An electrician friend of mine thinks my garage subpanel is against code. It was installed in early to mid 2017 and has been inspected, twice. I recall it was inspected once under 2014 code and once under 2017 code.
I installed a 200 amp main lug panel in the garage with four wire feed, no bond, and grounds/neutrals separated. It is fed by a 70 amp breaker in the main panel in the house. The wires for the feed are 3 AWG copper. The garage subpanel has a 70 amp breaker installed as the main breaker with the proper hold down kit.
My electrician friend claims because I have a 200 amp panel in the garage that I must have a 200 amp feed to the panel because it has a 200 amp bus. He says it is a code violation. I disagree because I have installed a 70 amp breaker at each end with appropriate wire and it has been inspected. Is this a code violation, or is my electrician friend smoking something funny?
I installed a 200 amp main lug panel in the garage with four wire feed, no bond, and grounds/neutrals separated. It is fed by a 70 amp breaker in the main panel in the house. The wires for the feed are 3 AWG copper. The garage subpanel has a 70 amp breaker installed as the main breaker with the proper hold down kit.
My electrician friend claims because I have a 200 amp panel in the garage that I must have a 200 amp feed to the panel because it has a 200 amp bus. He says it is a code violation. I disagree because I have installed a 70 amp breaker at each end with appropriate wire and it has been inspected. Is this a code violation, or is my electrician friend smoking something funny?