Not sure where this may belong - please feel free to move if necessary
Sorry for the long post - I am working on 3/4 HP, 3 phase, 1750 RPM, 2.8 FLA, dual voltage Delta motor. To date I have disassembled, cleaned, painted and replaced bearings. The motor came to me with no spacers or spring washers in either end and it had 5/64" end play. I used a spring washer in each end when assembling - no discernible end play now. The same problem exists with or without spring washers.
I am using an AB 160 series C VFD to power with single phase input. I have tried two different VFD's with different HP and both showed the same problem.
OK - the problem. When I initially powered up the motor it started and ran fine but after 2/.5 minutes in shut off with a VFD error of 7 - current over load. I checked all parameters and connections and tried again - same result/. Tried another VFD - same result. These VFD's have a set of non programmable parameters that display a series of data - one is VFD output in amps. I set that and observed output of 3.1 amps - so an over current situation did exist and the VFD appropriately shut down. I tested again and measured the current with a Sperry SNAP meter - it also showed 3.1 amps on all three leads and zero on the ground. BTW - this testing was done before adding an wavy washers. I proceeded to add a wavy washer in the fan end - same result. Added another to the opposite end - same result. I bumped up the VFD parameter for max current
42 [Motor Overload Current]Set to motor nameplate Full Load Amps (FLA).
I bumped it from 2.8 to 3.3 - motor ran fine (VFD did not shut off). I let it run 45 minutes - no smoke or smells and it only got a bit warm on the non fan end. I could easily put my hand on it and leave it there comfortably. Then I started adding wavy washers - after the first the operating amps on the VFD jumped up to 3.4 (adjusted VFD parameter to 3.5) - let it run and got the same as above. With two wavy washers the amps jumped up to 3.65 (adjusted VFD parameter to 4) - no adverse affects after 45 minutes although it did feel a bit warmer - again not hot.
I did measure the input volts - 250 as measured with a Sperry digital multimeter and 230 measured with a S[perry analog meter. I'm not sure which one is right or if it even matters.
So that is where I am at - even though there were no significant affects of the over current - I am concerned. This motor is destined for a Delta 17" VS drill press so I'm thinking as load is put on the motor the over current will get worse. Truth be known I have never looked at the operating amps dis[play on a VFD before so this may be normal but I don't think so? Questions
1. What are the potential causes of a motor running over the name plate FLA?
2. Should I be concerned about using this on a drill press?
3. What would the typical unloaded motor current draw be?
4. Is incoming voltage an issue and how can I validate my multimeter voltage readings
5. Given this motor came to me with no washers - should I remove them and live with the 5/64 end play. Ever Delta motor I have seen had spacers and/or spring washers
I guess that is it for now. Thanks for any ideas you may have
Rick
Sorry for the long post - I am working on 3/4 HP, 3 phase, 1750 RPM, 2.8 FLA, dual voltage Delta motor. To date I have disassembled, cleaned, painted and replaced bearings. The motor came to me with no spacers or spring washers in either end and it had 5/64" end play. I used a spring washer in each end when assembling - no discernible end play now. The same problem exists with or without spring washers.
I am using an AB 160 series C VFD to power with single phase input. I have tried two different VFD's with different HP and both showed the same problem.
OK - the problem. When I initially powered up the motor it started and ran fine but after 2/.5 minutes in shut off with a VFD error of 7 - current over load. I checked all parameters and connections and tried again - same result/. Tried another VFD - same result. These VFD's have a set of non programmable parameters that display a series of data - one is VFD output in amps. I set that and observed output of 3.1 amps - so an over current situation did exist and the VFD appropriately shut down. I tested again and measured the current with a Sperry SNAP meter - it also showed 3.1 amps on all three leads and zero on the ground. BTW - this testing was done before adding an wavy washers. I proceeded to add a wavy washer in the fan end - same result. Added another to the opposite end - same result. I bumped up the VFD parameter for max current
42 [Motor Overload Current]Set to motor nameplate Full Load Amps (FLA).
I bumped it from 2.8 to 3.3 - motor ran fine (VFD did not shut off). I let it run 45 minutes - no smoke or smells and it only got a bit warm on the non fan end. I could easily put my hand on it and leave it there comfortably. Then I started adding wavy washers - after the first the operating amps on the VFD jumped up to 3.4 (adjusted VFD parameter to 3.5) - let it run and got the same as above. With two wavy washers the amps jumped up to 3.65 (adjusted VFD parameter to 4) - no adverse affects after 45 minutes although it did feel a bit warmer - again not hot.
I did measure the input volts - 250 as measured with a Sperry digital multimeter and 230 measured with a S[perry analog meter. I'm not sure which one is right or if it even matters.
So that is where I am at - even though there were no significant affects of the over current - I am concerned. This motor is destined for a Delta 17" VS drill press so I'm thinking as load is put on the motor the over current will get worse. Truth be known I have never looked at the operating amps dis[play on a VFD before so this may be normal but I don't think so? Questions
1. What are the potential causes of a motor running over the name plate FLA?
2. Should I be concerned about using this on a drill press?
3. What would the typical unloaded motor current draw be?
4. Is incoming voltage an issue and how can I validate my multimeter voltage readings
5. Given this motor came to me with no washers - should I remove them and live with the 5/64 end play. Ever Delta motor I have seen had spacers and/or spring washers
I guess that is it for now. Thanks for any ideas you may have
Rick