Meter socket clearance

central1ny

Well-known member
Joined
Feb 22, 2009
Messages
134
My current electrical meter socket is installed on the side of my house right where the new garage breezeway will be. So my plan is to move the meter socket forward toward the front of the house by about 8 feet. There will be a clearance of 24" between the center of the meter socket and the wall of the breezeway.

Does anyone know of a code pertaining specifically to lateral clearance of meter sockets? I read in other places that 110.26 from the NEC may apply due to workspace clearance. If so, does the 30" requirement apply to lateral workspace? If so, does this mean that I need 15" on either side of the meter socket to be in compliance?

One other question. I have an underground electrical service cable from the pole to my current meter socket. My plan is to have the electric company cut power at the pole. I will then have an expert excavator dig down to a few inches above the cable at which point I will hand dig the rest of the way to avoid any damage to the cable. I will then reroute the cable to the new meter socket location. First, does anyone see any problems with this? Second, if by chance the cable is not long enough to be routed to the the socket location, can anyone recommend splices approved for underground use? Thanks.
 
To avoid these ads, REGISTER NOW!

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
you need to involve your power company before you start doing anything. typically a service planner will come out and tell you where to put the meter. I highly doubt they would have you do any splicing yourself on the power company owned service lateral.
 
OP
C

central1ny

Well-known member
Joined
Feb 22, 2009
Messages
134
you need to involve your power company before you start doing anything. typically a service planner will come out and tell you where to put the meter. I highly doubt they would have you do any splicing yourself on the power company owned service lateral.

I dealt with the power company last year and already got approval from the service planner. I will need to go through this process again since the project was delay. The underground service lateral is customer owned.
 

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,316
Location
Minneapolis
Meter location is generally regulated by the electric utility. They may have a handbook containing their regulations available on their website, most of them do these days.
 

Jarcese

Well-known member
Joined
Aug 17, 2010
Messages
194
Location
Boston, MA
Mass code is 3' of "working space" in all directions, but you're not in ma. The utility should have a pdf file of rules and regulations for electric service on their website, if not they will send you a booklet.
 
OP
C

central1ny

Well-known member
Joined
Feb 22, 2009
Messages
134
I have the electric specifications document from my service provider but there are not enough details about lateral clearance so I have an email off to them to clarify.
 
To avoid these ads, REGISTER NOW!

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
We typically use crimped buttsplices with T&B adhesive lined heatshrink for direct burial splices.

Look at these, esp the first one. Never heard of a customer owned service lateral. You may have paid for it, but I would think they own it.

There are a ton of them over here. One of the power companies here has us pull the wire into the pad mount transformer vaults. They land the wires in the transformer though...
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
When GA Power spliced the underground feeds to my house (after they burned in two in several places, years old, corrosion I guess) they used a **** splice that was crimped with a device that looked like a cordless drill with a special head on it, then sealed it over with the heat shrink with sealant on the inside.

Charles
 
OP
C

central1ny

Well-known member
Joined
Feb 22, 2009
Messages
134
When GA Power spliced the underground feeds to my house (after they burned in two in several places, years old, corrosion I guess) they used a **** splice that was crimped with a device that looked like a cordless drill with a special head on it, then sealed it over with the heat shrink with sealant on the inside.

Charles

Thanks for the pictures, very helpful. What book are these out of?
 
OP
C

central1ny

Well-known member
Joined
Feb 22, 2009
Messages
134
Never heard of a customer owned service lateral. You may have paid for it, but I would think they own it.

Charles


Maybe I used the wrong terminology. Per the electrical specification from the utility, they define the service lateral as "The underground conductors between the utility electric supply system and the service point."

They also say that the customer's responsibility are as follows: "The Customer shall provide the service entrance, in accordance with the Company’s requirements, and all premises wiring on the load side of the service point."

The attached picture shows the installation diagram from the spec, so this leads me to believe that I own the cable between the service point and the meter. I now see that they are referring to this cable as the underground service conductors.

By the way, my utility company is national grid in NY.


Service.JPG
 