with a junction box each conductor needs I believe 2.5 cu in of area and the grounds need 2.5. what are considered conductors both the black and white?
so if I have 2, 12 -2 romax wires running into a j-box I have used up 12.5 cu in of my box?
Jay D.
 
To avoid these ads, REGISTER NOW!
To avoid these ads, REGISTER NOW!

Cmreschke

Well-known member
Joined
Feb 15, 2014
Messages
775
Location
North of Detroit
with a junction box each conductor needs I believe 2.5 cu in of area and the grounds need 2.5. what are considered conductors both the black and white?
so if I have 2, 12 -2 romax wires running into a j-box I have used up 12.5 cu in of my box?
Jay D.

Correct. Except 12 guage is 2.25 cu in. 10 guage is 2.5. 14 guage is 2.0
 