Massive plumbing issue

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,406
Location
N CA
Put sleepers on the bedroom floor with new sub-floor and finish floor. You build up a minimum that likely will not be missed in the BR. It is enclosed above the envelope.
 
To avoid these ads, REGISTER NOW!
OP
S

Shriner

Active member
Joined
Nov 15, 2023
Messages
38
A lot of good ideas, thank you. I did think of BillK's idea previously and my thought process is to try to have 4" "vents" open on the floor above near the cavities which contain the supplies in order for these to be conditioned spaces. Then put closed cell spray foam in the garage from bottom of ceiling joist until we reached the required R-49 value. If we have to drop the garage ceiling 1-3", I guess there are greater tragedies. I have no idea if this will satisfy the County, but it is really my only reasonable solution. At the end of the day, I will be heating the garage after the occupancy permit is issued so frozen pipes are not a concern for me. Let's see how Tuesday's meeting goes.

Yes, I have proposed the variance idea. I am an attorney so am very familiar with hold harmless agreements. The plumbing inspector initially said yes, then days later said he would want the hold harmless from me AND a letter from an architect. Highly doubt I will be able to get the architect letter...
 

racecougar

Well-known member
Joined
Jan 26, 2021
Messages
4,979
Location
Missouri
No they don't. My house is built on a slab and all water supply runs in the ceilings and drops down, to both the toilet(s) and tub(s).

I sympathize with your plight, but I disagree with your presumption.
Agreed. I don't understand why the supplies need to be in the floor here.
 

CraigStu

Well-known member
Joined
May 22, 2014
Messages
4,009
Location
Blacksburg, Va
"Yes, you could probably do that re-routing at SIGNIFICANT cost and tearing out walls, but you still could not avoid toilet supply and tub supply being in the ceiling joists. Eventually the supplies have to get below the floor."
As others have questioned this so do I. I have seen plenty of toilets w/ the supply coming from the floor but there was always 12" of exposed pipe so it didn't HAVE to come from the floor. I suppose there may be tubs configured so the supply comes from the floor but if that is your case, how about a different tub? I know you don't want to redecorate but how about go w/ an industrial look and surface mount the supply pipes? Check the box stores for pipe made for use in building shelves and stuff. This is prebuilt but gives the idea.
Your supply pipes can be left as is or painted to match the wall to make them less obvious.
 

Bucko

Well-known member
Joined
Aug 23, 2021
Messages
679
Like others have said its difficult to brainstorm a solution without a visual idea of the Floorplan. Could a "chase" be built on the backside of the garage if it "T's" off next to a exterior wall of the home and the plumbing be run up the wall of the old exterior side which is now interior because of the added chase. It could double for HVAC, or make it even bigger and it could act as a storage area with a door on both floors.
 
OP
S

Shriner

Active member
Joined
Nov 15, 2023
Messages
38
Just to clarify all the questions about re-routing; it would be difficult for me to describe the layout but the bathroom is on the far end of the addition, which is above the garage. To get water from the original portion of the house to the bathroom, you have to go through the ceiling or floor, no other way around it. Walls would be blocked by a hallway. Ceiling and exterior walls are clearly forbidden per code over here. The garage ceiling is the grey area.

Tub faucet is similar to this:

The supplies are below floor.
 

Sturgeon

Well-known member
Joined
Oct 9, 2021
Messages
269
Location
W. Mt.
Maybe I missed it, is there some reason you can't drill out the floor joists for the water line's?
 

Wiz02

Well-known member
Joined
Jul 13, 2007
Messages
2,399
Location
Southeastern PA
Does anyone know the reasoning behind disallowing heat in a garage? If it's a concern about combustion, then why not allow heatpump, mini-split or electric baseboards?
 

Sturgeon

Well-known member
Joined
Oct 9, 2021
Messages
269
Location
W. Mt.
Maybe there thinking open flame in closed area with flamables. We're all going to be in trouble and power's to be aren't going to be reasonable signing off on any questionable lawsuit.
 

75gmck25

Well-known member
Joined
Jul 21, 2014
Messages
1,313
Location
Alexandria, VA
It's my understanding that in some areas they don't simply say you cannot heat a garage (if the system is safe, and properly installed).

However, if you do heat it, then it's now inspected and must meet all code requirement for living space (air infiltration, insulation, wiring, etc.). It is designed to prevent someone doing a budget conversion of a garage to a family room or bedroom by just adding a heater.

Now for a possibly crazy question. If you foamed your roof deck with the required thickness of insulation, and closed up all the exterior vents, and then removed the ceiling insulation on the room below, it's my understanding that your attic now becomes conditioned space. For code purposes it's now more like a basement. Does that mean you still cannot install water lines there?
 

Old tool guy

Well-known member
Joined
Apr 13, 2023
Messages
3,155
that would involve dropping the ceiling by roughly twelve inches in order to have R49 below the water supplies. I simply cannot lose twelve inches in the garage,

If you lose 12” of headroom … what does that leave? Is it a question of “can’t” or “don’t want to”?
 
OP
S

Shriner

Active member
Joined
Nov 15, 2023
Messages
38
75gmck25 is correct regarding hearting the garage. It basically is an "energy efficiency" issue per the County. When the garage door is opened, the heat goes out. I believe the same thing happens when you open the front door! You would have to insulate the garage, including overhead doors to meet an interior space; meet the blow test of having certain air infiltration, etc. My guess is the vast majority of heated garages were done without permits.

Sturgeon - Yes, the joists are drilled out for the copper to pass through. They are 14" wood I-Beams.
 
OP
S

Shriner

Active member
Joined
Nov 15, 2023
Messages
38
that would involve dropping the ceiling by roughly twelve inches in order to have R49 below the water supplies. I simply cannot lose twelve inches in the garage,

If you lose 12” of headroom … what does that leave? Is it a question of “can’t” or “don’t want to”?

Don't want to. If I can't fit a lift with two cars, the garage (which is the reason I bought the house) has essentially lost its purpose for me.
 

Old tool guy

Well-known member
Joined
Apr 13, 2023
Messages
3,155
Don't want to. If I can't fit a lift with two cars, the garage (which is the reason I bought the house) has essentially lost its purpose for me.
Ok, so looking at it from the outside, from the insurance or permit pov … there is a viable solution, you just don’t want to accept it. Not saying you’re wrong, just that your basis is eroded. If the lowered ceiling left you with … 7 ft … of headroom, it would clearly be a deal breaker. But not beingvable to install a lift?

But why would it take 12”? you can build a rated ceiling in just a few inches.
 
OP
S

Shriner

Active member
Joined
Nov 15, 2023
Messages
38
Ok, so looking at it from the outside, from the insurance or permit pov … there is a viable solution, you just don’t want to accept it. Not saying you’re wrong, just that your basis is eroded. If the lowered ceiling left you with … 7 ft … of headroom, it would clearly be a deal breaker. But not beingvable to install a lift?

But why would it take 12”? you can build a rated ceiling in just a few inches.

Correct, this is garage journal, nobody wants to lose 12" of garage height! R-49 is roughly 14" thick and we need to be below the water supplies. We might be able to save some inches if we do spray foam, we are looking into that, but I don't have much room to lose and be able to stack cars.

The new codes are pretty robust as far as where you can put water supplies and what insulation is required. R-49 is the minimum they will accept just in between garage ceiling and floor above. Zone 5.
 

racecougar

Well-known member
Joined
Jan 26, 2021
Messages
4,979
Location
Missouri
Does it have to be R-49 across the entire garage ceiling, or just the envelope containing the water lines? Could you drop into that cavity to cross your hallway, then get back into the upstairs interior wall(s)?
 
OP
S

Shriner

Active member
Joined
Nov 15, 2023
Messages
38
Does it have to be R-49 across the entire garage ceiling, or just the envelope containing the water lines? Could you drop into that cavity to cross your hallway, then get back into the upstairs interior wall(s)?

Per County, the entire ceiling has to be R-49. They will not budge on that.
 
To avoid these ads, REGISTER NOW!
OP
S

Shriner

Active member
Joined
Nov 15, 2023
Messages
38
With or without plumbing in place?

Correct, regardless of plumbing, ceiling must be R-49. The firefighters broke up multiple ceilings throughout the home and those attic spaces now all have to be upgraded to R-49.
 

racecougar

Well-known member
Joined
Jan 26, 2021
Messages
4,979
Location
Missouri
Still following my logic above, could you not insulate the entire ceiling with R-49, and only drop the ceiling down where necessary to get your plumbing across the hallway?
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,193
Location
VT
Isn't closed cell R7.5 per inch?

What are your floor joists?

How are unfinished basements (which I assume have plumbing) handled?

I feel like someone is misinterpreting the code in this situation, otherwise it all seems very ridiculous
 

GrayFlattop

Well-known member
Joined
Jan 18, 2018
Messages
1,037
Location
Chicago
Out of curiosity, what city / county?

But in a way, it doesn't matter as the inspector holds the cards. Do what they want, then after you get the occupancy permit, do whatever YOU want.

Heated garages aren't allowed, well that's just wrong.
 

flat350

Well-known member
Joined
Jan 1, 2009
Messages
1,006
Location
illinois
1000%! Suburbs of Chicago.
Cross linked polyethylene ( PEX ) is Illinois State code legal, has to be an amendment filed with the state to prohibit it.

Approved Materials for Water Distribution Pipe



1)Brass Pipe2ASTM B 43-2009
2)Chlorinated Polyvinyl Chloride2 (CPVC) Pipe/TubingASTM D 2846/D 2846M-2009be1
ASTM F 441/F 441M-2012
ASTM F 442/F 442M-2012
CSA B137.6-2009 in B137
JointsASTM D 2846/D 2846M-2009be1
CSA B137.6-2009 in B137
Solvent Cement1ASTM F 493-2010
CSA B137.6-2009 in B137
3)Copper/Copper Alloy Pipe2ASTM B 42-2010
ASTM B 302-2012
AWWA C606-2011
4)Copper/Copper Alloy Tubing2ASTM B 88-2009
5)Cross Linked Polyethylene2ASTM F 876-2013a
Distribution Systems

Joints
ASTM F 877-2011a
ASTM F 1807-2012
ASTM F 1960-2012
ASTM F 2080-2012
ASTM F 2098-2008
ASTM F 2159-2011
ASSE 1061-2011
CSA B137.5-2009 in B137
6)Galvanized Steel Pipe2ASTM A 53-2012
AWWA C606-2011
7)Poly Butylene (PB) Pipe/Tubing2
CSA B137.8-2009 in B137
8)Polypropylene Pipe2ASTM F 2389-2010
9)Polyvinyl Chloride (PVC) Pipe2, 3ANSI/NEMA Z535.1-2006 (R2011)
ASTM D 1785-2012
ASTM D 2241-2009
ASTM D 2672-2009
CSA B137.3-2009 in B137
JointsASTM D 2855-2010
ASTM F 441/F 441M-2012
CSA B137.2-2009 in B137
CSA B137.3-2009 in B137
PrimerASTM F 656-2010
Solvent Cement1ASTM D 2564-2012
CSA B137.3-2009 in B137
10)Stainless Steel Pipe2ASTM A 312/A 312M-2012
ASTM A 403/A 403M-2012
ASTM A 511/A 511M-2012
11)Welded Copper Water Tube2ASTM B 447-2012a WK, WL and WM
12)SolderASTM B 32-2008

Agency Notes:

1 Solvent cement must be handled in accordance with ASTM F 402-1988.
2 Water distribution pipe must meet the appropriate NSF standard for potable water. Plastic shall be rated at 160 psi at 73.4 degrees Fahrenheit.
3 Use for cold or tempered water only.
4 ASME B.1.20.1-1983.
5 Safety Color.
 

flat350

Well-known member
Joined
Jan 1, 2009
Messages
1,006
Location
illinois
I'm a retired Plumber in Cook Co., I'm trying to find the provision in the code about unconditioned spaces. I've done 100's of homes in Will, DuPage, Kane, Lake, and Cook Co., with plumbing waste and water lines in garage ceilings, must be something new they came up with. Anytime there was a doubt the HVAC guy would run some branches out to the plumbing, never had one freeze up that I know of. The state tried making a standard code years back and stop the local villages from having all kinds of weird amendments to it, it's possible they started letting the locals make up their own rules again. I just sent a text to the Schaumburg inspector about it.
Any chance the inspector is involved with TPI inspection services, they subcontract to some ares.
Only coming up with protecting traps from freezing, which a heat run would do, nothing seems to have changed in the wording on the IDPH website.
If they want R-49 in the garage ceiling below the conditioned space how much do they want in the attic above the conditioned space ?
 
Last edited:

Montauket

Well-known member
Joined
Mar 25, 2023
Messages
133
I’m just moving back home after a year of rebuilding from same. Pcustoms already described what we did. I have 2 garages under some bedrooms and the master bath. Radiant heat on the second floor as well but we can use pex. Spray foamed to r49 between the garage ceiling and second floor in the joist bays, r19 in the walls. Everything air sealed and fire caulked. Don’t know if they will allow that in your neck of the woods though.

To some of the others. Make sure you read the long form on your HO policy. In some cases your insurer only needs to make you whole to the condition the house was in on the date of the occurrence unless you have additional coverage. Without said additional they are not responsible to bring you up to new code such a rerouting the plumbing in this case. Not saying it can’t be done, depends on the adjuster and if there is any wiggle room in the exacatimate estimate to account for what you are doing. In some cases they may be able to finagle the depreciation to make things happen.

To the OP take tons of pictures they will come in handy later we took over 3000. It helped us when there were differences between what they estimated for and what reality was. I didn’t use a PA and wasn’t trying to screw the insurance either. I wound up GCing the job with my subs and was able to add a lot of value into the home that was not originally accounted for by their estimator/contractor. I wish you luck on the journey and if i can be of any help just ask. It ***** but you’ll get through it. Our appliances had a lead time of 9 months, cabinets 14-16 weeks , windows and doors 12 weeks. Hang in there bud.
 

flat350

Well-known member
Joined
Jan 1, 2009
Messages
1,006
Location
illinois
If your plumber is on the ball it is possible to call an Illinois State Plumbing inspector to look at it, they can over rule the local guy if he's pulling things out of his ***. I did this once and didn't make friends with the inspector that they overruled, he became a big PITA on future inspections by him
 

niget2002

Well-known member
Joined
Oct 2, 2012
Messages
11,112
Location
Josephine, TX
Couldn't you do a drop ceiling in the garage just where the pipes run? Run them around the edge of the garage so you don't lose the headroom in the middle.
 
OP
S

Shriner

Active member
Joined
Nov 15, 2023
Messages
38
I'm a retired Plumber in Cook Co., I'm trying to find the provision in the code about unconditioned spaces. I've done 100's of homes in Will, DuPage, Kane, Lake, and Cook Co., with plumbing waste and water lines in garage ceilings, must be something new they came up with. Anytime there was a doubt the HVAC guy would run some branches out to the plumbing, never had one freeze up that I know of. The state tried making a standard code years back and stop the local villages from having all kinds of weird amendments to it, it's possible they started letting the locals make up their own rules again. I just sent a text to the Schaumburg inspector about it.
Any chance the inspector is involved with TPI inspection services, they subcontract to some ares.
Only coming up with protecting traps from freezing, which a heat run would do, nothing seems to have changed in the wording on the IDPH website.
If they want R-49 in the garage ceiling below the conditioned space how much do they want in the attic above the conditioned space ?

Really appreciate the reply! Yes, this is something relatively new in DuPage (maybe State as well). No, the plumbing inspector is employed by the County directly. Are you saying it satisfies code to branch off ductwork to heat the joist cavities? If so, we could easily do that!
 
OP
S

Shriner

Active member
Joined
Nov 15, 2023
Messages
38
I’m just moving back home after a year of rebuilding from same. Pcustoms already described what we did. I have 2 garages under some bedrooms and the master bath. Radiant heat on the second floor as well but we can use pex. Spray foamed to r49 between the garage ceiling and second floor in the joist bays, r19 in the walls. Everything air sealed and fire caulked. Don’t know if they will allow that in your neck of the woods though.

To some of the others. Make sure you read the long form on your HO policy. In some cases your insurer only needs to make you whole to the condition the house was in on the date of the occurrence unless you have additional coverage. Without said additional they are not responsible to bring you up to new code such a rerouting the plumbing in this case. Not saying it can’t be done, depends on the adjuster and if there is any wiggle room in the exacatimate estimate to account for what you are doing. In some cases they may be able to finagle the depreciation to make things happen.

To the OP take tons of pictures they will come in handy later we took over 3000. It helped us when there were differences between what they estimated for and what reality was. I didn’t use a PA and wasn’t trying to screw the insurance either. I wound up GCing the job with my subs and was able to add a lot of value into the home that was not originally accounted for by their estimator/contractor. I wish you luck on the journey and if i can be of any help just ask. It ***** but you’ll get through it. Our appliances had a lead time of 9 months, cabinets 14-16 weeks , windows and doors 12 weeks. Hang in there bud.

Thank you so much, really excellent information and appreciate the sentiment. This is basically what we are going to try to sell the inspector on; fingers crossed it works.

Our insurance company has been amazing. I actually just told her what was going on and she said to let her know if we need anything or if we need to move anything and she will cover the cost with an invoice. I asked her about code coverage and she said we have $68k so that is nice to know.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,193
Location
VT
Isn't closed cell R7.5 per inch?

What are your floor joists?

How are unfinished basements (which I assume have plumbing) handled?

I feel like someone is misinterpreting the code in this situation, otherwise it all seems very ridiculous

Guess I'll reply to myself as these are still open questions....
 
OP
S

Shriner

Active member
Joined
Nov 15, 2023
Messages
38
Guess I'll reply to myself as these are still open questions....

Ha! Sorry, I missed some! Yes, that is my understanding of closed cell as well. Floor joists are 14" wood I-Beams. With closed cell, we would need to drop the ceiling by roughly 4" to be 7" below the lowest water supply.

Every unfinished basement I have been in is still conditioned by the house HVAC; so not a cold zone. That is how Chicago basements are set up for the most part.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,193
Location
VT
Ha! Sorry, I missed some! Yes, that is my understanding of closed cell as well. Floor joists are 14" wood I-Beams. With closed cell, we would need to drop the ceiling by roughly 4" to be 7" below the lowest water supply.

Why? Foam around the pipes and be done with it.


Every unfinished basement I have been in is still conditioned by the house HVAC; so not a cold zone. That is how Chicago basements are set up for the most part.

Interesting. I don't think I've ever been in a conditioned, unfinished basement in New England or New York State. Usually just a furnace ducted to the vents or a boiler plumbed to registers/radiator on the first floor.
 
OP
S

Shriner

Active member
Joined
Nov 15, 2023
Messages
38
Why? Foam around the pipes and be done with it.




Interesting. I don't think I've ever been in a conditioned, unfinished basement in New England or New York State. Usually just a furnace ducted to the vents or a boiler plumbed to registers/radiator on the first floor.

They want R-49 below the water supply pipes. We shall see how the meeting goes next week.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,193
Location
VT
They want R-49 below the water supply pipes. We shall see how the meeting goes next week.
Good luck. Thats either an asinine code requirement or someone is completely misinterpreting the code requirement.
 

nmk_61802

Well-known member
Joined
Mar 6, 2008
Messages
965
Location
Central IL
IPC does not prohibit installation in exterior walls, just says they must be freeze protected:

1711063694298.png

Unfortunately the 890.1210(a) is just a circular reference:
1711063825591.png

Insulating below the pipe and allowing the pipe to sit in the warm zone is a common method of freeze protection, but IPC does not recommend thickness. Again unfortunately it will be at the whim of the AHJ unless you can prove them wrong.
 