If your raceway is a single conduit, there's derating to consider and will most likely call for a larger wire size for each circuit.wires installed on breakers, run through the raceway and into the splice box
If your raceway is a single conduit, there's derating to consider and will most likely call for a larger wire size for each circuit.wires installed on breakers, run through the raceway and into the splice box
A lot is written about using the same brand of panel in house and garage, but how many times do you remove a breaker from one panel, and then later need the same size breaker in your other panel?
Follow up question; for the splice box, are these rail blocks kosher instead of the standard twist screw caps?
The "raceway" is sub 10 feet long, box, oversize (9"x4"), with minimal fill, vented. For a while I'm going to put a temperature sensor to monitor what's going on.If your raceway is a single conduit, there's derating to consider and will most likely call for a larger wire size for each circuit.
What voltage are they rated for? They look like DC distribution components.Follow up question; for the splice box, are these rail blocks kosher instead of the standard twist screw caps? They are rated to 10agw/30 amps, the highest amperage I'm using is 20 amps (there is one 30amp 220v circuit which should be 15 amps per leg).
If I do the hot splicing with these and the neutral using a ground bar I would think it be neater and less prone to issues.
Rated for 30 amp 600 volts. There is a version rated for 50 amp 600 volts.What voltage are they rated for? They look like DC distribution components.
Hey, I'm asking if it is doable. The run to the new location is about 9 feet long. Common ground is what they are right not at the original box so I'm just trying to figure out the better way to patch the ground to the new box.As for splicing the neutrals on a ground bar...... How is that going to work?
Are you really considering tying all the neutrals together on a common rail? And using a ground bar that is screwed to the box to do so? Hmmm. I hope I'm reading this wrong.
I'm talking only ground to a bar. Black/white spliced separately. If that makes sense.The only place neutral and ground should be bonded together is at the first point of disconnect. This is usually the main load center or a disconnect switch. After that neutral and ground are separate.
How many conductors will be in the splice box? Why will you need a temperature monitor?The "raceway" is sub 10 feet long, box, oversize (9"x4"), with minimal fill, vented. For a while I'm going to put a temperature sensor to monitor what's going on.
No, terminal blocks like that are commonly used in industrial applications and they are rated for 600 volts AC / DC. They are perfectly fine to use in a residential application. It's done all the time by electricians that know the application. Wago's are fine, but terminal blocks like those shown allow a neater job and are perfectly acceptable as long as they carry a UL listing.That 600 volt rating could still be DC only.
that only comes in to play code wise with 4 or CCCs and in reality only after 6 does it affect ampacity since the derating for 4-6 is 80% using 90° column w/ THWN-2.If your raceway is a single conduit, there's derating to consider and will most likely call for a larger wire size for each circuit.
this is overkill and not neededFor a while I'm going to put a temperature sensor to monitor what's going on.
Ignoring the 30/15A mistake, which was already commented on...Follow up question; for the splice box, are these rail blocks kosher instead of the standard twist screw caps? They are rated to 10agw/30 amps, the highest amperage I'm using is 20 amps (there is one 30amp 220v circuit which should be 15 amps per leg).
I read this response by the OP to be that there would be multiple circuits in the splice box. In that case, he would need to confirm if de-rating due to a single conduit is needed, and by how much, correct?that only comes in to play code wise with 4 or CCCs and in reality only after 6 does it affect ampacity since the derating for 4-6 is 80% using 90° column w/ THWN-2.
My (poor) understanding is that the "raceway" is both short (9') and spacious enough not to require de-rating 9"x4" or so. It is basically a 1/2"~3/4" plywood boxed channel near the ceiling to cover the wires. As usual I could be wrong.Ignoring the 30/15A mistake, which was already commented on...
I read this response by the OP to be that there would be multiple circuits in the splice box. In that case, he would need to confirm if de-rating due to a single conduit is needed, and by how much, correct?
welp that isnt raceway. thats just a cover. are you using NM-b? or individual conductors?My (poor) understanding is that the "raceway" is both short (9') and spacious enough not to require de-rating 9"x4" or so. It is basically a 1/2"~3/4" plywood boxed channel near the ceiling to cover the wires. As usual I could be wrong.
There are 19 circuits going into this panel but the 220v ones and a few others can be rewired directly from the new location, so about thirteen 110v/20 amp cables.
Pretty much. I call it a raceway just because it seems to be the most descriptive way to do it. I'm making it big enough so I can have cable separators and thus avoid them getting bundled, for no other reason than an overabundance of caution. And yes, good old Romex cabling.welp that isnt raceway. thats just a cover. are you using NM-b? or individual conductors?