Does the landlord have any idea what electric bill he/she is in for once all five tenants install AC and let it run 24/7 without insulation? Whew!

I don't think it will be as bad as you think. The temp inside is actually not bad during the day. I haven't been there at 3 pm yet, but at noon, it's tolerable.
 

BillK

Well-known member
Joined
Aug 24, 2006
Messages
9,368
Location
Beautiful Southern Maryland
My plan is to keep the AC going 24/7, but maybe with the thermostat at 80? Then when I'm there wrenching I can turn it down.
One of my customers installed mine and that is what he told me to do. He said to not even bother turning it up or down. Same with the heat. So I dont :) I really dont think it makes much difference in the electric bill.

You will be surprised at how cool even 80 will feel because it gets rid of the humidity. I keep mine at about 75 and when its in the 80's outside it almost feels cold inside at that temp :)
 
OP
B

bulletpruf

Well-known member
Joined
Nov 28, 2013
Messages
11,140
Location
San Antonio
Ok, so I'm going to go with a pair of mini-splits. The only issue at this point is whether I go with a pair of 2 ton units for $1,100 each or a pair of 3 ton units for $2,000 each.

They'll both be mounted on the back wall; that's really my only option since I'm in the middle unit and I can't place one up front. The outside unit will be on brackets above the ground a few feet.

Any thoughts on 2 or 3 ton?

Thanks,

Scott
 
Last edited:
OP
B

bulletpruf

Well-known member
Joined
Nov 28, 2013
Messages
11,140
Location
San Antonio
Using the BTU calculators online, I'm getting around 4 tons for my space - 20' x 50', 15' ceilings, poor insulation.

The guy who is doing the install thinks I could get away with using a single 3 ton, but I like the idea of going with a pair of 2 ton units.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,962
Location
Richmond, VA
Won't hurt to go bigger as Mini splits are inverters and will vary output, but a $2k difference isn't nothing.

I'd be tempted to do a single 3k and see how it does. Then add another as needed.

Wonder if you could get the landlord to split the cost of proper insulation?
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,927
Location
Austin, TX
Ok, so I'm going to go with a pair of mini-splits. The only issue at this point is whether I go with a pair of 2 ton units for $1,100 each or a pair of 3 ton units for $2,000 each.
When I installed, I found that 2 x 24K units were less expensive than a single 48k unit.
I like the idea of 2 units, especially on applications like this where you may need "hurry" cool down, but can run one unit to maintain temperature.

You may find (as I did) that when it's really cold in Texas (you know, 2-4 days every 2 years) that your heat pumps will not keep up... So just be aware.
 
OP
B

bulletpruf

Well-known member
Joined
Nov 28, 2013
Messages
11,140
Location
San Antonio
When I installed, I found that 2 x 24K units were less expensive than a single 48k unit.
I like the idea of 2 units, especially on applications like this where you may need "hurry" cool down, but can run one unit to maintain temperature.

You may find (as I did) that when it's really cold in Texas (you know, 2-4 days every 2 years) that your heat pumps will not keep up... So just be aware.

Yeah, I think 2 x 24k units will run me about $2,700 installed. A 48k unit will cost around $4,300 installed.

I like the idea of having two for redundancy -- if one shits the bed, you still have one operational unit.
 

gregs

Well-known member
Joined
Mar 16, 2007
Messages
1,609
That’s what I have. It sorta allows you to have multi stage. In the fall and spring running 1 is sufficient and works better to remove the humidity than a bigger one running short times because it’s reaching its set point temperature.
 

LXCam

ALLIANCE MEMBER
Joined
Apr 23, 2013
Messages
19,209
Location
AZ
Congrats on the shop scott. I’d go with two units for the same reason you just posted, redundancy. Plus the air flow will be much better depending on where your work area ends up being.
 

TxSteve

Well-known member
Joined
Aug 22, 2023
Messages
121
Location
Granbury, Texas
That’s what I have. It sorta allows you to have multi stage. In the fall and spring running 1 is sufficient and works better to remove the humidity than a bigger one running short times because it’s reaching its set point temperature.
This is what I have also for the same reasons
 

djkurious

Member
Joined
Jul 28, 2020
Messages
9
Location
Home
I have a 36x32 shop with open cell foam and triple-insulated doors. 36k senville (2- 18k units) and when it's close to 100 degrees outside I can almost get it to 65 degrees.
The sun is on the doors around noon and it seems to not bother the garage.
I'm in Tennessee.
 

TxSteve

Well-known member
Joined
Aug 22, 2023
Messages
121
Location
Granbury, Texas
I have a 36x32 shop with open cell foam and triple-insulated doors. 36k senville (2- 18k units) and when it's close to 100 degrees outside I can almost get it to 65 degrees.
The sun is on the doors around noon and it seems to not bother the garage.
I'm in Tennessee.
I kind of wish I'd gone with open cell under the roof. Closed cell does nothing to dampen the rain noise.
 

930dreamer

Super Moderator
Staff member
Joined
Oct 7, 2009
Messages
22,993
Location
Amarillo,TX and Stinnett,TX
Ok, so I'm going to go with a pair of mini-splits. The only issue at this point is whether I go with a pair of 2 ton units for $1,100 each or a pair of 3 ton units for $2,000 each.

They'll both be mounted on the back wall; that's really my only option since I'm in the middle unit and I can't place one up front. The outside unit will be on brackets above the ground a few feet.

Any thoughts on 2 or 3 ton?

Thanks,

Scott
3 ton, if you build later you'll have a good start in the hvac. That first year's lease and A/C is a chunk of dough. Does each shop have its own power service?
 
Last edited:
To avoid these ads, REGISTER NOW!
OP
B

bulletpruf

Well-known member
Joined
Nov 28, 2013
Messages
11,140
Location
San Antonio
3 ton, if you build later you'll have a good start in the hvac. That first year's lease and A/C is a chunk of dough. Does each shop have its own power service?

The power is potentially an issue. There's a 200A box on the back of the building that services all 5 units. Each 20' x 50' unit has a 125A box.

I'm not an electrician, but I think the main box should be 400A. Thinking about installing a 200A box in my unit, but not sure that this makes sense given the 200A box for the entire unit.

Thanks
 

TxSteve

Well-known member
Joined
Aug 22, 2023
Messages
121
Location
Granbury, Texas
The power is potentially an issue. There's a 200A box on the back of the building that services all 5 units. Each 20' x 50' unit has a 125A box.

I'm not an electrician, but I think the main box should be 400A. Thinking about installing a 200A box in my unit, but not sure that this makes sense given the 200A box for the entire unit.

Thanks
My 24k mini splits spec a max 30A breaker.

For a general shop - I can't imagine you'll ever need more than 125A. I've got 100A going to mine, and never have issues.
 

MoonRise

Well-known member
Joined
Nov 5, 2010
Messages
4,031
Location
NJ
For power, look into what machines and equipment you have now and also what you might add on soon/later.

Two minisplits each with 30A 240V double pole breakers is four panel slots right there.

Air compressor, anything 'decent' and you are using another two panel slots for a 240A breaker.

Welder? Another two slots for the 240A breaker.

Lighting? Suggest at least separate two circuits.

Utility or general use outlets? Again, at LEAST two separate circuits.

Already up to 12 slots in the breaker panel.

Landlord paying the electrical? Put in an EV charging station. :lol_hitti That's another 2 panel slots for the two-pole 240V breaker.

Make sure you have enough slots in the panel! Some 125A subpanels only have 8/16 slots.

Barring trying to run a big old transformer-based 'industrial' welder, you can run a big/decent 'modern' welder on a 50A 240V breaker. Again, short of full-out 'industrial' type stuff.
 
OP
B

bulletpruf

Well-known member
Joined
Nov 28, 2013
Messages
11,140
Location
San Antonio
For power, look into what machines and equipment you have now and also what you might add on soon/later.

Two minisplits each with 30A 240V double pole breakers is four panel slots right there.

Gotcha. Install on these will happen in the next several days.

Air compressor, anything 'decent' and you are using another two panel slots for a 240A breaker.

Ok, haven't figured out whether I'm moving my 80 gallon Quincy from home or not, but I'll have a big compressor one way or the other.

Welder? Another two slots for the 240A breaker.

Running a Miller 211, so I'll need 240 for it.

Lighting? Suggest at least separate two circuits.

Utility or general use outlets? Again, at LEAST two separate circuits.

Yep. Will need a few.

Already up to 12 slots in the breaker panel.

Landlord paying the electrical? Put in an EV charging station. :lol_hitti That's another 2 panel slots for the two-pole 240V breaker.

Make sure you have enough slots in the panel! Some 125A subpanels only have 8/16 slots.

This one has 16 slots.

Barring trying to run a big old transformer-based 'industrial' welder, you can run a big/decent 'modern' welder on a 50A 240V breaker. Again, short of full-out 'industrial' type stuff.

Just a Miller 211. Looks like anywhere from 30A - 50A will work, so I'll go with 50A.

Thanks
 

MoonRise

Well-known member
Joined
Nov 5, 2010
Messages
4,031
Location
NJ
Two minisplits on 30A breakers should be max 24A draw each. That's 48A right there.

Air compressor kicks on, maybe another 24A for that (not counting in-rush current when the motor first kicks on).

And you are welding at the same time. Maybe another 20A there if you are running the 211 hard.

That's about 90A current being pulled just there. And that's a use case easily done by just one person in the shop. With no lights or other things being run at the same time. Air fan to blow some air around to cool you off or get the welding fumes away from your face, a fridge for a cool drink, etc.

125A doesn't necessarily go that far when you add in HVAC to the shop space and just a couple of amp-hungry devices like a welder and a bigger air compressor. Just an FYI and to be aware of how quickly the amps can add up even with just one person in the shop.
 

racecougar

Well-known member
Joined
Jan 26, 2021
Messages
5,190
Location
Missouri
Yep. That's further justification for improving insulation, at least in cases when you own the building and have to pay the electric bill. I run a single 24k unit in my 30'x60'x13', often times while running the air compressor, welding, etc. While I'd love to have more, I only have 60A service. It has not posed a problem (never kicked out) in the five years that I've been working out there. Good insulation and envelope sealing allows you to get away with far less heating/cooling load.
 
OP
B

bulletpruf

Well-known member
Joined
Nov 28, 2013
Messages
11,140
Location
San Antonio
Two minisplits on 30A breakers should be max 24A draw each. That's 48A right there.

Air compressor kicks on, maybe another 24A for that (not counting in-rush current when the motor first kicks on).

And you are welding at the same time. Maybe another 20A there if you are running the 211 hard.

That's about 90A current being pulled just there. And that's a use case easily done by just one person in the shop. With no lights or other things being run at the same time. Air fan to blow some air around to cool you off or get the welding fumes away from your face, a fridge for a cool drink, etc.

125A doesn't necessarily go that far when you add in HVAC to the shop space and just a couple of amp-hungry devices like a welder and a bigger air compressor. Just an FYI and to be aware of how quickly the amps can add up even with just one person in the shop.

Thanks for the input. Will likely need to unplug the compressor while I'm welding.
 

jcarapet

Well-known member
Joined
May 22, 2017
Messages
280
Location
Texas
I kind of wish I'd gone with open cell under the roof. Closed cell does nothing to dampen the rain noise.
You can get open cell sprayed on top. That's what I did and yeah, made a huge difference.

Thanks for the input. Will likely need to unplug the compressor while I'm welding.
Fair warning that will be an issue if you ever do plasma cutter.

My 33x60x14 has 2" closed cell all around, another 5.5" open cell in roof. 4 ton Mr. Cool with 3 18k heads. Last Summer it couldn't keep up and go below 80 on the hottest days, but otherwise fine. Hoping another round of insulation and some double bubble on the roll up doors will help this year.

Jealous of San Antonio Rent prices
 
OP
B

bulletpruf

Well-known member
Joined
Nov 28, 2013
Messages
11,140
Location
San Antonio
Pallet of stuff showed up a few days ago from Amazon.

73930135900__B7663BF7-71D8-4B54-8842-32A5856054CE.jpg

HVAC crew showed up today to install. Three hombres, but not a ragtag crew. Had the requisite tools and equipment to complete the job. Price to install each unit went up from $350 to $480; according to the boss, they needed more supplies than they expected when they installed a pair of 24k units two doors down.

Not a huge fan of the particle board they hung the inside units on, but if it looks like it's sagging, I'll either brace it or replace it with 3/4" plywood.

IMG_1700.jpg

Took them about 4.5 hours to complete the job. Install looks fine to me, they cleaned up after themselves, and both units working fine.

IMG_1705.jpg

It was 97 in the shop before the install - hot, but not unbearable. Some air circulating would have made it much better. Anyway, temps dropped to 90 before I headed to the house, but if I stayed in the area where the cold air was blowing, it was quite comfortable.

IMG_1701.jpg
 

rharman

Well-known member
Joined
Apr 22, 2012
Messages
8,920
Location
SoCal
The backing boards look square and the units appear to mounted symmetrically relative to the breaker box and outside as well. That's a good sign.

3 guys, 4.5 hours for $480? Sounds like a deal.
 
OP
B

bulletpruf

Well-known member
Joined
Nov 28, 2013
Messages
11,140
Location
San Antonio
The backing boards look square and the units appear to mounted symmetrically relative to the breaker box and outside as well. That's a good sign.

3 guys, 4.5 hours for $480? Sounds like a deal.

Yes, they took some measurements before installation, so they're symmetrical.

It was $480 per unit for a total of $960.

Thanks
 
OP
B

bulletpruf

Well-known member
Joined
Nov 28, 2013
Messages
11,140
Location
San Antonio
That is a JOKE for insulation in TX ! For a metal roof in TX, you need at least 6" of insulation, 12" better !

You can cool it, but you will need a MUCH LARGER A/C !

I really don't think I will need a larger AC. The HVAC guy thought I could have gotten by with a single 3 ton unit, but I went with a pair of 2 ton units instead.
 

TxSteve

Well-known member
Joined
Aug 22, 2023
Messages
121
Location
Granbury, Texas
I really don't think I will need a larger AC. The HVAC guy thought I could have gotten by with a single 3 ton unit, but I went with a pair of 2 ton units instead.
I've got 2" of closed cell all over in my 40x50 with two 24k units. It works great. Laser thermometer on the inside of the roof shows ~80-81 degrees with outside temps in the mid 90s. It's also a white roof.
 

TxSteve

Well-known member
Joined
Aug 22, 2023
Messages
121
Location
Granbury, Texas
Pallet of stuff showed up a few days ago from Amazon.

73930135900__B7663BF7-71D8-4B54-8842-32A5856054CE.jpg

HVAC crew showed up today to install. Three hombres, but not a ragtag crew. Had the requisite tools and equipment to complete the job. Price to install each unit went up from $350 to $480; according to the boss, they needed more supplies than they expected when they installed a pair of 24k units two doors down.

Not a huge fan of the particle board they hung the inside units on, but if it looks like it's sagging, I'll either brace it or replace it with 3/4" plywood.



Took them about 4.5 hours to complete the job. Install looks fine to me, they cleaned up after themselves, and both units working fine.



It was 97 in the shop before the install - hot, but not unbearable. Some air circulating would have made it much better. Anyway, temps dropped to 90 before I headed to the house, but if I stayed in the area where the cold air was blowing, it was quite comfortable.
These are the same units I have. OSB will be fine. The interior units aren't very heavy.

Congrats! I love having the cool work space.
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,927
Location
Austin, TX
If I read the OP's post correctly, I believe he paid $960 for the install. Still quite cheap for the install of two units. Though that install is about as easy as it gets.
Yea, that's cheap. Takes me at least 6 hours to install one of these in a shop.

I see some issues though:
  • Brace that OSB, just like you mentioned, OP. 2x4s should do fine. You can get 2x4s up there between the gurts and frame it behind the OSB. Tie the framing into the gurts with vertical metal-attachment screws.

  • Are these hung on a single screw through the gurt? I'm not a fan. I always use uni-strut between gurts then tie to that.

1718204245467.png

  • Make sure they put the vibration dampners in.. I don't see them, might be there though:
1718204385368.png


  • Get rid of these kit water lines. They are going to plug up. Install 3/4" PVC water lines.
1718204467759.png
 