Having discussions with my inspector about wire size from my house to detached garage. Distance is 225 ft. I have the 2.5" conduit in place.
I will be using a 125A breaker in my house panel to feed the garage.
Based on using some of the online voltage drop calculators, it looks like 4/0 (aluminum xhhw) is what is recommended.
So the wire would be: 4/0, 4/0, 4/0, #4
He says that is overkill. From his email: "1/0 is good for 135amps in the 90 degree column. It also meets your voltage drop percent based on more than actual usage. The choice is yours but 4/0 is overkill and this would save you money and still be code compliant. "
He also states "Also remember that you will never use close to the maximum load on the breaker. At a max at one time you may use 50 amps."
For which I replied " My biggest load being actively used would probably be my Millermatic 252 welder, but I am also thinking future and "non-planned" loads such as HVAC, full size refrigerator, one of my sons using air tools (kicking the compressor on), lights, TV/stereo, etc. Technically they could all be on or start simultaneously - pulling more amps for a short time, correct?"
Having discussions with my inspector about wire size from my house to detached garage. Distance is 225 ft. I have the 2.5" conduit in place.
I will be using a 125A breaker in my house panel to feed the garage.
Based on using some of the online voltage drop calculators, it looks like 4/0 (aluminum xhhw) is what is recommended.
So the wire would be: 4/0, 4/0, 4/0, #4
He says that is overkill. From his email: "1/0 is good for 135amps in the 90 degree column. It also meets your voltage drop percent based on more than actual usage. The choice is yours but 4/0 is overkill and this would save you money and still be code compliant. "
He also states "Also remember that you will never use close to the maximum load on the breaker. At a max at one time you may use 50 amps."
For which I replied " My biggest load being actively used would probably be my Millermatic 252 welder, but I am also thinking future and "non-planned" loads such as HVAC, full size refrigerator, one of my sons using air tools (kicking the compressor on), lights, TV/stereo, etc. Technically they could all be on or start simultaneously - pulling more amps for a short time, correct?"