Hi All,

Needed your advice. Just had a 16x30 Monolith foundation poured for our future garage. Forgot to mention that this will be a TuffShed Garage so can't make changes. Took a few months to get approved sadly.

The concrete guy didn't set the L bolt down far enough. His reasoning was he thought I was doing double bottom plate. I double check the building plans and see that it just single plate.

So now the issue is there isnt enough threads for the nut and washer to reach.
I tried to run a 1/2-13 die but the diameter of L bolt is more narrow than threads above. So once the nut gets to the new thread it just falls.

My thoughs where
1.) Have then cut a block for each anchor
Or
2.) Use couplers instead of normal nut
 
Last edited:
To avoid these ads, REGISTER NOW!

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
31,942
Location
Coronado, CA
If the diameter of the bolt below the threads is too small to cut new threads to securely tighten the nut, why not use a coupling nut and thick washers?
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,487
Location
Richmond, VA
I think your blocks will need to be fairly wide to avoid splitting them. If a double bottom plate is doable, I'd try to go that way. Only the bottom layer needs to be PT.

This could also allow you do set the mudsill with foam and sealant, then place the fully assembled wall on top, which may be easier than messing with the foam while handling the whole wall assembly
 
OP
L

longlv85

Member
Joined
Oct 16, 2022
Messages
22
64 more feet of lumber? Jeez man just put the green plate down first and buy 6 more kd 16 footers and have a better building.
I wish it were that easy. Tuffshed is building it and getting last minute changes might require zoning and building approval agian. It was a nightmare to even get this far.
 
OP
L

longlv85

Member
Joined
Oct 16, 2022
Messages
22
I will see if they can modify the plans. If not sounds like a 2x4 spacer is my next best solution. Thanks all for the advice. Looking forward to learning more and sharing my project once it is all done.
 

BillK

Well-known member
Joined
Aug 24, 2006
Messages
9,320
Location
Beautiful Southern Maryland
How about just putting some round spacers on the bolt before the nut ???? Something like this but it does not need to be this expensive.

 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,487
Location
Richmond, VA
How about just putting some round spacers on the bolt before the nut ???? Something like this but it does not need to be this expensive.

It would have to have a much larger OD to work and I would be surprised if that was allowed by an inspector
 

BillK

Well-known member
Joined
Aug 24, 2006
Messages
9,320
Location
Beautiful Southern Maryland
It would have to have a much larger OD to work and I would be surprised if that was allowed by an inspector

As long as the spacer was the same od as the nut I dont see what difference it would make. The one I showed was just for an example. Personally I would rather have the spacer compared to another piece of wood. the spacer wont compress. It would have to be approved by the inspector and I don't know what they would say.

I think a call to Tuffshed might be in order too. I'm sure they have run into this before and would know what to do. Especially if they are actually building it.
 

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,963
Location
Thousand Islands NYS
It would have to have a much larger OD to work and I would be surprised if that was allowed by an inspector
It would seem to only need to be as big as the nut, to put pressure on the washer. I thought pieces of 1/2" galvanized schedule 40 against the washer would be sufficient. Or get the washers liked used in a portal frame - 3 x 3 x 1/4 plates. Simple and not bad looking.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,487
Location
Richmond, VA
It would seem to only need to be as big as the nut, to put pressure on the washer. I thought pieces of 1/2" galvanized schedule 40 against the washer would be sufficient. Or get the washers liked used in a portal frame - 3 x 3 x 1/4 plates. Simple and not bad looking.
Yeah, fair enough. I was being dumb and didn't think of the washer below it.

I still wonder if it would pass an inspection. Not sure if there is an allowable limit to the "washer length"
 

619DioFan

Well-known member
Joined
Apr 9, 2013
Messages
3,617
Location
San Diego , Ca.
Is the shed being delivered assembled? Be pretty hard to add a second bottom plate , making a spacer out of wood is my suggestion.
 
To avoid these ads, REGISTER NOW!
OP
L

longlv85

Member
Joined
Oct 16, 2022
Messages
22
Why? He could just install a plate now then they place the shed on that instead of the concrete

If I installed a place now It would put me over the max allowable height for the town. Which would require another Variance. If I applied now my hearing wouldn't be for another 2 months. I had to fight to be able to get this now. lol.
 

Sumboodie

Well-known member
Joined
Mar 20, 2021
Messages
10,676
Location
AK
Double plate is ideal. PT bottom and regular top. Gives much more room to nail the OSB or drywall, as you want to keep it off the floor a good 1/2-3/4". Aside from a bit more $$, there's no reason not to that I can think of.
 
OP
L

longlv85

Member
Joined
Oct 16, 2022
Messages
22
Double plate is ideal. PT bottom and regular top. Gives much more room to nail the OSB or drywall, as you want to keep it off the floor a good 1/2-3/4". Aside from a bit more $$, there's no reason not to that I can think of.
Yea thats make sense. I wonder if they only do single plate because the foundation sits 6" from grade1666027888087.png
 

Sumboodie

Well-known member
Joined
Mar 20, 2021
Messages
10,676
Location
AK
If I installed a place now It would put me over the max allowable height for the town. Which would require another Variance. If I applied now my hearing wouldn't be for another 2 months. I had to fight to be able to get this now. lol.
Wow, that's a some tight limits if 1.5" higher is something even noticed!
 

Sumboodie

Well-known member
Joined
Mar 20, 2021
Messages
10,676
Location
AK
Yea thats make sense. I wonder if they only do single plate because the foundation sits 6" from grade1666027888087.png
Yeah having a stem wall it's not so much a problem. I had in mind it was going on a flat slab. In that case, I'd just put some blocks to take up the space. The bolts are there to mostly hold for uplift.
I've worked on many buildings that they had just framed on the slab and the only thing holding it was gravity. Generally over the years the walls tend to move though, sometimes off the slab even.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,487
Location
Richmond, VA
I thought about that but won't that kill the value of them being galvanized?
The stuff touching the PT would still be galvanized which is what matters. The top could be hit with a little spray paint if desired, but if they ruse enough to be a problem, you have major water issues otherwise
 

Monza Harry

Well-known member
Joined
Dec 29, 2018
Messages
1,433
Location
Windsor ON
Mick and longlv85, that would seem like a likely answer but these are probably a rolled thread and a non-nominal dia. If I did my math right they would be very close to 11mm which is also very close to 7/16". 7/16"-14 isn't that easy to find at the corner hardware store (possible, but maybe not easy), but easier than 7/16-20 which would be a little stronger but less friendly to cement splashes. Your diagram in post 22 is a good fix and doesn't derate the studs strength or ruin the coating like Bill mentioned. Harry
 

strutaeng

Well-known member
Joined
Dec 12, 2011
Messages
2,263
Location
Dallas, TX
I used extra long j bolts for an addition I did. The framers framed their walls and used shot pins. I came behind with PT blocking (a lot of it was scraps anyway) and installd those large square bearing plates, washers and nuts.

I was going to install taller baseboards and wanted to have more nailing on the sill plates. Was slow, but turned out good when I was nailing baseboards.
 
Last edited:

readhead

Well-known member
Joined
Dec 8, 2012
Messages
6,177
Location
Durango, Co.
Having suffered through being a Tuff shed dealer I know that they will not deviate from the plan. Have some 2x material on hand and make the spacers yourself. Make the spacer the width of the stud bay so it looks like it belongs.

Be patient. Keep in mind that the guys that show up are not carpenters. They are shed installers. It was a garage that finally made me quit Tuff shed. They did not line and brace any of the walls so when they set the trusses the roof followed the curve in the walls. Ultimately the whole roof including the trusses had to be removed and replaced by order of the building inspector. After three failed inspections they finally won on the fourth.

I’m only bringing this up to suggest that you watch the process carefully from beginning to end to make sure that you get a plumb, level and square building. One major thing to watch for is the roofing. If you are having shingles installed their policy is to cut the shingles flush with the drip edge rather than extending past. Force the issue and don’t let them do that. If they don’t agree simply show them the instructions on the bundle. Oddly enough roof sheeting damage and rot is their number one warranty claim. Also they install all the drip edge and then the felt. The drip edge on the rake goes on after the felt.

If you watch the process things should go well. Don’t hesitate to ask questions if you see something you don’t like.
 
OP
L

longlv85

Member
Joined
Oct 16, 2022
Messages
22
Just wanted to follow up on this thread to show the garage. What they ended up doing was cut off all the old anchors and install new ones.They have to come back and paint the trim and install the garage door.


Timelapse of the build


20221116_141756.jpg20221116_141817.jpg20221116_141739.jpg
 
Last edited:

finn

Well-known member
Joined
Mar 27, 2005
Messages
16,227
Location
The UP, God's country
Adding a doubl bottom plate would be a pretty big job for a factory built shed outfit. It would force cutting all of the studs shorter, and adjusting the doors, or adding taller siding / wall panels.

That’s not going to happen with a factory shed.

Just add 2x4 spacers as others have proposed.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,487
Location
Richmond, VA
Adding a doubl bottom plate would be a pretty big job for a factory built shed outfit. It would force cutting all of the studs shorter, and adjusting the doors, or adding taller siding / wall panels.

That’s not going to happen with a factory shed.

Just add 2x4 spacers as others have proposed.
The post immediately above yours shows the shed installed
 
OP
L

longlv85

Member
Joined
Oct 16, 2022
Messages
22
Adding a doubl bottom plate would be a pretty big job for a factory built shed outfit. It would force cutting all of the studs shorter, and adjusting the doors, or adding taller siding / wall panels.

That’s not going to happen with a factory shed.

Just add 2x4 spacers as others have proposed.
They rolled up with whole garage on a trailer.
 

Attachments

  • 20221115_075309.jpg
    20221115_075309.jpg
    511.3 KB · Views: 55

readhead

Well-known member
Joined
Dec 8, 2012
Messages
6,177
Location
Durango, Co.
So that was an approved change to the plans? I see that they cut off the hold down bolts. That generally requires an engineer approved change. Hopefully it all works out well for you.
 

Wolley

Well-known member
Joined
Jun 24, 2022
Messages
420
Location
Maine
Expandable anchors seems like a good option for a building of this nature.
 
To avoid these ads, REGISTER NOW!