Hey everyone. I am finally moving away from propane and kerosene heaters. I found a great deal for this TPI F2F5107CA1L heater and I am picking it up tomorrow morning. $100 for 2 of them and my buddy is taking the other one. The guy said they work and are only a year old. The heater will likely cook me out of my well insulated 2 car garage. It's alright I can work in my underwear.
I am not the best at electrical so I want to make sure I get this right. The part that is messing me up is the phasing. It says it is 1/3 phase. I assume that means it can do both.
So correct me if I am wrong. I just had a new panel installed last year and I upgraded my service to 200 amp. Now obviously I need to install a new breaker, which it looks like a 40 amp double pole would be right. Based off of that I should run a 8-2 Romex wire from the panel to a box that will be right near the heater. Then a whip to the box to the heater. Am I right?
Since I am running a single phase will it run at 36.1 amps or 20.8 amps? If it's only running 20.8 amps, it would of course change the gauge wire and breaker.
Fan Forced Suspended Unit Heater TPI F2F5107CA1L Specifications
UPC 686334645201
Power 7.5 KW
BTU / Hr 25.6
VOLTAGE 208 V
PHASE 1 / 3
AMPS 36.1/20.8
Control Voltage 24
Temperature Rise 34 F
Air Throw 22'
CFM 700
Here is a link to the product:
http://www.heater-store.com/fan_forced_unit_heater_tpi_10319_prd1.htm
I am not the best at electrical so I want to make sure I get this right. The part that is messing me up is the phasing. It says it is 1/3 phase. I assume that means it can do both.
So correct me if I am wrong. I just had a new panel installed last year and I upgraded my service to 200 amp. Now obviously I need to install a new breaker, which it looks like a 40 amp double pole would be right. Based off of that I should run a 8-2 Romex wire from the panel to a box that will be right near the heater. Then a whip to the box to the heater. Am I right?
Since I am running a single phase will it run at 36.1 amps or 20.8 amps? If it's only running 20.8 amps, it would of course change the gauge wire and breaker.
Fan Forced Suspended Unit Heater TPI F2F5107CA1L Specifications
UPC 686334645201
Power 7.5 KW
BTU / Hr 25.6
VOLTAGE 208 V
PHASE 1 / 3
AMPS 36.1/20.8
Control Voltage 24
Temperature Rise 34 F
Air Throw 22'
CFM 700
Here is a link to the product:
http://www.heater-store.com/fan_forced_unit_heater_tpi_10319_prd1.htm