It's hard to believe local codes would make a particular connections a mandatory, unless they have a really good case. The problem is that if the local codes forces people to braze, Trane or American Standards can not be sold in that town (or county) because they use Rotolock (a similar mechanical fastener to connect the compressor to the lines).
 

Climatecreator

Well-known member
Joined
Dec 8, 2006
Messages
245
Location
CT
Not just that but now they even are using zoom lock for line sets.

Same kind of stuff used to happen when PEX first came out too. Sometimes local inspectors / building "officials" tend to get stuck with what they know and disregard the newest technology.

CC
 

alexb2000

Well-known member
Joined
Feb 7, 2010
Messages
664
Location
Fort Worth, TX
I believe they require a flare because there are too many guys that don't take the time to setup a nitrogen purge when they braze. That and they overheat the valves, TXV, etc. I can completely understand the move to flares and knock on wood I haven't any problems with them.
 

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,406
Location
N CA
Speaking from Fujitsu's viewpoint, when I represented them, they did not want brazed joints. The flares are a giant pitn, but with care they are great. With Great Care. I had a customer who insisted upon brazing the evaps. He was a successful contractor and over the years we did a great deal of business on assorted products. I had a really good relationship with him, but I could not get him to stop brazing. Problem was that he was having a lot of problems with systems. It doesn't take a lot of silver solder to plug up a 1/4" line. He would cut out evap and send them back but never with the brazed joint on the return. Fujitsu finally said they wanted to see the joints too. He had many times the problems of any contractor I sold Fujitsu to. He finally said he was going to Mitsu. Honestly, at the point I was happy to see him go. A couple years later at a trade show I saw the Mitsu Regional and asked how he was doing. He said he was having problems with evaporators.
Can you braze? Sure, but the back purge is critical as is the technique. A skilled guy won't pour the silver to it and plug the line. Are you skilled working in an awkward position. With welding or brazing, it is the position work that tells the tale on the guy doing the work. Also, putting the flame that near the body of the evap is dicey. Those drain pans are styrofoam. Whichever way you choose, practice wins the day.
 

johnnyradiant

Well-known member
Joined
Mar 27, 2017
Messages
833
Location
Vancouver, BC
Speaking from Fujitsu's viewpoint, when I represented them, they did not want brazed joints. The flares are a giant pitn, but with care they are great. With Great Care. I had a customer who insisted upon brazing the evaps. He was a successful contractor and over the years we did a great deal of business on assorted products. I had a really good relationship with him, but I could not get him to stop brazing. Problem was that he was having a lot of problems with systems. It doesn't take a lot of silver solder to plug up a 1/4" line. He would cut out evap and send them back but never with the brazed joint on the return. Fujitsu finally said they wanted to see the joints too. He had many times the problems of any contractor I sold Fujitsu to. He finally said he was going to Mitsu. Honestly, at the point I was happy to see him go. A couple years later at a trade show I saw the Mitsu Regional and asked how he was doing. He said he was having problems with evaporators.
Can you braze? Sure, but the back purge is critical as is the technique. A skilled guy won't pour the silver to it and plug the line. Are you skilled working in an awkward position. With welding or brazing, it is the position work that tells the tale on the guy doing the work. Also, putting the flame that near the body of the evap is dicey. Those drain pans are styrofoam. Whichever way you choose, practice wins the day.

So are you saying it's a bit of an old dogs n new tricks kinda stubborn thing combined with maybe a bit of an ego thing that 'I can braze better than those other guys'?
 

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,406
Location
N CA
So are you saying it's a bit of an old dogs n new tricks kinda stubborn thing combined with maybe a bit of an ego thing that 'I can braze better than those other guys'?

I have no idea if you can braze better than those other guys. You might want to read it again. Keep in mind that as the factory rep I covered a six state area for Fujitsu. I only got called to look at catastrophes. You learn. I only use flare fittings on mini-splits.
 

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
As far as code I wonder if they are more concerned with brazing vs solder, I've run across more then 1 unit plumbed with lead solder. I would sit down with the head mechanical inspector and get a clarification if I was in doubt.


Even if you purge nitrogen you will get some oxides when brazing, you get a lot less with nitrogen but you will still have some.

I had a Daikin training class this spring, two reps from daikin said 90% of the problems they see are either leaky flares or sealant plugging the electronic expansion valve, Nylog and Leak lock were the two that they called out by name, they also stated that warranty would be denied if sealant was found on the flare fittings.

We spent several hours dealing with how to make a proper flare, I had several flare tools but none would consistently make a perfect flare, I ended up buying a CPS flare tool kit that makes it relatively easy along with a digital torque wrench to ensure that each one is properly tightened.

I have used leak lock in the past but will not use it now, I test all my flares to 500 psi to ensure that they are sound.
 

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,406
Location
N CA
As far as code I wonder if they are more concerned with brazing vs solder, I've run across more then 1 unit plumbed with lead solder. I would sit down with the head mechanical inspector and get a clarification if I was in doubt.


Even if you purge nitrogen you will get some oxides when brazing, you get a lot less with nitrogen but you will still have some.

I had a Daikin training class this spring, two reps from daikin said 90% of the problems they see are either leaky flares or sealant plugging the electronic expansion valve, Nylog and Leak lock were the two that they called out by name, they also stated that warranty would be denied if sealant was found on the flare fittings.

We spent several hours dealing with how to make a proper flare, I had several flare tools but none would consistently make a perfect flare, I ended up buying a CPS flare tool kit that makes it relatively easy along with a digital torque wrench to ensure that each one is properly tightened.

I have used leak lock in the past but will not use it now, I test all my flares to 500 psi to ensure that they are sound.

What digital torque wrench set-up are you using?
 

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
Are not the DIY units with the connected purged line set brazed ? That's how they used to do them.

Don't get the industry -- there has to be better way. With automotive applications using crimp connectors and o rings -- this should be the direction.
 

Trey T

Well-known member
Joined
Aug 3, 2011
Messages
3,749
Location
Houston, TX
Rotolock (on Trane/American Standard) and Zoomlock are alternative to terminate lines that's similar to automotive applications. They're expensive and complex (rotolock) for streamline process.

The flare is a good alternative but requires a high level of conscientious approach. If you're not conscientious about the flaring method, it will cause problem like many of you stated.

The difference between the Rotolock (and Zoomlock) and flare, is that Rotolock allows for error and compensated by the o-ring. The flare has no o-ring and requires high precision mating surfaces.
 

Gerald O

Well-known member
Joined
Mar 5, 2013
Messages
1,884
Location
NC
Nylog is more of a lubricant than a sealant. It should never cause a blockage because it dissolves in the refrigerant.
 

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
This is the torque wrench and flare kit I use. Torque wrench has presets for different size lines so it's quick and easy to get the right setting. Flare kit has a nice cutter, flare block with depth stop, deburring tool and and a go/no go sizeing plate to make sure that the flare is the correct size.

I also have a CPS bender kit that's pretty nice, I had very little exposure to CPS tools before this stuff but it's pretty darn nice stuff.IMG_20180626_134938201.jpgIMG_20180626_134943088.jpgIMG_20180626_135024449.jpgIMG_20180626_135033381.jpg

Sent from my XT1254 using Tapatalk
 

eddieK

Well-known member
Joined
Mar 2, 2017
Messages
695
Location
Nampa Idaho
I always use refrigerant oil on the flares, was trained years ago that the oil is your final seal.

Technique - technique - technique ...and a pressure test before you open the valves. I always test to 350 - 400 PSI Nitrogen
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
Are not the DIY units with the connected purged line set brazed ? That's how they used to do them.

Don't get the industry -- there has to be better way. With automotive applications using crimp connectors and o rings -- this should be the direction.

They did that in the 60's. The Aeroquip "flex lines" sucked big time.

People seem to have problems with flares. I never really had an issue with ones I made, but have found most "bad" fittings could be fixed be redoing them, or using a copper flare gasket in a pinch. I don't use any type of sealer on anything other than pipe thread fittings.

Tommy
 
Last edited:

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
They did that in the 60's. The Aeroquip "flex lines" sucked big time.

People seem to have problems with flares. I never really had an issue with ones I made, but have found most "bad" fittings could be fixed be redoing them, or using a copper flare gasket in a pinch. I don't use any type of sealer on anything other than pipe thread fittings.

Tommy

Do the copper flare gasket work to form a leak free seal? I have situation where it is too short to cut and make a new flare
 
To avoid these ads, REGISTER NOW!

Trey T

Well-known member
Joined
Aug 3, 2011
Messages
3,749
Location
Houston, TX
No. You're potentially making things worst, creating two surfaces for leakage. Those copper washer are typically used in conjunction w/ another material, like aluminum or steel lines. You have to re-flare it for good seal because the copper was crushed precisely to that mating surface. Once you take the flare fitting off, it's impossible to realign it and make a perfect seal.

It's like a crush washer you have on your oil drain plug to keep the mating surface sealed. After it's used, you have to replace it. Same w/ the copper flare fitting.
 

kneeman

Well-known member
Joined
Mar 12, 2014
Messages
1,704
No. You're potentially making things worst, creating two surfaces for leakage. Those copper washer are typically used in conjunction w/ another material, like aluminum or steel lines. You have to re-flare it for good seal because the copper was crushed precisely to that mating surface. Once you take the flare fitting off, it's impossible to realign it and make a perfect seal.

It's like a crush washer you have on your oil drain plug to keep the mating surface sealed. After it's used, you have to replace it. Same w/ the copper flare fitting.
All true but I have a Honda with 200k miles that I have never replaced the metal washer. No leaks. One day it will let me down though. Oil is thicker and not under pressure like hvac stuff, what he said is correct.
 

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
We had a sales guy of some sort drop off some samples of a copper washer with a loctite coating designed to seal flare fittings, flaretite was the name, I have no idea if they are worthwhile but it's an interesting idea as a dry coating wouldn't have much of a chance of causing contamination.
 

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
We had a sales guy of some sort drop off some samples of a copper washer with a loctite coating designed to seal flare fittings, flaretite was the name, I have no idea if they are worthwhile but it's an interesting idea as a dry coating wouldn't have much of a chance of causing contamination.

Just wondering if you know these copper gaskets are meant to be used up things brass to brass, which you will definitely need.
Or, repair an existing leak.

https://www.flaretite.com/flaretite-seal
 

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
Just wondering if you know these copper gaskets are meant to be used up things brass to brass, which you will definitely need.
Or, repair an existing leak.

https://www.flaretite.com/flaretite-seal

I really don't know anything about them other then what's on the website, they are made local to us so the rep that dropped them off might be a customer of ours or something, I would give them a ring and see what they say.
 

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
it's been my experience of my own and also watching a manufacturer accredited installer make flares and used a torque wrench, use refrig oil etc, about half the joints seem to leak, not enough to go flat quick but probably in a year or two. Not sure the quality of the flare, maybe bad deburing job. Installers are in a rush and they make more money putting in furnace circuit boards and capacitors.

I had a machine that was installed by a guy who tightened ALOT with adjustable wrenches with crappy flare that came with the lineset, and it doesn't leak.

I have a bit of issue with the torque specs for the small 1/4" lines, just 11 to 13 foot pounds, that's barely any torque and seems not enough.
 

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
have watched youtube, one of those guys braze the evap. Being that up a 18 feet to leak test isn't very good. By brazing it (Nitrogen back purged and leak tested) you eliminated the possibility of leak by 50%.

The compressor and valves are brazed in at the factory. The coils are a series of brazes. Once the unit is put in service, there is oil residue in the tubing and I am not sure even if nitrogen back purge will be enough to be clean. I always feel that is of iffy because the mini splits don't have any filters on them.
 

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,406
Location
N CA
This is the torque wrench and flare kit I use. Torque wrench has presets for different size lines so it's quick and easy to get the right setting. Flare kit has a nice cutter, flare block with depth stop, deburring tool and and a go/no go sizeing plate to make sure that the flare is the correct size.

I also have a CPS bender kit that's pretty nice, I had very little exposure to CPS tools before this stuff but it's pretty darn nice stuff.IMG_20180626_134938201.jpgIMG_20180626_134943088.jpgIMG_20180626_135024449.jpgIMG_20180626_135033381.jpg

Sent from my XT1254 using Tapatalk

Much obliged!
 

Trey T

Well-known member
Joined
Aug 3, 2011
Messages
3,749
Location
Houston, TX
All true but I have a Honda with 200k miles that I have never replaced the metal washer. No leaks. One day it will let me down though. Oil is thicker and not under pressure like hvac stuff, what he said is correct.
I actually mentioned about the exact exception but deleted it. Honda is unique because that washer is stay fixed.
 

alexb2000

Well-known member
Joined
Feb 7, 2010
Messages
664
Location
Fort Worth, TX
it's been my experience of my own and also watching a manufacturer accredited installer make flares and used a torque wrench, use refrig oil etc, about half the joints seem to leak, not enough to go flat quick but probably in a year or two. Not sure the quality of the flare, maybe bad deburing job. Installers are in a rush and they make more money putting in furnace circuit boards and capacitors.

Half the flare joints leak? Really? So if there are four flare joints per unit all of them statistically will leak?

Pulling a vacuum with a micron gauge will 100% determine if there is a slow leak, so no systems should be put into service leaking, correct?

Of course quality of the flare is important, no industry has figured out a way around crappy installers. However, using the above the installer should know if there is a leak before they even release the refrigerant.
 

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
Half the flare joints leak? Really? So if there are four flare joints per unit all of them statistically will leak?

Pulling a vacuum with a micron gauge will 100% determine if there is a slow leak, so no systems should be put into service leaking, correct?

Of course quality of the flare is important, no industry has figured out a way around crappy installers. However, using the above the installer should know if there is a leak before they even release the refrigerant.

Yes, I have a leak detector (now) and a manifold with total 5 flare connections at the condenser unit, the results are worry some. The installer blanked off the valve and wanted to see a certain micron level and released immediately.
I am guessing he knows his micron gauge leaks, but paired with a nitrogen pressure test you make a call how the system is doing.

I am going to take it apart see if I can find the cause. One of the joints is a factory made reducer with a flare so cannot fault the installer because he didn't make the flare. I think the torque is not tight enough
 

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
also, when you put nylog on the threads of the male flare, even like a drop, when you thread it together there is nylog on the threads, you can see it has filled it at the end, it's likely going to give you a leak free pressure and micron test.

The stuff is like molasses so if it's going to drip out it is not going to be during your installation time frame. But weeks and many hours of operation. If there was a small leak at the flare that may eventually show itself, but not at install time.

So I wanted to know what you guys do, should you put nylog on the threads, maybe just very sparingly or not at all?
 

alexb2000

Well-known member
Joined
Feb 7, 2010
Messages
664
Location
Fort Worth, TX
Yes, I have a leak detector (now) and a manifold with total 5 flare connections at the condenser unit, the results are worry some. The installer blanked off the valve and wanted to see a certain micron level and released immediately.
I am guessing he knows his micron gauge leaks, but paired with a nitrogen pressure test you make a call how the system is doing.

I am going to take it apart see if I can find the cause. One of the joints is a factory made reducer with a flare so cannot fault the installer because he didn't make the flare. I think the torque is not tight enough

So once again an installer that cannot read instructions or even understand the purpose of using a micron gauge.

Why over complicate a procedure that is being used everyday with high success? I use the factory flare nut, use a good flaring tool like the Yellow Jacket 60278 and take my time making my own flares, use Nylog lightly on face and threads (not so much to seal as to allow a proper torque on the flare face), and a flare torque wrench (I use a Yellow Jacket 60652). I use a JB pump and pull to ~500 microns, then let it set 15min.

Using the above (or equivalent tools and steps), I just don't have problems.:dunno:
 

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
So once again an installer that cannot read instructions or even understand the purpose of using a micron gauge.

Why over complicate a procedure that is being used everyday with high success? I use the factory flare nut, use a good flaring tool like the Yellow Jacket 60278 and take my time making my own flares, use Nylog lightly on face and threads (not so much to seal as to allow a proper torque on the flare face), and a flare torque wrench (I use a Yellow Jacket 60652). I use a JB pump and pull to ~500 microns, then let it set 15min.

Using the above (or equivalent tools and steps), I just don't have problems.:dunno:

Yes, I have very much just quit dealing with installers with handling things myself with better success.
 

Ohmthis

Well-known member
Joined
Jan 20, 2013
Messages
3,001
Location
Outside of Louisville KY
So once again an installer that cannot read instructions or even understand the purpose of using a micron gauge.

Why over complicate a procedure that is being used everyday with high success? I use the factory flare nut, use a good flaring tool like the Yellow Jacket 60278 and take my time making my own flares, use Nylog lightly on face and threads (not so much to seal as to allow a proper torque on the flare face), and a flare torque wrench (I use a Yellow Jacket 60652). I use a JB pump and pull to ~500 microns, then let it set 15min.

Using the above (or equivalent tools and steps), I just don't have problems.:dunno:

I use the same flaring tool and feel it’s foolproof if taken the time to use it correctly. I use the factory flare nuts, nylog, and I use a set of adjustable wrench’s to tighten the flare (I know, I’m too cheap to buy the torque wrench) I have had one flare leak and it was because I pretty much over looked it and didn’t tighten it. I’ve never even considered brazing the connections. I HAVE brazed the line to extend a line set. I flowed nitrogen and used as little sil-fos as necessary to make a good joint. Those 1/4” lines are so little, it wouldn’t take much to overfill it.
 

alexb2000

Well-known member
Joined
Feb 7, 2010
Messages
664
Location
Fort Worth, TX
One other tool that I really like for mini-split installs is this Rigid tubing cutter:

https://www.amazon.com/gp/product/B001P81OK6/?tag=atomicindus08-20

It makes glass smooth cuts without crushing the tubing. Perfect for making refrigeration flares. It also works great if you are fabricating your own brake or fuel lines so it is multipurpose.

I know it's more than a regular copper tubing cutter, but hey this site is about tools right?
 