Installing stand by generator
Don1357
Palmer, AK
I'm self installing a small stand-by generator just to protect the boiler and critical circuits during winter storms. I'm in Alaska outside of city limits, I don't have to pull any permits. Looking at the installation manual it is missing quite a bit of info, mainly the stuff they assume would be done by an electrician. I'm hoping you guys will help me fill in those gaps.
The unit in question is the Generac 7.5kwh propane/6kw natural gas generator (the baby one). The installation seems pretty simple; the generator (outside of the house) powers the transfer switch box (inside of the house). Said box has 8 circuits it protects (not a whole house standby generator, just those), a 50 amp circuit then connects the transfer switch box to a 50 amp breaker on the main house panel. When things are good, power comes from the regular house electrical panel. When power drops the generator senses it, fires up, and the circuits on the transfer switch box are juiced up. When power is restored, the generator turns off and power is again supplied from the house panel.
First question: The manual doesn't even specify the wiring size, so being on a 50 amp circuit it should be 6 AWG copper? Total run is probably about 40 feet.
Second question: What kind of conduit should I use?
Thanks in advance.
mm08822
#6 copper works for the 50a.
I would run 1-1/4" minimum. 1.5" ok also. Sch 40 pvc, depends how easy run is and your ability. May prefer FNMC in same size.
D
Don1357
Palmer, AK
The run should be fairly straight forward, I'm yet to find out if where I want it I'm going to hit wood or the poured foundation. That would make it a tad less fun but doable.
Can Romex come out of the house if it is in the conduit or do I need to use an outdoor rated wire?
My last writing job was to bring a 100amp service to the workshop. I dug the trench, installed the panel on the workshop, installed the box to do the split next to the main service, did the wiring, and then paid the electrician to do the final hookup into power. I should be able to tackle this one as I can readily disconnect power while I work.
HamAndEggs
Houston, TX
I would run larger wire just incase you decide to upsize the generator
I went with a 27kw unit and don't regret it now I have an EV too
D
Don1357
Palmer, AK
This is strictly for emergency winter power and honestly it is only an emergency if I'm not here. We get wicked wind storms, two years ago while I was gone power went out for over a day, long enough for frozen pipes and water fountains... If I'm here is not an issue, I just burn wood.
D
Don1357
Palmer, AK
So... Can I bring the Romex outside if it is inside of the conduit? Or would I need a different cable?
mm08822
Romex in exterior conduit not permitted.
Your xfer panel should require 2 connections:
To panel
To gen
Depending on model that you have it may already include conductors in flexible conduit that terminates in an exterior jbox. From the jbox to gen there should be LFMC with individual conductors.
Post model #s.
D
Don1357
Palmer, AK
Generac 7.5kw ds-6808. On the installation manual, the entirety of the information about the hot wiring side is this:
"Note: Main AC wiring must be in accordance with local jurisdiction and codes."
Page 28 here:
Basically at the point it comes out of the house more conduit would continue for about 20 feet before it ends up next to where the generator will be. So I'm thinking junction box there and from junction box to generator.
The other type of cable I'm seeing is 6/3 UF-B Wire, Underground Feeder and Direct Earth Burial Cable. Can I run that on conduit inside and out?
Sumboodie
AK
Can bury UF without conduit.
Otherwise use THHN in conduit, no sense fussing with UF.
That windstorm was bad, had no power for 5 days, barely kept the garage freezing up by keeping the door open between house and garage. All my utilities in the garage, so freezing up would have been bad.
But then stove was only keeping house around 60*.
A buddy came home from the slope to a helluva mess when pipes froze then thawed when power came back.
I picked up an 8k a couple weeks ago for auto backup. Haven't messed with it yet, likely won't happen before winter.
PCustoms
VT
I would run individual strands of Xhhw-2 or thwn
4 lengths of the correct size should run about $1.50/ft. UF is close to $5/ft and ***** to work with IMHO.
How are you trying this into your panel in the house? Is there a standalone panel inside?
Most auto setups I've seen have the main feed from the grid nter the transfer switch, then the feed goes to the house. It sounds like your are feeding just 50A from generator to house, somewhere you have to transfer/lockout the grid power feed
dcg9381
Austin, TX
As others have mentioned Romex is not allowed in conduit. I may or may not know of someone who has bent this rule before.
1.25" conduit sounds good to me minimum. Around here, 1.25" there is a lesser selection of it, so I'd choose 1.5" or 2".
6AWG copper will typically do 50-60A, but I agree with others, 6AWG XHHW-2 Wire is a lot less expensive. I'd probably do 4AWG of the same stuff just for future proof.
One thing to watch - you can get 600V rated "control wire" - I think it's 7 wires (off the top of my head) which are the ATS / generator control wires. Right wire you can run in the same conduit as the power wire. It's pretty think stuff.
larry4406
Northern Virginia
Here it is. Pretty cool stuff, all in one pull. Direct burial, freewire like Romex, etc.
D
Don1357
Palmer, AK
Fantastic, thank you guys for setting me on the right path. I'm going with these:
And a spool of these for the control wire:
It wasn't pretty when I came back...
You should try to make some progress this year. This is basically a 4-part project; 1-foundation and placement of the generator, 2-tapping the natural gas and running the line, 3-running the electrical inside of the house and into the transfer panel, 4-wiring it all up together. The whole project may be quite a bit of effort but each discrete part is not that bad.
This weekend I want to pour the slab and get the parts I'll need to tap into the gas line. I may even get around to install those.
dcg9381
Austin, TX
Nope. Not unless you want to run that in a separate conduit. That's advertised as "18/5 Low Voltage LED Cable". I doubt it's even UL listed. It's also a wire short of what you need.
Better check how many control wires your generator takes. I believe that Generac's need 6 wires. I think you need something like this:
not quite. its not allowed in conduit OUTDOORS. NM-b can be ran in conduit INDOORS
mm08822
If you are pulling all of this to the gen in a single conduit, having all individual conductors is easiest than dealing with a cable or two.
3 - #4 AL XHHW (one taped white)
1 - # 6 AL XHHW green ( or make it #4 also and tape green - then only 1 wire size to purchase)
and
6 - #14 THHN/THWN Cu (N1, N2, T1, 194, 23 and 0) Add the "0" conductor for troubleshooting - it is your dc common from gen back to xfer switch. You will never have a problem with #14 cu for control/sense lines.
This all fits nicely in one 1-1/4" conduit.
mm08822
It only needs 5 if run in the same conduit as power as the grd can be shared.
The w/d doesn't require "0" which is dc common (6th conductor). I would pull it for troubleshooting purposes.
The cable OP picked was rated for 300V so it would be fine in this application. UL listing is questionable.......if it's not mentioned, assume it is not - amazon neglects minor details - buyer beware!! Regardless, I would pull individual conductors.
dcg9381
Austin, TX
Guys, thanks a lot, your time and effort is truly appreciated. The "installation manual" is pretty much worthless on this.
Well, generac probably wants you to buy their cable.
Wire and Cable Your way. Someone else can double check this for the use case, but as it's approved for "wet" I assume it can be used in conduit with the primary conductors:
D
Don1357
Palmer, AK
My bump on the road is that a lot of places either don't ship to Alaska or charge more for shipping than the cable itself... This is why I try to find things on Amazon, at least I don't have to keep giving my info on a bunch of random places just to find out they won't ship it :-\
I'll see if I can hunt down a THHN wet/dry rated cable.
PCustoms
VT
I asked this before, but what does the panel look like that you will be installing inside?
How does the generator get isolated from the grid power?
D
Don1357
Palmer, AK
The explanation was on the very first post. Generator has a power switch box that goes next/near your regular breaker panel. That box has 8 breaker slots for the stuff you want to protect. One feed goes to the generator, one feed to a 50amp breaker on your breaker box. When there is house power your breaker box does the work. When power goes off the generator senses it, starts, and provides the power to the switch box.
theres a reason some of that is cheap.... buyer beware
mm08822
Make this easy on yourself.......buy a 500 ft roll of #14 stranded black or red thhn/thwn from Home Depot. Color code the wires with colored tape or number them.
Romex buried in conduit must still be rated as UF,
If you are going to install conduit, save time and money and use THWN individual strands. You can transition to Romex at a junction box inside the outer wall or run conduit inside.
romex is a brand of NM-b NOT UF-b