I had this same issue with a client of mine. They had a 'stick framed' roof out of 2x4 top and bottom cord with 3/8" plywood gussets on the joints. They gussets were only 8"x8" and were failing after a huge snowfall in '96. So..... how we solved this problem was like this; We had a 4" sag in a standard flat ceiling. Removed the drywall ceiling, v.b. and drywall. We gave the client a vaulted ceiling by contacting our local truss company. Had them come in and measure, produce the vaulted truss in 2 pieces so we could do the work from the inside as they had a new roof so we didn't want to remove it. Nailed the 2 halves to the existing trusses, joined the 2 pieces with 3/4" ply, PL400 and plenty of nails. Cut away the old truss to produce the vault. All engineered.
The troubled roof was from gable to gable so the gable ends had no sag. Strung a line under the peak on the vault. Raised each truss up individually, and made sure everything was looking good inside. The roofline on the exterior ended up looking good.
The troubled roof was from gable to gable so the gable ends had no sag. Strung a line under the peak on the vault. Raised each truss up individually, and made sure everything was looking good inside. The roofline on the exterior ended up looking good.