Had another meeting with the engineer, asking if there was an alternative to the expensive LVL beams. He wouldn’t budge off his design plan. According to a horizontal roof rafter Maximum span calculator I should be fine with 2x12 lumber at 24in spacing ( maximum span is 20ft the length of the rafters in my garage would be 18ft) and this calculation is considering a max live load of 20ft/lbs squared. I think I would be fine with regular #1 2x12 lumber. But to cover myself I’ll go with the advise of the “trained professional”
Sent from my iPhone using The Garage Journal mobile app
Does that span calculator consider shear? What dead load did you use? Can you post both sets of calcs and we will put our propeller hats on and give you a good answer?
Also, based on where your engineer is located, the snow load could vary. The ground snow load values fluctuate from 25 to 55 psf depending what county you live in. PGC is min 30 psf roof snow load plus drift.
Can you give your location too?
Last edited: