaker on the existing welder circuit.
 
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,129
Location
NJ
That's the problem with many threads. There isn't sufficient information given so all one can do is ask q's, guess or assume.
The replies cover the spectrum of "what ifs" and the thread takes a right turn quickly.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,317
Location
Richmond, VA
That's the problem with many threads. There isn't sufficient information given so all one can do is ask q's, guess or assume.
The replies cover the spectrum of "what ifs" and the thread takes a right turn quickly.
This is the internet, not paid-for professional advice. It is how it goes and how it always will
 
OP
X

Xkylescorex

Well-known member
Joined
Jan 10, 2016
Messages
160
I have welder on a 50 amp. After lots of research Im just gonna pony up and do it correctly. Run a direct circuit. Got the oven free off next door so a $40 breaker and $30 for a few feet of 8/3 guess I gotta pay to play
 