Friends house is kicking a breaker. Breaker appears to be lightly loaded with 2 fluorescent lights and a couple of incandescent lights.
The kicker is, the load center/breaker box is on a pole about 40 feet from the house. All the circuits are run with ROMEX, underground in plastic 2"+ conduit to the house. He has already abandoned one ROMEX line and moved the circuit to a spare. Now it is kicking the breaker again.
I figure the best move would be to set a load center on the end of the house where the ROMEX comes up from underground and treat it as a subpanel. Then abandon all the underground ROMEX and run a 100 amp underground feeder to the new load center.
So what are the odds that all that old ROMEX is going bad underground? It has probably been there 20 years.
The kicker is, the load center/breaker box is on a pole about 40 feet from the house. All the circuits are run with ROMEX, underground in plastic 2"+ conduit to the house. He has already abandoned one ROMEX line and moved the circuit to a spare. Now it is kicking the breaker again.
I figure the best move would be to set a load center on the end of the house where the ROMEX comes up from underground and treat it as a subpanel. Then abandon all the underground ROMEX and run a 100 amp underground feeder to the new load center.
So what are the odds that all that old ROMEX is going bad underground? It has probably been there 20 years.
Not strange at all if the are Romex and were run at the same time.