I have a MrCool 4th gen DIY 18k unit that I am going to install and just want to make sure I'm using the correct items.

It says in the manual for the 18k unit it is preferred to use 8 awg -

1722355000165.png

So I'm going to use 8 gauge wire from the panel to the unit but I want to make sure I am getting the right breaker and disconnect.

Can anyone point me in the right direction for the breaker, the outdoor disconnect & whip?

Thanks!
 
To avoid these ads, REGISTER NOW!

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,351
Location
VT
Ignore the manual completely.

Do you have the unit?

What does the label on the unit say?

I went through this a few months ago trying to determine fuse vs. breaker. All that matters is the label on the unit.

Btw, my 18k is on a 25A breaker and #12
 
OP
L

Lovthebass

Active member
Joined
Dec 30, 2017
Messages
44
Ignore the manual completely.

Do you have the unit?

What does the label on the unit say?

I went through this a few months ago trying to determine fuse vs. breaker. All that matters is the label on the unit.

Btw, my 18k is on a 25A breaker and #12
I do have the unit but I didn't open it up yet.

I will when I get home from work tonight and post the label.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,351
Location
VT
I do have the unit but I didn't open it up yet.

I will when I get home from work tonight and post the label.

Here's my thread:


Summary: these manuals ****, the specs are different depending where you look. Tag on unit rules them all
 
OP
L

Lovthebass

Active member
Joined
Dec 30, 2017
Messages
44
Here's my thread:


Summary: these manuals ****, the specs are different depending where you look. Tag on unit rules them all
Ah, I see this can get confusing. I believe you have the same unit that I have but will confirm later.

So you used 12 gauge wire, 25 amp breaker & a non-fused disconnect I see.

Everything seems fine? How is the unit working for you?

Also, which disconnect did you go with?
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,351
Location
VT
Ah, I see this can get confusing. I believe you have the same unit that I have but will confirm later.

So you used 12 gauge wire, 25 amp breaker & a non-fused disconnect I see.

Fused disconnect.

Everything seems fine? How is the unit working for you?

Works good. Seems to have some harmonics, a few of my cheap LED light flicker when it's on. It's 86+ out right now and the far end of the house was 68 at lunch, so I'm happy.
Also, which disconnect did you go with?

I think GE, it was whatever Home Depot had in stock.
 
OP
L

Lovthebass

Active member
Joined
Dec 30, 2017
Messages
44
Fused disconnect.



Works good. Seems to have some harmonics, a few of my cheap LED light flicker when it's on. It's 86+ out right now and the far end of the house was 68 at lunch, so I'm happy.


I think GE, it was whatever Home Depot had in stock.
Oh, I see the reply you got from MrCool that said a non-fused disconnect was OK.

What fuse size did you need to get for the disconnect?

I'm glad it's working good! I'm excited to install this.
 
OP
L

Lovthebass

Active member
Joined
Dec 30, 2017
Messages
44
8 is a waste of money unless the run is 150+ feet.

I'd run 12
I have 10 gauge going to an electric heater halfway to where I would want to mount the disconnect box.

I'm going to decommission the heater so can I just connect to that wire once I disconnect the heater and run it to the disconnect box?
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,351
Location
VT
Oh, I see the reply you got from MrCool that said a non-fused disconnect was OK.

What fuse size did you need to get for the disconnect?

I'm glad it's working good! I'm excited to install this.
25A I believe.

It came down to it didn't matter what Mr cool told me via email, the label said X, you better do X to be compliant
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,403
Location
Richmond, VA
I have 10 gauge going to an electric heater halfway to where I would want to mount the disconnect box.

I'm going to decommission the heater so can I just connect to that wire once I disconnect the heater and run it to the disconnect box?
Yes. Go for it. I'd keep that run at 10 for the rest of the way. Make sure you keep the junction box accessible
 

Raisedonadeere

Well-known member
Joined
Jul 31, 2017
Messages
436
Location
Central KY
Something screwy about that manual. #8 would run a monster AC. I have 2 different 18k mini's hyper heat units, on 12ga and 15 amp breakers. I meant to use 20 amp breakers but had 15s when I installed and started using expecting the 15s to trip. Now, six years running. never a trip so I never installed the 20's. The data plate on my units look almost identical to yours.

For now just go by the minimum ampacity and realize that 12GA is good for 20 amp so 12Ga exceeds that. Run your wires, and settle later on what breaker to use.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,351
Location
VT
Can anyone help on this? I was hoping to pick up what I need soon. Thanks!

Thought I responded yesterday, sorry.

Get a 30A rated disconnect and 2 30A fuses.

You mentioned abandoning an existing feed to a heater, how much (if any) do you need to add on?

What breaker is that wire on?
 
OP
L

Lovthebass

Active member
Joined
Dec 30, 2017
Messages
44
Thought I responded yesterday, sorry.

Get a 30A rated disconnect and 2 30A fuses.

You mentioned abandoning an existing feed to a heater, how much (if any) do you need to add on?

What breaker is that wire on?
Last night I looked at what is there and the existing heater has 10/3 wire going to it. If I can use the existing 10/3 wire I would need to add about 25 feet. The total run would be about 45-50 feet.

Right now the breaker is 50A.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,403
Location
Richmond, VA
Last night I looked at what is there and the existing heater has 10/3 wire going to it. If I can use the existing 10/3 wire I would need to add about 25 feet. The total run would be about 45-50 feet.

Right now the breaker is 50A.
10/3? So a 4 wire connection? That needs to be a 30a breaker. A 50a would only be ok if it was a welder circuit

You only need 10/2 to get to the a/c
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,351
Location
VT
Last night I looked at what is there and the existing heater has 10/3 wire going to it. If I can use the existing 10/3 wire I would need to add about 25 feet. The total run would be about 45-50 feet.

Right now the breaker is 50A.

You sure it's 10/3?

I'd extend off that using 10/2 (cap the white wire on both ends) and reduce the breaker to 30A.

If starting from the panel, I think (would need to double check) you could run 12/2.
 
OP
L

Lovthebass

Active member
Joined
Dec 30, 2017
Messages
44
You sure it's 10/3?

I'd extend off that using 10/2 (cap the white wire on both ends) and reduce the breaker to 30A.

If starting from the panel, I think (would need to double check) you could run 12/2.
I apologize, it is 10/2

2 wires and a ground.
 
To avoid these ads, REGISTER NOW!
OP
L

Lovthebass

Active member
Joined
Dec 30, 2017
Messages
44
30a is max. I bet it would run fine on a 20a,but you won't gain anything by stepping down that far and a 30 will cost the same as a 20 or 25
I'm looking at this wire closer and the text on it says 8 gauge with a 10 gauge ground, sorry for the mistake.

So I can add onto this with 8/2 wire the rest of the way. Might be overkill but it's already half way there.

And the manual says 8 AWG is "preferred"
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,403
Location
Richmond, VA
I'm looking at this wire closer and the text on it says 8 gauge with a 10 gauge ground, sorry for the mistake.

So I can add onto this with 8/2 wire the rest of the way. Might be overkill but it's already half way there.

And the manual says 8 AWG is "preferred"
Ignore the preferred junk. It's a waste of money.

I'd extend with no larger than 10. Personally, I'd likely do it with 12 and install a 20a breaker
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,351
Location
VT
If you have access I'd just run new 12/2.

Screwing around with #8, a junction box, wire nuts etc. would frustrate me.

EDIT: don't forget all junction boxes must remain accessible.
 
Last edited:
OP
L

Lovthebass

Active member
Joined
Dec 30, 2017
Messages
44
I spoke to an electrician friend of mine and he said the following -

I can connect to the existing 8awg wire and keep going to the disconnect box.

Switch out the breaker to a 30 amp.

He said the disconnect doesn't matter, I can get any size unfused disconnect as long as I have a 30amp breaker.

Does all this sound correct?
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,403
Location
Richmond, VA
I spoke to an electrician friend of mine and he said the following -

I can connect to the existing 8awg wire and keep going to the disconnect box.

Switch out the breaker to a 30 amp.

He said the disconnect doesn't matter, I can get any size unfused disconnect as long as I have a 30amp breaker.

Does all this sound correct?
That's the same as what we have been saying
 

erik a

Well-known member
Joined
Jan 31, 2017
Messages
58
Location
Silver Spring MD
Ignore the manual completely.

Do you have the unit?

What does the label on the unit say?

I went through this a few months ago trying to determine fuse vs. breaker. All that matters is the label on the unit.

Btw, my 18k is on a 25A breaker and #12
ditto
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,351
Location
VT
I spoke to an electrician friend of mine and he said the following -

I can connect to the existing 8awg wire and keep going to the disconnect box.

Switch out the breaker to a 30 amp.

He said the disconnect doesn't matter, I can get any size unfused disconnect as long as I have a 30amp breaker.

Does all this sound correct?
No, that's not correct. You need a fused disconnect
 
OP
L

Lovthebass

Active member
Joined
Dec 30, 2017
Messages
44
No, that's not correct. You need a fused disconnect
He said if it's connected to a 30 amp breaker, a fused disconnect is not needed.

And If the breaker was bigger than 30amp, then a 30amp fused disconnect would need to be used.

Is he mistaken? If so, how?
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,351
Location
VT
He said if it's connected to a 30 amp breaker, a fused disconnect is not needed.

And If the breaker was bigger than 30amp, then a 30amp fused disconnect would need to be used.

Is he mistaken? If so, how?
Go read my thread I posted.

If the equipment tag says "max fuse", you need a fuse.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,351
Location
VT
There has been some debate on this here. I thought the same but was told be the real sparkies that it doesnt

Thanks for that shot...

I was told by them here that it does, so I returned my non-fused and bought the fused version.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,351
Location
VT
:)

I have no idea what the real answer is. I'd use one with fuses
That's where I landed.. didn't make any sense to me, but if the nameplate rules all it was simpler just to use them.

A couple quotes from my thread:

the nameplate is controlling. If it's wrong, they need a recall campaign to supply the correct nameplate.

Looks like they need to update their nameplate as thats what you should be basing the circuit off of
 
OP
L

Lovthebass

Active member
Joined
Dec 30, 2017
Messages
44
So I finished installing the unit and it came out well. I used 8 awg wire, 30 amp fused disconnect and a 30 amp breaker. I also installed a surge protector. I must say it was very easy to install and the unit works great for AC so far. I’ll see how the heat is in the winter. Using 8 gauge wire was overkill and hard to deal with sometime, 10 gauge would be definitely easier to deal with. The build quality of the MrCool unit seems to be made well, if it heats well and lasts years then I believe it was a good buy.
 

teknikfrog

Well-known member
Joined
Apr 29, 2023
Messages
216
I bet when the data plate says "max fuse" it just means:

"some means of interrupting the power"

So a breaker on the circuit is completely fine. Fuse / breaker no difference. Obviously a fused disconnect adds some manner of protection but is not needed.

(Not an electrician)
 