Lincoln Power Mig 215 MPi Welder Plug Type

Homewrecker

Well-known member
Joined
Sep 19, 2013
Messages
159
Location
Toronto, Ontario, Canada
Hello all,

I plan on ordering the Lincoln Electric Power Mig 215 MPi Multi Process Welder. I have a roughed in 240V 4 11/16" box with 4 wires. I need to install the matching receptacle for this welder but cannot find any information on the plug type (even the instructions don't mention it).

Does anyone know what receptacle this welder needs? From what I've been able to find it may have a Nema 6-50P plug but I'm not 100 certain. Ideally, I'd like to have the outlet wired before the the welder arrives.

Thanks.
 
To avoid these ads, REGISTER NOW!

The Cobbler

Super Moderator
Staff member
Joined
Oct 24, 2013
Messages
26,176
Location
Niagara Region, Ontario, Canada
welders typically use 3 wire ( no neutral) as they are 240 volt only . the only time 4 wire is used is if you need a neutral to supply 120/240 to the outlet
typically they use 6-30 or 6-50 depending on the amperage of the welder
 
OP
H

Homewrecker

Well-known member
Joined
Sep 19, 2013
Messages
159
Location
Toronto, Ontario, Canada
Why did you run a 4 wire feed?
I didn't run the 4 wire feed. It was a new construction home and I requested 240V rough-ins for the garage in anticipation of a Lift and my welder so for some reason the electrician ran 4 wires. When I installed my lift (https://www.garagejournal.com/forum...ad-lets-see-them.347432/page-12#post-10132451) I capped off one of the wires and ran the 240V with a ground and 2 hot legs.

Now I'm looking to do the same for the other rough-in but for a welder this time. I do know they use only 3 wires but need to know what receptacle I need to install.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
They ran 6-4.
Wow, overkill by a lot, but it wont hurt anything except the trouble of terminating the wires and closing up the box.

I bet a call to lincoln tech support gets you an answer, but if it was my shop, I'd do a 6-50 and then change the welder plug if needed. It's the most common plug type for welders and plasma cutters.
 
OP
H

Homewrecker

Well-known member
Joined
Sep 19, 2013
Messages
159
Location
Toronto, Ontario, Canada
This.

My 210 is a 6-50, this would be as well.

Though since it is dual voltage, any old 120v outlet will work!
Appreciate the info. Also got a couple of 20A 120V Outets that the manual calls for.

Since I have the the 240V available I might as well wire for that too. At that power rating it'll let me weld a thickness of steel I'll never need or use lol.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
It's a 50A circuit for which #6 wire is recommended.
Not for a welder.

I didn't look up the duty cycle but I bet #12 is sufficient. The NEC allows for downsizing wiring based on that and still using a 50a breaker and receptacle

Edit...you are in the great white north though. No idea on CEC rules for that
 
OP
H

Homewrecker

Well-known member
Joined
Sep 19, 2013
Messages
159
Location
Toronto, Ontario, Canada
Not for a welder.

I didn't look up the duty cycle but I bet #12 is sufficient. The NEC allows for downsizing wiring based on that and still using a 50a breaker and receptacle

Edit...you are in the great white north though. No idea on CEC rules for that
I simply told them I wanted a 240V 50A (The Lift circuit is 10-2 30A) circuit so that's the cable the electrician ran since I'm pretty certain the sales centre didn't exactly specificy to him that it was for a welder. Not complaining, since I got what I paid extra for lol.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
I simply told them I wanted a 240V 50A (The Lift circuit is 10-2 30A) circuit so that's the cable the electrician ran since I'm pretty certain the sales centre didn't exactly specificy to him that it was for a welder. Not complaining, since I got what I paid extra for lol.
It's all good. I said it will work fine.

And if it wasn't specifically for a welder, derating wouldn't be allowed, so yes, you got what you asked for.

It's just an exception that isn't commonly known.
 
To avoid these ads, REGISTER NOW!
OP
H

Homewrecker

Well-known member
Joined
Sep 19, 2013
Messages
159
Location
Toronto, Ontario, Canada
Lincoln finally got back to me. They confirm it is a 6-50P Plug. Thanks all for the feedback.

Going to have fun trying to find a 4 11/16" box cover plate with that size cutout in the middle lol.
 
OP
H

Homewrecker

Well-known member
Joined
Sep 19, 2013
Messages
159
Location
Toronto, Ontario, Canada
A 2-1/8" deep 4" square box would have worked just as good as a 4-11/16, but since it appears it might be too late...

Unfortunately the 4 11/16" boxes were builder installed so not my choice. But I do appreciate the extra space for thicker gauge wire.

I'm in Canada so ordering something that small from the US would not make alot of sense. I'll check with my local electrical supply shop. Amazon Canada may have something as well since I managed to find what I needed on there to wire my 2 post lift to the same size of box.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,123
Location
Central Iowa
Unfortunately the 4 11/16" boxes were builder installed so not my choice. But I do appreciate the extra space for thicker gauge wire.

I'm in Canada so ordering something that small from the US would not make alot of sense. I'll check with my local electrical supply shop. Amazon Canada may have something as well since I managed to find what I needed on there to wire my 2 post lift to the same size of box.
Didn't catch the Canada part. If the supply house carries Raco, the part # is 888. You could also use a two gang mud ring and a plate.


Or if it's surface mounted, which a raised cover is intended for, just change the box.
 

tfi racing

Well-known member
Joined
Apr 19, 2008
Messages
2,907
Location
Cedar,BC
Unfortunately the 4 11/16" boxes were builder installed so not my choice. But I do appreciate the extra space for thicker gauge wire.

I'm in Canada so ordering something that small from the US would not make alot of sense. I'll check with my local electrical supply shop. Amazon Canada may have something as well since I managed to find what I needed on there to wire my 2 post lift to the same size of box.
Conversion/mud ring plates for 4 11/16" to 4" so you can use 4" devices and covers are readily available in Canada, shouldn't be hard to find.


Here is another useful 4 11/16" cover, commonly used to convert a range outlet to a 15A receptacle when changing over to a NG range.

 
Last edited:
OP
H

Homewrecker

Well-known member
Joined
Sep 19, 2013
Messages
159
Location
Toronto, Ontario, Canada
I managed to find a 4 11/16" 1/4" raised 2 gang mud ring at Home Depot. For some reason 2 of the 4 holes do not correspond with the holes on the box. Just going to drill new ones.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,123
Location
Central Iowa
I managed to find a 4 11/16" 1/4" raised 2 gang mud ring at Home Depot. For some reason 2 of the 4 holes do not correspond with the holes on the box. Just going to drill new ones.
That's the way they are. Blanks, raised covers, and mud rings mount with two screws.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,123
Location
Central Iowa
The Blank Cover Plate and the 1 gang Mud Ring I have both have 4 holes that line up with the box.

The box comes with two screws. There are four holes in case the ring or cover needs to be rotated 90°. You can drill holes if you want, but the intention is for two screws to hold the ring

I don't have a ring or cover, only a blank. A ring or cover will have two more holes just in case the box is mounted facing the wrong direction.
 

Attachments

  • 1689123119555893569262588811694.jpg
    1689123119555893569262588811694.jpg
    589.1 KB · Views: 12
Last edited:

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,952
I simply told them I wanted a 240V 50A (The Lift circuit is 10-2 30A) circuit so that's the cable the electrician ran since I'm pretty certain the sales centre didn't exactly specificy to him that it was for a welder. Not complaining, since I got what I paid extra for lol.
They almost certainly assumed you were planning for an electric car, or a sub panel for 220V shop tools.
 