Multi-Wire Branch Circuit - Common Neutral

To avoid these ads, REGISTER NOW!

dledinger

Well-known member
Joined
Apr 14, 2009
Messages
345
Big fan of MWBCs where permissible, and especially in shop environments.

Not a fan, in any application, of lights and receptacles on the same branch circuit.

I never liked seeing “shared neutral”, just because it’s not a very good description of what the neutral is doing.

Anyway, glad to see you’re getting it done.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,600
Location
BC
When I feed a wall of outlets off a 3-wire circuit, I tend to alternate which leg I hook up, or do a quad box with an outlet on each. It ends up with better load balancing, and you have both circuits available for future expansion. You can also add in a 240V outlet anywhere along that run.


Big fan of MWBCs where permissible, and especially in shop environments.

Not a fan, in any application, of lights and receptacles on the same branch circuit.

:thumbup:
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,584
Location
Fullerton, CA
The fact that every POCO uses multiwire circuits exclusively from the generating station to the customer's service, yet some people don't want use them for their branch circuits has never made much sense to me. :headscrat
 

slow

Well-known member
Joined
Feb 26, 2006
Messages
2,596
Location
near Orlando
The biggest reason I don't like MWBC's is the required double pole GFCI requirements for places like "garages" A GFCI receptacle is $16, a 2 pole GFCI breaker is $80 for a SQD QO panel. Around here a 250 foot roll of 12/3 NM-B is $58 and a roll of 12/3 is 112 from home depot, so you are not really saving any money on wire cost if running romex.

If it was not for GFCI and ACFI requirements, and especially if running in conduit where you do have a wire cost savings no reason not to use them, but those are my reasons to not use them.
 

AntonLargiader

Well-known member
Joined
Nov 20, 2016
Messages
1,372
Location
Charlottesville, VA
Are GFCI breakers really required, rather than GFCI receps?

The biggest reason I don't like MWBC's is the required double pole GFCI requirements for places like "garages" A GFCI receptacle is $16, a 2 pole GFCI breaker is $80 for a SQD QO panel. Around here a 250 foot roll of 12/3 NM-B is $58 and a roll of 12/3 is 112 from home depot, so you are not really saving any money on wire cost if running romex.

If it was not for GFCI and ACFI requirements, and especially if running in conduit where you do have a wire cost savings no reason not to use them, but those are my reasons to not use them.
 

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
Are GFCI breakers really required, rather than GFCI receps?

Only if you're going to install GFCI receptacles at EVERY location. You can't feed a bunch of regular receptacles from the load side of a GFCI using a shared neutral.

Unless you're only using the shared neutral for the home run back to the panel, and it splits off into 2 individual circuits with their own separate neutral wires.
 

AntonLargiader

Well-known member
Joined
Nov 20, 2016
Messages
1,372
Location
Charlottesville, VA
Depends what you are trying to do, I guess. My MWBCs go somewhere and then split to two different things, I can GFCI at the split and protect the rest of that branch. But if you're trying to keep that shared neutral as you go from device to device, yeah, that won't work.

Only if you're going to install GFCI receptacles at EVERY location. You can't feed a bunch of regular receptacles from the load side of a GFCI using a shared neutral.

Unless you're only using the shared neutral for the home run back to the panel, and it splits off into 2 individual circuits with their own separate neutral wires.
 

dledinger

Well-known member
Joined
Apr 14, 2009
Messages
345
Yep - and this is the reason there are so few MWBCs today. They’re basically legislated into the history books.
 

dledinger

Well-known member
Joined
Apr 14, 2009
Messages
345
Lol...all I’m saying is that the GFCI requirements had a major impact in the use of MWBCs. That’s the most commonly cited example of why they are difficult to use and avoided.
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,765
Lol...all I’m saying is that the GFCI requirements had a major impact in the use of MWBCs. That’s the most commonly cited example of why they are difficult to use and avoided.

I would not say they are difficult to use, a bit more expensive now but not difficult.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,600
Location
BC
Lol...all I’m saying is that the GFCI requirements had a major impact in the use of MWBCs. That’s the most commonly cited example of why they are difficult to use and avoided.

Oh the irony.... maybe its the GFCIs that make things difficult and should be avoided :lol_hitti
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,584
Location
Fullerton, CA
I would put AFCIs at the top of that list.

2 pole dual function (with both AFCI and GFCI protection) cost more than regular breakers but just have 1 extra wire to terminate; the wire from the breaker to the neutral bar, so there is minimal additional labor involved. They even ship the breaker's wire pre-stripped
:lol_hitti
 

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
2 pole dual function (with both AFCI and GFCI protection) cost more than regular breakers but just have 1 extra wire to terminate; the wire from the breaker to the neutral bar, so there is minimal additional labor involved. They even ship the breaker's wire pre-stripped
:lol_hitti
I have Eaton CH panels in my house and Eaton doesn't make 2-pole dual function breakers; the only dual function breakers they offer are single pole.
 

dledinger

Well-known member
Joined
Apr 14, 2009
Messages
345
Anyway you decide to slice it, I’ve seen a huge decrease in the use of MWBCs. Maybe locale driven, I don’t know.

Regardless, I remain a fan particularly in shop applications.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I use them when it makes sense, need to reduce fill, long runs. Lots of places, small garages or simple residential I like it on single pole and simple.
 