whats the biggest circuit i can run through one inch pvc approx 40ft? thanks in advance.
chris
chris
1 inch sch40 PCV conduit can take four #4 Cu THWN-2 which is rated at 85 amps at 75 degrees C. Other wire types will be less, such as RHH/RHW is four #8 Cu which is 50 amps @ 75 deg C.
thanks patten, i assume that sch 80 will cut that down some? i was looking to run 60 amp with it. it was already there when i bought the house. if not ill use it for something else.
1 inch sch40 PCV conduit can take four #4 Cu THWN-2 which is rated at 85 amps at 75 degrees C. Other wire types will be less, such as RHH/RHW is four #8 Cu which is 50 amps @ 75 deg C.
#8 THHN/THWN is not 55A, it's 50A @ 75 deg. C.
Who you gonna believe, a HD chart, or pattenp??That's not what the big chart at the home depot said. It called out 55 amps but I still breakered it at 50.
That's not what the big chart at the home depot said. It called out 55 amps but I still breakered it at 50.
Who you gonna believe, a HD chart, or pattenp??
I'll give you a hint: He's NOT orange.
Just brought up the HD chart since it was there and a surprising amount of work gets installed based on that chart. So are you saying the chart is wrong?
I stuck to 50 amps on 8 gauge thwn-2, which jives with pattenp's advice. Pattenp has been very helpful to me and others on this forum and I never said he was wrong.
Just went to HD and their chart does show what the NEC table has for #8 THHN which is 55 amps @ 90 degrees C. The catch is even though technically THHN is a dry location rating and is listed in the 90 degree C column the terminal connections on devices such as breakers are only rated at 75 degrees C, so you need to size the conductor by 75 degrees C. I think it's misleading to the unknowing DYI'er who looks at that chart and may think it's okay to use THHN at the amps for 90 degree C. I also stopped at Lowes and checked their chart and it only list the 60C or 75C amp ratings for the different wire. So the #8 THHN is shown as 75C for 50 amps.
I run into this issue at work all the time with contractors. I dont even know why they list 90 deg c if all of the termination points are always rated at 75 degrees.
Can be very miss leading. You'd be surprised at the amount of electrician's that i have to explain this too. I have been in the business for 4 years while some them have been doing this for 20 plus years.
Thanks Pattenp, I didn't mean to make you go running all over town but I do appreciate the information.
The 90 degree column is usually used for derating purposes.
I run into this issue at work all the time with contractors. I dont even know why they list 90 deg c if all of the termination points are always rated at 75 degrees.
Can be very miss leading. You'd be surprised at the amount of electrician's that i have to explain this too. I have been in the business for 4 years while some them have been doing this for 20 plus years.
It is amazing how many LICENSED contractors are out there who dont really know what theyre doing. My boss(30 yr union electrician) at the last company i worked at thought that different brands of breakers were interchangeable with different brands of panels if the breakers fit the panel. I told him that would violate the U/L listing and its against code(had my code book in hand and was going to point out the code section) and he said 'no, its fine, if the breakers fit then theres no issue.' He was always giving me brands of breakers that didnt match the panel but I always made sure to match the correct breakers with the correct panel because i didnt want any issues down the road!
It is amazing how many LICENSED contractors are out there who dont really know what theyre doing. My boss(30 yr union electrician) at the last company i worked at thought that different brands of breakers were interchangeable with different brands of panels if the breakers fit the panel. I told him that would violate the U/L listing and its against code(had my code book in hand and was going to point out the code section) and he said 'no, its fine, if the breakers fit then theres no issue.' He was always giving me brands of breakers that didnt match the panel but I always made sure to match the correct breakers with the correct panel because i didnt want any issues down the road!