Yes, no problem removing/moving them.
Yes, same unit with attached lines.
My AC tech adds freon based on pressure. At least that's how I understand it. The first service they did not evacuate, they charged and used a leak probe. It was working fine, but I thought since I was getting a replacement unit, that rather than let the freon leak out I would close the valves.
It's working great, but I have a hunch it needs a little more freon. 60oz capacity.
I have a call in for our local tech - he's great. Probly cost me $100. Well worth it.
The new wifi program is really great.
So -- you needed to remove the old head and line and install both new?
The new Mr. Cool warranty provides some $$ for labor ... but -- the new system would allow for just head reattach if you can move things around since it's not three independent parts.
Minisplits don't get charged based on pressure -- they are weight charged. The expansion valve is in the outside unit. i'm sure it is undercharged as some leaked out and the new head/ lineset is not proving the charge.
There is a good possibility the head was damaged when it was installed -- this is a common problem when trying to get them installed ... the less expensive units don't have the evap protection as some do.