1 inch sch40 PCV conduit can take four #4 Cu THWN-2 which is rated at 85 amps at 75 degrees C. Other wire types will be less, such as RHH/RHW is four #8 Cu which is 50 amps @ 75 deg C.
 
Last edited:
OP
M

Mike Honcho

Well-known member
Joined
Mar 17, 2009
Messages
163
Location
SE Michigan
1 inch sch40 PCV conduit can take four #4 Cu THWN-2 which is rated at 85 amps at 75 degrees C. Other wire types will be less, such as RHH/RHW is four #8 Cu which is 50 amps @ 75 deg C.

thanks patten, i assume that sch 80 will cut that down some? i was looking to run 60 amp with it. it was already there when i bought the house. if not ill use it for something else.
 

Highbeam

Well-known member
Joined
Feb 15, 2011
Messages
2,292
Location
Mt Rainier foothills, WA
I just pulled 70 feet of wire through 1" conduit this weekend. It was only 2-#8 and 1-#10 (all THHN-THWN-THWN2 multi rated as I recall) and it went okay but the 4-90 degree bends made lube necessary. In a "dry" location it would appear that the #8 is rated for 55 amps which you can round up to 60. Of course you'll need 3-#8s and a 10 guage.

Just because you can does not mean it will be easy.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
For 60A use THHN/THWN-2, three #6 Cu and one #10 Cu for the equipment ground. That will fit nicely in sch80 PVC.

#8 THHN/THWN is not 55A, it's 50A @ 75 deg. C.

thanks patten, i assume that sch 80 will cut that down some? i was looking to run 60 amp with it. it was already there when i bought the house. if not ill use it for something else.
 
Last edited:

rockwithjason

Well-known member
Joined
Jan 8, 2006
Messages
2,633
Location
Las Vegas
1 inch sch40 PCV conduit can take four #4 Cu THWN-2 which is rated at 85 amps at 75 degrees C. Other wire types will be less, such as RHH/RHW is four #8 Cu which is 50 amps @ 75 deg C.

yup your right, i goof brained and read the wrong column
 
To avoid these ads, REGISTER NOW!

Highbeam

Well-known member
Joined
Feb 15, 2011
Messages
2,292
Location
Mt Rainier foothills, WA
Just brought up the HD chart since it was there and a surprising amount of work gets installed based on that chart. So are you saying the chart is wrong?

I stuck to 50 amps on 8 gauge thwn-2, which jives with pattenp's advice. Pattenp has been very helpful to me and others on this forum and I never said he was wrong.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I never took it as being said I was wrong. I try my best to give correct information, but being human I do get things wrong at times. It's always good to question information and to do some research to make sure the info you are receiving is consistent.

I need to take a look at that HD chart.

Just brought up the HD chart since it was there and a surprising amount of work gets installed based on that chart. So are you saying the chart is wrong?

I stuck to 50 amps on 8 gauge thwn-2, which jives with pattenp's advice. Pattenp has been very helpful to me and others on this forum and I never said he was wrong.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Just went to HD and their chart does show what the NEC table has for #8 THHN which is 55 amps @ 90 degrees C. The catch is even though technically THHN is a dry location rating and is listed in the 90 degree C column the terminal connections on devices such as breakers are only rated at 75 degrees C, so you need to size the conductor by 75 degrees C. I think it's misleading to the unknowing DYI'er who looks at that chart and may think it's okay to use THHN at the amps for 90 degree C. I also stopped at Lowes and checked their chart and it only list the 60C or 75C amp ratings for the different wire. So the #8 THHN is shown as 75C for 50 amps.
 

mdd1986

Well-known member
Joined
Jun 7, 2013
Messages
52
Just went to HD and their chart does show what the NEC table has for #8 THHN which is 55 amps @ 90 degrees C. The catch is even though technically THHN is a dry location rating and is listed in the 90 degree C column the terminal connections on devices such as breakers are only rated at 75 degrees C, so you need to size the conductor by 75 degrees C. I think it's misleading to the unknowing DYI'er who looks at that chart and may think it's okay to use THHN at the amps for 90 degree C. I also stopped at Lowes and checked their chart and it only list the 60C or 75C amp ratings for the different wire. So the #8 THHN is shown as 75C for 50 amps.

I run into this issue at work all the time with contractors. I dont even know why they list 90 deg c if all of the termination points are always rated at 75 degrees.

Can be very miss leading. You'd be surprised at the amount of electrician's that i have to explain this too. I have been in the business for 4 years while some them have been doing this for 20 plus years.
 
Last edited:

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
I run into this issue at work all the time with contractors. I dont even know why they list 90 deg c if all of the termination points are always rated at 75 degrees.

Can be very miss leading. You'd be surprised at the amount of electrician's that i have to explain this too. I have been in the business for 4 years while some them have been doing this for 20 plus years.

The 90 degree column is usually used for derating purposes.
 

mdd1986

Well-known member
Joined
Jun 7, 2013
Messages
52
The 90 degree column is usually used for derating purposes.

That is a great point. When you have more than 3 current carrying conductors in a single conduit and you need to de-rate it. I believe thats the rule but not a 100 percent sure. I have only run into that on a few occasions.
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,030
Location
Modesto, CA
I run into this issue at work all the time with contractors. I dont even know why they list 90 deg c if all of the termination points are always rated at 75 degrees.

Can be very miss leading. You'd be surprised at the amount of electrician's that i have to explain this too. I have been in the business for 4 years while some them have been doing this for 20 plus years.

It is amazing how many LICENSED contractors are out there who dont really know what theyre doing. My boss(30 yr union electrician) at the last company i worked at thought that different brands of breakers were interchangeable with different brands of panels if the breakers fit the panel. I told him that would violate the U/L listing and its against code(had my code book in hand and was going to point out the code section) and he said 'no, its fine, if the breakers fit then theres no issue.' He was always giving me brands of breakers that didnt match the panel but I always made sure to match the correct breakers with the correct panel because i didnt want any issues down the road!
 

mdd1986

Well-known member
Joined
Jun 7, 2013
Messages
52
It is amazing how many LICENSED contractors are out there who dont really know what theyre doing. My boss(30 yr union electrician) at the last company i worked at thought that different brands of breakers were interchangeable with different brands of panels if the breakers fit the panel. I told him that would violate the U/L listing and its against code(had my code book in hand and was going to point out the code section) and he said 'no, its fine, if the breakers fit then theres no issue.' He was always giving me brands of breakers that didnt match the panel but I always made sure to match the correct breakers with the correct panel because i didnt want any issues down the road!

Hahah i hear you on that. I think when ul test it, they test the panel as whole with their breakers.

The best is when i find contractors installing stuff that doesn't match what the approved shop drawings call for. So many times i find that they use the cheap chinese dimmer switches that are not ul listed even though the shop drawing they submit clearly states levtion/lutron/hubble etc. Never mind that the switches are will almost burn your hand when you you go to turn off the switch lol.
 

Roots

Well-known member
Joined
Oct 31, 2010
Messages
1,788
It is amazing how many LICENSED contractors are out there who dont really know what theyre doing. My boss(30 yr union electrician) at the last company i worked at thought that different brands of breakers were interchangeable with different brands of panels if the breakers fit the panel. I told him that would violate the U/L listing and its against code(had my code book in hand and was going to point out the code section) and he said 'no, its fine, if the breakers fit then theres no issue.' He was always giving me brands of breakers that didnt match the panel but I always made sure to match the correct breakers with the correct panel because i didnt want any issues down the road!

That's some scary ineptitude and a lawsuit in the future!
 