Friends house is kicking a breaker. Breaker appears to be lightly loaded with 2 fluorescent lights and a couple of incandescent lights.

The kicker is, the load center/breaker box is on a pole about 40 feet from the house. All the circuits are run with ROMEX, underground in plastic 2"+ conduit to the house. He has already abandoned one ROMEX line and moved the circuit to a spare. Now it is kicking the breaker again.

I figure the best move would be to set a load center on the end of the house where the ROMEX comes up from underground and treat it as a subpanel. Then abandon all the underground ROMEX and run a 100 amp underground feeder to the new load center.

So what are the odds that all that old ROMEX is going bad underground? It has probably been there 20 years.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,074
Location
Modesto, CA
Came on here thinking someone was kicking breakers with their foot.

Proper term is TRIPPING

Yikes.

Rip all that out and run a feeder.

Are you sure its Romex, aka NM-b?

What color is it?
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
If it is indeed Romex then it's a good chance that moisture has gotten in it and causing a random short. I had to fix the same problem on an old house that had a Romex feeder run to a detached garage underground in conduit. The conduit collected water and the Romex failed, but the Romex managed to work for over 15 years before failing.
 

shadycrew31

Well-known member
Joined
Jun 23, 2017
Messages
58
Location
Burbs of Philly
Dumb question, are you sure there isn't a short in one of the loads thats being fed by the line, or that the breaker isn't failing? Seems strange that two lines failed...
 

rpcraft

Well-known member
Joined
Aug 14, 2014
Messages
1,057
Location
Waco
Just a thought, have you tried swapping out the breaker? Maybe with a new one or one that is known not to be tripping previously?
 
To avoid these ads, REGISTER NOW!

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,752
Location
SE Michigan
If I read right, every circuit has an additional 40 feet of underground wiring between the remote panel and the house (?)

If so, that seems like a large waste of wire plus the obvious no-no of putting NM-b underground.

I like your idea to relocate the load center, pull THHN underground and land the existing circuits on the new load center. I would also negotiate rights to the scrap copper as I think there will be a bit of it :)
 

Bretny

Well-known member
Joined
Jul 31, 2017
Messages
3,918
Location
Dutchess county NY
If its tripping the breaker with no loads and you put a new breaker in it sounds like a new feeder is needed. Your DVOM should tell you this.
 

toplessHO

Well-known member
Joined
Oct 20, 2014
Messages
14,089
Location
central florida
we used to have a machine called a thumper for finding faults in underground direct burial feeders
You could actually see the dirt jump in the spot it was bad.
not that you would need something like this,its just triggered another old memory
 