These are the taps you can use for #12 feeding through strip fixtures with a #18 ballast lead:
http://www.newark.com/jsp/search/productdetail.jsp?SKU=90F6225&CMP=AFC-GB100000001
I like them for a new install, don't really care to come back to them for ballast changes, because I don't like to splice the tap, just my opinion. New fixtures do come w/ ballast disconnects so that is in most cases a moot point & I think the 2011 NEC requires them to be used when servicing existing ones, but since on the '08 not sure about that one.
Edit:
410.30(G)(1) does require it in other then residential & assoc. structures.
(G) Disconnecting Means.
(1) General. In indoor locations other than dwellings and
associated accessory structures, fluorescent luminaires that utilize
double-ended lamps and contain ballast(s) that can be
serviced in place shall have a disconnecting means either internal
or external to each luminaire. For existing installed luminaires
without disconnecting means, at the time a ballast is
replaced, a disconnecting means shall be installed. The line
side terminals of the disconnecting means shall be guarded.
Exception No. 1: A disconnecting means shall not be required
for luminaires installed in hazardous (classified)
location(s).
Exception No. 2: A disconnecting means shall not be required
for emergency illumination required in 700.16.
Exception No. 3: For cord-and-plug-connected luminaires,
an accessible separable connector or an accessible
plug and receptacle shall be permitted to serve as the disconnecting
means.
Exception No. 4: A disconnecting means shall not be required
in industrial establishments with restricted public
access where conditions of maintenance and supervision
ensure that only qualified persons service the installation
by written procedures.
Exception No. 5: Where more than one luminaire is installed
and supplied by other than a multiwire branch circuit,
a disconnecting means shall not be required for every
luminaire when the design of the installation includes disconnecting
means, such that the illuminated space cannot
be left in total darkness.
(2) Multiwire Branch Circuits. When connected to multiwire
branch circuits, the disconnecting means shall simultaneously
break all the supply conductors to the ballast,
including the grounded conductor.
(3) Location. The disconnecting means shall be located so
as to be accessible to qualified persons before servicing or
maintaining the ballast. Where the disconnecting means is
external to the luminaire, it shall be a single device, and
shall be attached to the luminaire or the luminaire shall be
located within sight of the disconnecting means.
2011 NEC
Since most folks here are wiring home shops, this is not required but I have come to like the ballast disconnects, but that is just my opinion again.